APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-06-26 05:30 AM . Last Modified: 2024-03-19 12:46 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:30 AM . Last Modified: 2024-03-19 12:46 AM
Dear,
We have 2 Numbers of Smart-UPS RT 10000 XL getting power from same source. However, today we have got an alarm from one of them only as below:
Please note that the UPS went to battery and back to AC power within 1 second.
I have doubt if there is a power problem we should get this alarm in both UPS but we have got it only in one of them.
What are other possibilities to have this such of alarm in one of the UPS only?
Is it possible that if we connect an equipment during this time to the PDU connect to this UPS can caused this? because we were connecting a small router to the PDU of this UPS during this time.
regards
Mahmood
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:30 AM . Last Modified: 2024-03-19 12:46 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:30 AM . Last Modified: 2024-03-19 12:46 AM
please tell me ups installed on three or single phase(L1..L2..L3..N .. or L1.......N), and selector switch position ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:30 AM . Last Modified: 2024-03-19 12:46 AM
It's always possible for a power condition to trigger one UPS but not another. It may have been a marginal case at the edge of the decision boundary.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:30 AM . Last Modified: 2024-03-19 12:46 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:30 AM . Last Modified: 2024-03-19 12:46 AM
please tell me ups installed on three or single phase(L1..L2..L3..N .. or L1.......N), and selector switch position ?
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.