Posted: 2021-06-28 04:30 AM . Last Modified: 2024-03-18 04:29 AM
I receive Compensating for a low input voltage. 0x010B message every day
Since this is power quality issue of building , I can't fixed it.
4/07/2016 08:54:54 Device UPS: No longer compensating for a low input voltage. 0x010C
04/07/2016 08:54:51 Device UPS: Compensating for a low input voltage. 0x010B
Can I change ups setting (eg: input voltage)for avoiding this message occurred from network management card ?
Smart-UPS X 3000 Data Log:
Date Time Vmin Vmax Vout Iout %Wout %out FrqOut %Cap Vbat Tups
04/07/2016 12:03:23 209.12 213.03 211.87 1.93 10.91 13.65 49.98 100.00 135.84 27.74
04/07/2016 11:53:23 209.10 213.70 213.00 1.93 10.98 13.86 49.98 100.00 135.84 27.67
04/07/2016 11:43:23 208.71 213.32 209.98 1.93 11.01 13.77 49.98 100.00 135.87 27.58
04/07/2016 11:33:23 209.20 213.98 212.40 1.96 11.16 13.99 49.98 100.00 135.93 27.35
04/07/2016 11:23:23 209.71 213.71 211.73 1.93 11.05 13.86 49.98 100.00 135.96 27.23
04/07/2016 11:13:22 210.25 214.20 211.92 1.93 11.02 13.89 49.98 100.00 135.96 27.16
04/07/2016 11:03:22 209.96 213.93 212.68 1.93 11.00 13.87 49.98 100.00 136.00 27.04
04/07/2016 10:53:22 209.67 213.73 212.04 1.93 11.05 13.86 49.98 100.00 136.06 26.81
04/07/2016 10:43:22 208.40 213.18 209.81 1.96 11.10 13.80 49.98 100.00 136.09 26.69
04/07/2016 10:33:22 209.89 213.60 211.06 1.96 11.19 13.88 50.06 100.00 136.09 26.58
04/07/2016 10:23:22 208.62 213.04 212.92 1.93 11.06 13.89 50.06 100.00 136.12 26.47
04/07/2016 10:13:22 208.43 212.34 212.15 1.93 11.01 13.87 49.97 100.00 136.18 26.20
04/07/2016 10:03:22 208.51 213.06 211.59 1.96 11.07 13.90 49.97 100.00 136.25 26.04
04/07/2016 09:53:22 209.67 213.39 212.29 1.96 11.08 13.93 49.97 100.00 136.28 25.88
04/07/2016 09:43:22 208.37 215.79 211.96 1.93 11.08 13.90 49.97 100.00 136.31 25.75
04/07/2016 09:33:22 207.45 215.85 214.65 1.93 11.09 14.03 49.97 100.00 136.34 25.60
04/07/2016 09:23:22 207.90 212.75 209.09 1.96 11.12 13.76 49.97 100.00 136.37 25.49
04/07/2016 09:13:22 208.95 212.50 211.31 1.96 11.07 13.90 49.97 100.00 136.37 25.41
04/07/2016 09:03:22 195.20 213.35 211.89 1.93 11.03 13.85 49.97 100.00 136.40 25.37
04/07/2016 08:53:22 209.07 216.21 212.17 1.84 11.01 13.05 49.97 100.00 134.43 25.41
04/07/2016 08:43:22 208.28 215.07 213.84 1.81 10.97 13.13 49.97 100.00 134.65 25.50
04/07/2016 08:33:22 209.23 213.54 211.37 1.84 10.92 13.00 49.97 100.00 134.90 25.60
04/07/2016 08:23:22 209.07 213.65 212.14 1.84 10.93 13.05 49.97 100.00 135.18 25.70
04/07/2016 08:13:22 209.34 214.28 212.21 1.84 10.94 13.04 49.97 100.00 135.53 25.76
04/07/2016 08:03:22 210.10 214.60 212.57 1.93 10.97 13.79 49.98 100.00 136.31 25.77
04/07/2016 07:53:22 210.56 215.62 214.06 1.90 10.85 13.65 49.98 100.00 136.28 25.80
04/07/2016 07:43:22 209.71 214.57 211.40 1.93 10.85 13.68 49.98 100.00 136.28 25.85
04/07/2016 07:33:22 210.35 215.28 214.57 1.90 10.89 13.75 49.98 100.00 136.28 25.89
04/07/2016 07:23:22 210.67 214.92 213.45 1.90 10.87 13.75 49.98 100.00 136.31 25.78
04/07/2016 07:13:22 210.07 213.96 211.78 1.93 10.92 13.81 49.98 100.00 136.28 25.85
04/07/2016 07:03:22 211.84 215.53 213.76 1.93 11.11 13.92 49.98 100.00 136.28 25.85
04/07/2016 06:53:21 212.42 215.81 214.09 1.90 10.86 13.69 49.98 100.00 136.28 25.85
04/07/2016 06:43:21 212.89 217.25 214.89 1.96 11.43 14.24 49.98 100.00 136.28 25.86
04/07/2016 06:33:21 212.31 219.00 215.45 1.90 10.97 13.89 49.98 100.00 136.28 25.88
04/07/2016 06:23:21 211.18 214.84 212.48 1.84 10.14 13.09 49.98 100.00 136.28 25.88
04/07/2016 06:13:21 210.51 215.56 214.54 1.84 10.20 13.19 49.98 100.00 136.28 25.89
04/07/2016 06:03:21 212.84 216.45 214.64 1.84 10.18 13.22 49.98 100.00 136.28 25.91
04/07/2016 05:53:21 213.25 217.21 214.57 1.84 10.19 13.21 49.98 100.00 136.25 25.93
04/07/2016 05:43:21 213.81 216.53 215.64 1.90 10.94 13.77 49.98 100.00 136.25 25.95
04/07/2016 05:33:21 215.29 217.78 215.43 1.90 10.95 13.84 49.98 100.00 136.25 25.98
04/07/2016 05:23:21 216.03 217.75 217.34 1.93 11.11 14.07 49.98 100.00 136.25 26.03
04/07/2016 05:13:21 215.70 217.54 217.39 1.90 10.99 13.90 49.98 100.00 136.21 26.08
04/07/2016 05:03:21 216.51 217.79 216.92 1.90 10.91 13.82 49.98 100.00 136.25 26.03
04/07/2016 04:53:21 215.84 217.95 217.51 1.90 10.91 13.86 50.06 100.00 136.25 26.05
04/07/2016 04:43:21 216.81 217.92 217.82 2.12 12.95 15.62 49.98 100.00 136.21 26.05
04/07/2016 04:33:21 216.65 217.89 217.60 1.93 11.39 14.25 49.98 100.00 136.21 26.06
04/07/2016 04:23:21 216.98 218.17 217.51 1.96 11.38 14.28 49.98 100.00 136.21 26.08
04/07/2016 04:13:21 217.39 218.32 218.15 1.90 11.01 13.91 49.98 100.00 136.21 26.10
04/07/2016 04:03:21 216.68 218.25 217.65 1.81 10.14 13.34 49.98 100.00 136.21 26.12
04/07/2016 03:53:21 217.51 218.26 218.04 1.84 10.22 13.41 49.98 100.00 136.21 26.14
04/07/2016 03:43:21 216.92 218.32 217.93 1.84 10.20 13.41 49.98 100.00 136.21 26.16
04/07/2016 03:33:21 216.35 218.17 217.68 1.84 10.14 13.38 49.98 100.00 136.21 26.18
04/07/2016 03:23:21 216.60 217.96 217.68 1.81 10.17 13.37 49.98 100.00 136.18 26.21
04/07/2016 03:13:21 216.59 218.01 217.45 1.84 10.19 13.37 49.98 100.00 136.18 26.27
04/07/2016 03:03:21 216.87 218.31 217.82 1.84 10.21 13.40 49.98 100.00 136.15 26.32
04/07/2016 02:53:21 216.60 217.84 217.59 1.84 10.22 13.39 49.98 100.00 136.15 26.36
04/07/2016 02:43:20 216.42 217.87 217.62 1.84 10.21 13.38 49.98 100.00 136.15 26.33
04/07/2016 02:33:20 216.04 217.81 217.46 1.84 10.23 13.37 49.98 100.00 136.15 26.35
04/07/2016 02:23:20 216.18 217.64 217.42 1.84 10.21 13.37 49.98 100.00 136.15 26.39
04/07/2016 02:13:20 216.35 217.65 217.09 1.84 10.21 13.36 49.98 100.00 136.15 26.39
04/07/2016 02:03:20 216.28 217.32 217.14 1.84 10.23 13.36 49.98 100.00 136.15 26.42
04/07/2016 01:53:20 216.35 217.93 217.01 1.84 10.19 13.35 49.98 100.00 136.12 26.46
04/07/2016 01:43:20 216.06 217.78 217.54 1.84 10.19 13.37 50.06 100.00 136.12 26.50
04/07/2016 01:33:20 216.48 217.50 217.21 1.81 10.11 13.33 49.98 100.00 136.12 26.53
04/07/2016 01:23:20 214.84 217.57 217.00 1.81 10.18 13.33 50.06 100.00 136.12 26.58
04/07/2016 01:13:20 214.12 217.51 215.73 1.84 10.21 13.28 49.98 100.00 136.09 26.66
04/07/2016 01:03:20 215.57 217.73 216.81 1.84 10.17 13.32 50.06 100.00 136.06 26.71
04/07/2016 00:53:20 215.53 218.17 217.25 1.84 10.18 13.35 50.06 100.00 136.09 26.69
04/07/2016 00:43:20 214.89 217.67 217.32 1.81 10.14 13.34 49.98 100.00 136.06 26.71
04/07/2016 00:33:20 214.65 217.82 216.81 1.81 10.12 13.31 49.98 100.00 136.06 26.75
04/07/2016 00:23:20 214.85 217.46 216.29 1.84 10.31 13.30 50.06 100.00 136.06 26.79
04/07/2016 00:13:20 214.73 218.25 216.57 1.84 10.20 13.32 49.98 100.00 136.06 26.83
