Two SUVTP15KH4B4S in Parrallel with Dual Utility Supplies - How?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Two SUVTP15KH4B4S in Parrallel with Dual Utility Supplies - How?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
123
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 06:04 AM . Last Modified: ‎2024-03-19 12:22 AM

0 Likes
3
772
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:04 AM . Last Modified: ‎2024-03-19 12:22 AM

Two SUVTP15KH4B4S in Parrallel with Dual Utility Supplies - How?

Hi,

Sorry in advance if this question has been covered but I couldn't find something similar on the forums at the moment. We have two of these http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SUVTP15KH4B4Scurrently one is connected and in operation and has been for a couple of years. it is a 3 phase UPS on a single utility supply powering our small server room.

The Questions:

1. We'd like to add UPS redundancy by connecting up another identical UPS in parallel or in some other way to allow a single UPS to fail but the load to continue. How might we do this, what are the options?

(Note: we only have a 10Kva load (or thereabouts) so we just need the second UPS as redundancy i.e. N+1, however we have heard it can do 2N so both are active at the same time, and in the event of failure one or the other takes the full load.)

2. We'd like to add utility power redundancy by adding another utility supply to supply both UPSes, so if a utility supply was to fail, both (or one) UPS continues to run (without shutting the servers down with PowerChute) how might this be done, what are the options?

3. How are all the servers connected to both the UPSes? I.e. how do I connect them up so that a single utility supply or single UPS failure doesn't take down all the connected equipment?

4. Otherwise, who at APC or Schneider do I need to speak to get some consultancy time to design a solution?


Thank you for any help you might have.

Thanks


Tristan

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 06:04 AM . Last Modified: ‎2024-03-19 12:22 AM

0 Likes
0
771
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:04 AM . Last Modified: ‎2024-03-19 12:22 AM

1. Can the whole system work with a single input to each UPS? but those single inputs come from an external switch panel which is using two inputs. I.e. there is some site switch gear in front of the UPS that switches between input 1 and input 2 (i.e whichever is live) and then always delivers a working single input to both UPSes through the maintenance bypass panel (unless a grid power failure takes both inputs out)?

The reason I ask this is we are looking to have a generator socket as another input, but this would only be temporary power supply in the event of a very long power outage, so in reality we'd want 3 inputs, where input 3 is a generator socket. Which is why I ask about having some site switching gear that is external to the maintenance bypass panel and the UPSes. We'd also be running air conditioning (not off the UPS) that we'd want to have dual input too, so it kind of points to external input switching to be required external to UPS to give us this. Then just a single input to the two UPS.

Yes. The UPS's come with jumpers between the bypass input and the mains input, so if you were to use only 1 source with no external bypass feed then you would leave the jumpers installed.

2. Yes, i'd stumbled across the maintenance service bypass panel: SBPAR10K20H-WP, didn't know these could be customised though, I couldn't find that part code: QPBL78374 for the customisation? I assume this is something we need to ask for when we order, rather than find on the website?

The part I actually quoted to you is a part that is put together by our configuration team in Denmark. In order to be able to purchase one of these, your sales rep will need to have a quotation created by that Danish team. No need for this step if you are purchasing an off the shelf product.

Also how does the maintenance service bypass panel avoid back feeding the other UPS, i.e. one UPS is active and supplying the load, the other UPS is off, how does it stop this power going back, is this done by the maintenance service bypass panel itself?

No. The UPS is designed in such a way that the path back through the UPS is opened in the event of a fault developing. 

Further technical information can be found here: http://www.apcmedia.com/salestools/ALEX-73YKER/ALEX-73YKER_R2_EN.pdf

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 06:04 AM . Last Modified: ‎2024-03-19 12:22 AM

0 Likes
0
771
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:04 AM . Last Modified: ‎2024-03-19 12:22 AM

Hi Tristan,

I asked our EMEA support for some assistance since I am based in NAM and unfamiliar with this unit. Here is what they provided to me.

1. We'd like to add UPS redundancy by connecting up another identical UPS in parallel or in some other way to allow a single UPS to fail but the load to continue. How might we do this, what are the options?

(Note: we only have a 10Kva load (or thereabouts) so we just need the second UPS as redundancy i.e. N+1, however we have heard it can do 2N so both are active at the same time, and in the event of failure one or the other takes the full load.)

