UPS NIC keeps rebooting after failed firmware update.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS NIC keeps rebooting after failed firmware update.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

0 Likes
3
1129
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

UPS NIC keeps rebooting after failed firmware update.

I have a Smart UPS 3000 with an AP9617 NIC. I had this all configured and ready to go into production but I thought I'd just run the firmware update to 3.7.3 as I have done on several other UPS we have here.

The first time the firmware upgrade failed using the executable. I've seen this happen before, so using suggestions in other topics in this forum I followed the FTP flashing instructions. Everything seemed to go well, but then as I tried to reconnect to the UPS I either got a page cannot be displayed error or I got an APC screen telling me the device was rebooting. After waiting for a while I tried again and got the same results.

I tried connecting to it locally via the serial connection and could get through, so reset the card back to defaults, apart from the tcpip settings, but I also kept seeing that the telnet session would occasionally freeze and send me back to the login prompt, which lead me to think that the NIC was rebooting.

Running a constant ping I get intermittent replies for about 5 pings, then several timeouts, this repeats endlessly.

When connecting via serial the status of the UPS is P+ N+ A?

Is my NIC fried?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:07 AM . Last Modified: ‎2024-03-13 11:29 PM

0 Likes
0
1129
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:07 AM . Last Modified: ‎2024-03-13 11:29 PM

no problem. it would also to know what colors the status LED was blinking to find out what state the card was in. glad its all set.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

0 Likes
0
1128
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

what is the status LED on the card doing when this happens? do you have enough time to check the event log to tell us what events its reporting? when you telnet in and do Ctrl + L, it should pop up for you. that'd be helpful.

once you get this info, i would try to reseat the card in the smartslot and see what happens. pull the card out of the slot and leave it out for about 30 seconds then reinsert it. the information above may be helpful first if you have not done this already.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

0 Likes
0
1128
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:06 AM . Last Modified: ‎2024-03-13 11:29 PM

The status LED was just blinking on and off repeatedly.. During the time I posted this and now I have resolved the problem by turning everything off and reseating the card.

I didn't know that about the event log. Could be handy if things go wrong in the future.

Cheers for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:07 AM . Last Modified: ‎2024-03-13 11:29 PM

0 Likes
0
1130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:07 AM . Last Modified: ‎2024-03-13 11:29 PM

no problem. it would also to know what colors the status LED was blinking to find out what state the card was in. glad its all set.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.