04/07/2016 00:03:20 214.51 218.62 216.59 1.81 10.13 13.26 49.98 100.00 136.03 26.89
04/06/2016 23:53:20 214.43 217.78 216.92 1.84 10.19 13.34 49.98 100.00 136.03 26.94
04/06/2016 23:43:20 214.17 217.62 216.23 1.81 10.16 13.25 49.98 100.00 136.00 27.02
04/06/2016 23:33:20 213.07 218.03 217.37 1.84 10.20 13.37 49.98 100.00 136.00 27.10
04/06/2016 23:23:20 214.64 218.26 216.06 1.84 10.20 13.28 49.98 100.00 136.06 26.83
04/06/2016 23:13:20 214.89 218.29 217.51 1.84 10.33 13.42 50.06 100.00 135.96 27.14
04/06/2016 23:03:20 213.70 218.35 215.51 1.81 10.15 13.23 49.98 100.00 135.96 27.18
04/06/2016 22:53:20 213.00 218.23 216.26 1.84 10.18 13.31 49.98 100.00 135.96 27.24
04/06/2016 22:43:20 212.28 216.75 215.40 1.84 10.14 13.24 49.98 100.00 135.93 27.30
04/06/2016 22:33:19 213.51 217.57 216.00 1.81 10.14 13.26 50.06 100.00 135.93 27.37
04/06/2016 22:23:19 210.75 216.67 215.32 1.81 10.16 13.21 49.98 100.00 135.90 27.46
04/06/2016 22:13:19 210.98 215.78 213.60 1.84 10.19 13.14 49.98 100.00 135.87 27.53
04/06/2016 22:03:19 212.43 215.87 214.35 1.81 10.18 13.15 49.98 100.00 135.87 27.54
04/06/2016 21:53:19 210.09 216.31 215.59 1.84 10.16 13.26 49.98 100.00 135.87 27.60
04/06/2016 21:43:19 211.00 214.78 213.17 1.84 10.12 13.11 49.98 100.00 135.84 27.67
04/06/2016 21:33:19 210.06 214.10 213.67 1.84 10.16 13.14 49.98 100.00 135.84 27.75
04/06/2016 21:23:19 210.56 216.82 212.42 1.84 10.09 13.07 49.98 100.00 135.81 27.84
04/06/2016 21:13:19 212.71 217.20 214.03 1.84 10.14 13.17 49.98 100.00 135.78 27.95
04/06/2016 21:03:19 212.87 217.17 215.57 1.84 10.19 13.24 49.98 100.00 135.78 28.01
04/06/2016 20:53:19 212.98 216.84 215.00 1.81 10.16 13.19 49.98 100.00 135.75 28.07
04/06/2016 20:43:19 212.57 216.00 213.87 1.84 10.10 13.14 49.98 100.00 135.75 28.14
04/06/2016 20:33:19 211.01 216.06 214.34 1.84 10.14 13.19 49.98 100.00 135.71 28.23
04/06/2016 20:23:19 211.50 215.90 215.21 1.84 10.14 13.23 49.98 100.00 135.68 28.32
04/06/2016 20:13:19 211.06 216.37 213.73 1.84 10.12 13.15 49.98 100.00 135.65 28.46
04/06/2016 20:03:19 211.85 216.07 214.73 1.84 10.21 13.21 50.06 100.00 135.65 28.55
04/06/2016 19:53:19 210.21 215.95 213.93 1.84 10.18 13.16 50.06 100.00 135.62 28.62
04/06/2016 19:43:19 210.65 214.67 213.98 1.84 10.17 13.16 49.98 100.00 135.59 28.74
04/06/2016 19:33:19 209.34 213.93 213.32 1.84 10.18 13.13 49.98 100.00 135.56 28.85
04/06/2016 19:23:19 209.62 213.48 210.46 1.84 10.19 12.95 49.98 100.00 135.53 29.00
04/06/2016 19:13:19 208.28 212.96 211.37 1.84 10.20 13.02 49.98 100.00 135.50 29.16
04/06/2016 19:03:19 207.28 212.64 210.84 1.93 10.85 13.67 49.98 100.00 135.53 29.03
04/06/2016 18:53:19 209.10 213.18 209.06 1.93 10.89 13.62 49.98 100.00 135.43 29.43
04/06/2016 18:43:19 209.92 214.01 212.40 1.93 10.95 13.73 49.98 100.00 135.40 29.60
04/06/2016 18:33:19 209.92 214.43 213.04 1.90 10.88 13.66 49.98 100.00 135.37 29.75
04/06/2016 18:23:19 210.12 215.09 212.31 1.90 10.94 13.69 49.98 100.00 135.37 29.74
04/06/2016 18:13:19 210.23 214.64 211.65 1.93 10.98 13.75 49.98 100.00 135.37 29.73
04/06/2016 18:03:18 207.70 214.28 212.59 1.90 10.90 13.72 49.98 100.00 135.37 29.74
04/06/2016 17:53:18 209.75 213.71 211.89 1.93 11.04 13.86 49.98 100.00 135.37 29.71
04/06/2016 17:43:18 209.37 215.51 211.03 1.96 11.14 13.87 49.98 100.00 135.37 29.66