Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

UPS: The output has a short-circuit

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS: The output has a short-circuit
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-25 11:09 PM . Last Modified: ‎2024-03-19 03:19 AM

0 Likes
1
4645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 11:09 PM . Last Modified: ‎2024-03-19 03:19 AM

UPS: The output has a short-circuit

Hello,

Anyone experience UPS: The output has a short-circuit that commanded outlet groups to turn off when accidentally tripped the input cable?
Should the ups would battery mode and not to turn off the outlet group?

Device: SRT 5000

Logs:

04/02/2019 08:45:13 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
04/02/2019 08:45:13 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
04/02/2019 08:45:12 Device UPS: The output no longer has a short-circuit. 0x015E
04/02/2019 08:45:04 System Email: Could not resolve 'smtp.office365.com'. 0x001A
04/02/2019 08:44:34 System Email: Could not resolve 'smtp.office365.com'. 0x001A
04/02/2019 08:44:06 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to turn off, sequenced. 0x0174
04/02/2019 08:44:06 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to turn off, sequenced. 0x0174
04/02/2019 08:44:05 Device UPS: The output power is turned off. 0x0114
04/02/2019 08:44:05 Device UPS: The graceful shutdown period has ended. 0x014F
04/02/2019 08:44:05 Device UPS: The output has a short-circuit. 0x015D
03/31/2019 13:15:08 Device UPS: Self-Test passed. 0x01D2
03/31/2019 13:14:47 Device UPS: Self-Test started by management device. 0x0137
Regards,
Labels
  • Labels:
  • Getting Started
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-25 11:09 PM . Last Modified: ‎2024-03-19 03:19 AM

0 Likes
0
4642
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 11:09 PM . Last Modified: ‎2024-03-19 03:19 AM

Had the same thing happened a day ago although i don't know the reason.

Currently I've just replaced it with a spare but i really need to find out why this happened?

Below are the logs.

05-Jun-19 13:36:37 Device UPS: The output power is turned off. 0x0114
05-Jun-19 13:36:37 Device UPS: The output power is now turned on. 0x0113
05-Jun-19 13:36:37 Device UPS: The output power is turned off. 0x0114
05-Jun-19 13:36:37 Device UPS: The output power is now turned on. 0x0113
05-Jun-19 13:36:37 Device UPS: The output power is turned off. 0x0114
05-Jun-19 13:36:37 Device UPS: The output power is now turned on. 0x0113
05-Jun-19 13:36:37 Device UPS: The output power is turned off. 0x0114
05-Jun-19 13:36:37 Device UPS: The output power is now turned on. 0x0113
05-Jun-19 13:36:37 Device UPS: The output power is turned off. 0x0114
05-Jun-19 13:36:37 Device UPS: The graceful shutdown period has ended. 0x014F
05-Jun-19 13:36:36 Device UPS: The power for switched outlet group 3, Outlet Group 3, is off. 0x0186
05-Jun-19 13:36:36 Device UPS: The power for switched outlet group 2, Outlet Group 2, is off. 0x0186
05-Jun-19 13:36:36 Device UPS: The power for switched outlet group 1, Outlet Group 1, is off. 0x0186
05-Jun-19 13:36:36 Device UPS: The output has a short-circuit. 0x015D
05-Jun-19 13:36:34 Device UPS: Restored the local network management interface-to-UPS communication. 0x0101
05-Jun-19 13:36:23 System Network service started. IPv6 address FE80::2C0:B7FF:FE9B:BA71 assigned by link-local autoconfiguration. 0x0007
05-Jun-19 13:36:20 System Network service started. System IP is 10.147.162.199 from manually configured settings. 0x0007
05-Jun-19 13:36:13 System Network Interface coldstarted. 0x0001
05-Jun-19 13:19:04 System Network service started. IPv6 address FE80::2C0:B7FF:FE9B:BA71 assigned by link-local autoconfiguration. 0x0007
05-Jun-19 13:19:02 System Network service started. System IP is 10.147.162.199 from manually configured settings. 0x0007
05-Jun-19 13:18:54 System Network Interface coldstarted. 0x0001
05-Jun-19 13:18:33 Device UPS: Self-Test started by automatic timer. 0x0137
30-May-19 12:49:28 System Web user 'apc' logged out from 10.147.16.118. 0x001F

Any help or explanations as to why this happened would be much appreciated.

See Answer In Context

  • Tags:
  • shortcircuit
  • smx1500rmi2unc
Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-25 11:09 PM . Last Modified: ‎2024-03-19 03:19 AM

0 Likes
0
4643
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 11:09 PM . Last Modified: ‎2024-03-19 03:19 AM

Had the same thing happened a day ago although i don't know the reason.

Currently I've just replaced it with a spare but i really need to find out why this happened?

Below are the logs.

05-Jun-19 13:36:37 Device UPS: The output power is turned off. 0x0114
05-Jun-19 13:36:37 Device UPS: The output power is now turned on. 0x0113
05-Jun-19 13:36:37 Device UPS: The output power is turned off. 0x0114
05-Jun-19 13:36:37 Device UPS: The output power is now turned on. 0x0113
05-Jun-19 13:36:37 Device UPS: The output power is turned off. 0x0114
05-Jun-19 13:36:37 Device UPS: The output power is now turned on. 0x0113
05-Jun-19 13:36:37 Device UPS: The output power is turned off. 0x0114
05-Jun-19 13:36:37 Device UPS: The output power is now turned on. 0x0113
05-Jun-19 13:36:37 Device UPS: The output power is turned off. 0x0114
05-Jun-19 13:36:37 Device UPS: The graceful shutdown period has ended. 0x014F
05-Jun-19 13:36:36 Device UPS: The power for switched outlet group 3, Outlet Group 3, is off. 0x0186
05-Jun-19 13:36:36 Device UPS: The power for switched outlet group 2, Outlet Group 2, is off. 0x0186
05-Jun-19 13:36:36 Device UPS: The power for switched outlet group 1, Outlet Group 1, is off. 0x0186
05-Jun-19 13:36:36 Device UPS: The output has a short-circuit. 0x015D
05-Jun-19 13:36:34 Device UPS: Restored the local network management interface-to-UPS communication. 0x0101
05-Jun-19 13:36:23 System Network service started. IPv6 address FE80::2C0:B7FF:FE9B:BA71 assigned by link-local autoconfiguration. 0x0007
05-Jun-19 13:36:20 System Network service started. System IP is 10.147.162.199 from manually configured settings. 0x0007
05-Jun-19 13:36:13 System Network Interface coldstarted. 0x0001
05-Jun-19 13:19:04 System Network service started. IPv6 address FE80::2C0:B7FF:FE9B:BA71 assigned by link-local autoconfiguration. 0x0007
05-Jun-19 13:19:02 System Network service started. System IP is 10.147.162.199 from manually configured settings. 0x0007
05-Jun-19 13:18:54 System Network Interface coldstarted. 0x0001
05-Jun-19 13:18:33 Device UPS: Self-Test started by automatic timer. 0x0137
30-May-19 12:49:28 System Web user 'apc' logged out from 10.147.16.118. 0x001F

Any help or explanations as to why this happened would be much appreciated.

  • Tags:
  • shortcircuit
  • smx1500rmi2unc
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore