UPS immediately performs a power-off of all Outlet Groups

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS immediately performs a power-off of all Outlet Groups
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
kpn
kpn
Cadet

Posted: ‎2024-05-24 11:00 AM

0 Likes
1
393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-24 11:00 AM

UPS immediately performs a power-off of all Outlet Groups

Hello!

I have a Smart-UPS SRT 6000.

I performed a scheduled battery replacement on the APCRBC140.
Self-Test is successful.
But now, if there is any short-term power failure, the UPS does not switch to battery power, but immediately performs a power-off of all Outlet Groups.
And then again performs power-on of all Outlet Groups

 

Log below

 05/24/2024 15:53:59 Device UPS: Bypass not in range ; distorted waveform.
 05/24/2024 15:53:59 Device UPS: The graceful shutdown period has ended.
 05/24/2024 15:53:59 Device UPS: The output power is turned off.
 05/24/2024 15:53:59 Device UPS: The power for the main outlet group, Unswitched Group, is now turned off.
 05/24/2024 15:53:59 Device UPS: Main outlet group, Unswitched Group, has been commanded to shutdown with on delay.
 05/24/2024 15:53:59 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.
 05/24/2024 15:53:59 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay.
 05/24/2024 15:53:59 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off.
 05/24/2024 15:53:59 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay.
 05/24/2024 15:53:59 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off.
 05/24/2024 15:53:59 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay.
 05/24/2024 15:54:11 Device UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.
 05/24/2024 15:54:12 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on.
 05/24/2024 15:54:12 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on.
 05/24/2024 15:54:12 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on.
 05/24/2024 15:54:12 Device UPS: The output power is now turned on.
 05/24/2024 15:54:13 Device UPS: The power for the main outlet group, Unswitched Group, is now turned on.

 

Shutdown Settings  bellow attachment

Shutdown_Settings.JPG

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Teken
Janeway Teken
Janeway

Posted: ‎2024-05-28 06:22 AM

0 Likes
0
380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-28 06:22 AM

For starters based on the screen capture it doesn’t appear the UPS is defined very well?!? Obviously this is up to you but the following suggestions makes a lot more sense.

 

Low Battery Duration: The default is 2 minutes but you set yours to 20?!? A good compromise is 5 minutes before the system begins a shutdown. The basic low battery duration should be defined the same if 5 minutes is used. 

 

The UPS should be defined to restart once AC Mains is restored. You have defined the system to remain off?!? 🤔

 

As it relates to the outlets turning off then on. Without seeing and knowing how this device was programmed it could be improper defined settings.

 

If you’re in doubt about how this unit is setup. I would encourage you to default the system to an OEM state. Doing so will at least eliminate user error / poor user defined settings. ☝️

 

If you see the same behaviour once the unit is in a default state. We can focus on the next steps and possible solutions. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of