UPS communication lost error - vMA on ESX 5.1

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS communication lost error - vMA on ESX 5.1
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 03:18 AM . Last Modified: ‎2024-03-05 10:59 PM

0 Likes
4
1367
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:18 AM . Last Modified: ‎2024-03-05 10:59 PM

UPS communication lost error - vMA on ESX 5.1

Hello everyone,

I just joined this forum specifically to address this problem.  We have an HP Proliant ML350P Gen 8 with an ESX 5.1 installed on it.  We will eventually be converting a Windows Server 2003 VM on it and we need to add a graceful shutdown option to the server.  We bought a SmartUPS 1500 to manage the power for the server.  I then followed the instructions found here in the link below to install vMA and set up PowerChute Business Edition:

http://www2.schneider-electric.com/resources/sites/SCHNEIDER_ELECTRIC/content/live/FAQS/165000/FA165...

Obviously since I'm installing on a linux machine (vMA) running SUSe, I have to use the RJ-45 to Serial cable. The installation goes well and once it's done I'm able to manage from the web browser for a certain period of time.  The problem is when I come in the next day I can no longer view the UPS status in the PCBE web browser.  When I log in, a message says "UPS Communication lost".  I have already tried the following steps:

1) Verify the UPS-to-server cable is correct.  I am using the suggested 940-0625 cable.  I have tried re-seating it and even changing to a backup cable of the same type (yes, it is also an APC cable).  None of these restore the communication.

2) Restart the services on the vMA.  I do this with two methods:

                  sudo /etc/rc.d/init.d/PBEAgent stop, sudo /etc/rc.d/init.d/PBEAgent start

                  ./opt/APC/PowerChuteBusinessEdition/Agent/bin/ startup stop /opt/APC/PowerChuteBusinessEdition/Agent/bin/ startup start

     The reset is working since I lose access to the PCBE web session but when I log back in after the service is up the UPS communication is still lost.

3) Reset machines.  I tried resetting the vMA, and even the server.  When they come back online there is no change in the status.

4) The ONLY option that works so far is to completely power everything off, turn off the UPS, uplug and replug and then power everything back on.  Once I do this, everything returns to normal and I have access to all PCBE's functions.  This is not an optimal solution since it once again loses communication the following day.

I have been troubleshooting this for over a week now and it is very frustrating.  I even tried reinstalling the vMA on a completely new UPS on a completely different Dell server with the same result.  Obviously there is something wrong with the configuration so I called Schneider to open a ticket.  We walked through the same processes above with the same result.  One suggested solution was to use a USB cable, but the linux install does not give that option.  It only allows a DB9 or RJ-45.  Since our UPS only comes with an RJ-45 and a USB type B, we have no choice but to use RJ-45 to Serial (unless there is some sort of RJ-45 to USB cable that APC supports).

Does anyone else have any ideas about how to get this thing working?  The only difference between the instructions above and the way I did things was to use thin provisioning instead of thick provisioning on the vMA.  I doubt this has any affect on the UPS communication but I could be wrong so I may try that approach today.  FYI, I had a hard time installing the VMWare tools but I finally got them working (somewhat).  VMware tools are for time synchronization and shutdown helping.  However, since the shutdown was working fine beforehand I don't think this is the issue.  This may be a time synchronization issue, so checked my time stamps on the vMA and the ESX.  They were way off so I fixed those and will try a new installation with all of those settings tonight.

I apologize for the long-winded explanation, but I need to have this UPS up and running by the end of the day on Thursday so I only have 2 more days to finish it!  Can anyone please share their wisdom and APC ninja skills with me?

Thank you very much.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • communication_lost
  • esx_5.1
  • smartups_1500
  • vma
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:18 AM . Last Modified: ‎2024-03-05 10:59 PM

0 Likes
0
1366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:18 AM . Last Modified: ‎2024-03-05 10:59 PM

Hi,

It sounds like the HP server has iLO enabled. Check out these HP knowledge base documents.

http://h20000.www2.hp.com/bizsupport/TechSupport/Document.jsp?objectID=c00843255〈=en&cc=us&taskId=10...

http://h20000.www2.hp.com/bizsupport/TechSupport/Document.jsp?lang=en&cc=us&objectID=c01139344&jumpi...


See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:18 AM . Last Modified: ‎2024-03-05 10:59 PM

0 Likes
0
1367
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:18 AM . Last Modified: ‎2024-03-05 10:59 PM

Hi,

It sounds like the HP server has iLO enabled. Check out these HP knowledge base documents.

http://h20000.www2.hp.com/bizsupport/TechSupport/Document.jsp?objectID=c00843255〈=en&cc=us&taskId=10...

http://h20000.www2.hp.com/bizsupport/TechSupport/Document.jsp?lang=en&cc=us&objectID=c01139344&jumpi...


Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 03:18 AM . Last Modified: ‎2024-03-05 10:59 PM

0 Likes
0
1366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:18 AM . Last Modified: ‎2024-03-05 10:59 PM

Thank you for the reply, BIll.

I hadn't thought of that so I will try it when I get back to the office later today and report my findings.  You are correct that it has an iLO port and if that's blocking serial connections that may be our culprit.

Also to report my findings from last night's tests, I reset the APC unit again and matched the times up on the servers (manually) and left it overnight.  This morning when I checked it's still communicating!  I'll check once more when I get back to the office later today.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 03:18 AM . Last Modified: ‎2024-03-05 10:57 PM

0 Likes
0
1366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:18 AM . Last Modified: ‎2024-03-05 10:57 PM

Bill that was remarkably simple.  It seems to be working for now because right after I disabled CLI through the serial cable on the iLO the communication was back!  I will see if this is still the case tomorrow but that's amazing that it fixed things so quickly!  Thank you so much for the help smile

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 03:18 AM . Last Modified: ‎2024-03-05 10:57 PM

0 Likes
0
1366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:18 AM . Last Modified: ‎2024-03-05 10:57 PM

Definitely qualifies as ninja skills!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore