UPS ES 550 electrical power down no report

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS ES 550 electrical power down no report
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
138
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 12:58 AM . Last Modified: ‎2024-03-19 02:39 AM

0 Likes
5
1102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:58 AM . Last Modified: ‎2024-03-19 02:39 AM

UPS ES 550 electrical power down no report

Hi, since you don't have french forum, I will tried to explain my problem in English has much that I can. 

I have a BACK-UP UPS ES 550G, and when a electrical power failure occur, the system does not hold the power to the computer and others attach instruments to it. Everything shutdown on the electrical power failure. I have install the software PowerChute Personal Edition 3.1.0 that tell's me that everything is working fine. Although that I have a electrical power failure for more than an hour and half, it that not report that failure or anyother failures for that matter. The software inform me that the battery is at 82% and charging. The electrical power is at 124 volts. The software does not permit me to do a power test with the Back-UP system. I have done a Brain dead test, and it did not solve the problem. 

Could you please give me more information on this problem so that I may know what is the problem with with this tool. 

I thank you for your support on this matter. 

Labels
  • Labels:
  • General Questions & Suggestions
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-26 12:58 AM . Last Modified: ‎2024-03-19 02:39 AM

0 Likes
0
1102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:58 AM . Last Modified: ‎2024-03-19 02:39 AM

Bonjour Bill,

Merci de votre réponse. Alors, je devrai changer d'UPS, il est défectueux. 

Tous les appareils qui y sont branchés, fonctionnement avec le courant électrique, mais l'appareil ne prend plus les surcharges et les sous tensions. 

Salutations

Marcel 

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 12:58 AM . Last Modified: ‎2024-03-19 02:39 AM

0 Likes
0
1102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:58 AM . Last Modified: ‎2024-03-19 02:39 AM

Hi Marcel,

The first thing to check is that your devices are connected to correct outlets, on that unit some of the sockets are surge protection only and some are surge and backup power.

Another thing to check would be the load is not above what the device is rated for, you can test thing by only connecting something with a low power usage to the unit and unplugging it from the mains, something like a phone charger and seeing if it maintains that load.

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 12:58 AM . Last Modified: ‎2024-03-19 02:39 AM

0 Likes
0
1102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:58 AM . Last Modified: ‎2024-03-19 02:39 AM

Hi Gavan, thank you for your reply.

There are 4 devices connected to the outlets. Three of them on the surge and back-up power, the computer, the modem and the screen and one on the surge only, the speakers use only a low power. 

When there is a electrical power shut down, the unit would provide power to the devices for at least an half hour. It does not do that anymore. The unit provide electrical power in the same way that the devices would be plugs into an outlet. So if there is a power failure, the unit would not provide the power to the units and when the electrical power comes back, everything works fine. In other words, having this unit to provide power back-up and the surge, since it does not work anymore, it's like not having it at all. I have done a reset to it, but that did not change anything. 

Surprisingly, the software does not give the right report on the usage of the unit. Actually, it gives a report like if everything is working fine. There doesn't seem to have a battery charge-up problem because the light near the power push-button is green. There is a constant beep when a electrical power shut-down occur. 

Hopefully, you would be able to help me with this problem, I thank you for your support.

Best regards,

Marcel 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 12:58 AM . Last Modified: ‎2024-03-19 02:39 AM

0 Likes
0
1102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:58 AM . Last Modified: ‎2024-03-19 02:39 AM

Well, it's seems that I will not get help with this problem. Can someone at least tell me who I should see to see what is wrong with this unit. My last post is of the 14th of June. No follow up since then. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 12:58 AM . Last Modified: ‎2024-03-19 02:39 AM

0 Likes
0
1102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:58 AM . Last Modified: ‎2024-03-19 02:39 AM

Hi,

On 6/16/2020 12:13 PM, Marcel said:

There is a constant beep when a electrical power shut-down occur. 

A constant tone indicates an overload state. If as you wrote the UPS is not overloaded that would indicate an internal component failure so the UPS should be replaced. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 12:58 AM . Last Modified: ‎2024-03-19 02:39 AM

0 Likes
0
1103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 12:58 AM . Last Modified: ‎2024-03-19 02:39 AM

Bonjour Bill,

Merci de votre réponse. Alors, je devrai changer d'UPS, il est défectueux. 

Tous les appareils qui y sont branchés, fonctionnement avec le courant électrique, mais l'appareil ne prend plus les surcharges et les sous tensions. 

Salutations

Marcel 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore