Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey
UPS fails to read battery percentage
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-10-0705:39 AM
UPS fails to read battery percentage
Apc power supply unit fails to monitor the battery percentage as reading 0% this is still after a complete new battery purchased, but still the same condition
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-10-0706:25 AM
The proper steps when replacing the RBC are outlined below if applicable. Keep in mind the RBC must be allowed to fully charge for a minimum of 24-72 hours depending upon the capacity:
Date: Update the battery installation date via APC Power Chute Software. Doing so resets internal counters and adjusts charging tables if applicable.
Self Test: Manually initiate a self test via LCD, Power button, Power Chute and let pass and recover to 100% SOC (State of Charge).
Battery Calibration: Manually initiate a battery calibration via LCD, Power Chute with a minimum of 30% attached load. Once complete allow the system to recover and recharge the RBC to 100% SOC.
The LCD will now reflect the operational runtime more accurately when the system engages battery only mode.