From the installation manual (http://www.apcmedia.com/salestools/AHIE-7WCHJU/AHIE-7WCHJU_R1_EN.pdf ) (page 11) a diagram shows 2 X UPS's configured in parallel:

1653_suvt.jpg

The customer will require an additional component, the maintenance service bypass panel: SBPAR10K20H-WP. There will also be additional work involved by an APC Field Service Engineer such as removing the bypass switch from each of the UPS's in question. It should be noted that this SBP is an off the shelf solution and does not incorporate the switches (as seen above) Q1 or Q5. If the customer would prefer to have a SBP with these switches installed within the SBP, then a custom SBP can be created and the part number required is QPBL78374.....this would make wiring the installation simpler. Otherwise the Q1 & Q5 breakers will have to be provided external to the SBP and UPS.

2. We'd like to add utility power redundancy by adding another utility supply to supply both UPSes, so if a utility supply was to fail, both (or one) UPS continues to run (without shutting the servers down with PowerChute) how might this be done, what are the options?

The SUVT UPS can accommodate 2 utility supplies. Again referring to the installation manual, you can clearly see the points at which the electrical connections should be made for Mains 1 & Mains 2. In the diagram above the mains 2 is connected to the Q5B breakers. In the event of a power failure on mains 1, the UPS would go to battery operation until low DC shutdown.....that is if it is not configured to go to bypass operation when it gets to low battery. If it is configured to go to bypass when it gets to low battery then the load will be powered by mains 2 when the UPS transfers to bypass operation.

3. How are all the servers connected to both the UPSes? I.e. how do I connect them up so that a single utility supply or single UPS failure doesn't take down all the connected equipment?

The fact that the UPS's are working in parallel means that if one UPS is completely removed from the system the load will continue to be powered from the other UPS (provided the load does not exceed the capacity of the UPS in which case it would go to bypass to support it). In the diagram above, Q2A & Q2B are the output breakers on the bypass panel from each of the UPS's. If one of these is opened the load will not suffer any ill effects. Likewise if either of the UPS's fail the load will still continue to be powered by the other UPS.

4. Otherwise, who at APC or Schneider do I need to speak to get some consultancy time to design a solution?

If you feel the need to speak to somebody regarding designing a solution it is best to call our local support number (0800 2799254) who can best direct your call to either technical sales or technical support.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-26 06:04 AM . Last Modified: ‎2024-03-19 12:22 AM

0 Likes
0
771
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:04 AM . Last Modified: ‎2024-03-19 12:22 AM

Okay that's great thank you, it all seems to make more sense now.

Just a couple of points to clarify.

1. Can the whole system work with a single input to each UPS? but those single inputs come from an external switch panel which is using two inputs. I.e. there is some site switch gear in front of the UPS that switches between input 1 and input 2 (i.e whichever is live) and then always delivers a working single input to both UPSes through the maintenance bypass panel (unless a grid power failure takes both inputs out)?

The reason I ask this is we are looking to have a generator socket as another input, but this would only be temporary power supply in the event of a very long power outage, so in reality we'd want 3 inputs, where input 3 is a generator socket. Which is why I ask about having some site switching gear that is external to the maintenance bypass panel and the UPSes. We'd also be running air conditioning (not off the UPS) that we'd want to have dual input too, so it kind of points to external input switching to be required external to UPS to give us this. Then just a single input to the two UPS.

2. Yes, i'd stumbled across the maintenance service bypass panel: SBPAR10K20H-WP, didn't know these could be customised though, I couldn't find that part code: QPBL78374 for the customisation? I assume this is something we need to ask for when we order, rather than find on the website?


Also how does the maintenance service bypass panel avoid back feeding the other UPS, i.e. one UPS is active and supplying the load, the other UPS is off, how does it stop this power going back, is this done by the maintenance service bypass panel itself?

Many thanks


Tristan

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 06:04 AM . Last Modified: ‎2024-03-19 12:22 AM

0 Likes
0
772
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 06:04 AM . Last Modified: ‎2024-03-19 12:22 AM

1. Can the whole system work with a single input to each UPS? but those single inputs come from an external switch panel which is using two inputs. I.e. there is some site switch gear in front of the UPS that switches between input 1 and input 2 (i.e whichever is live) and then always delivers a working single input to both UPSes through the maintenance bypass panel (unless a grid power failure takes both inputs out)?

The reason I ask this is we are looking to have a generator socket as another input, but this would only be temporary power supply in the event of a very long power outage, so in reality we'd want 3 inputs, where input 3 is a generator socket. Which is why I ask about having some site switching gear that is external to the maintenance bypass panel and the UPSes. We'd also be running air conditioning (not off the UPS) that we'd want to have dual input too, so it kind of points to external input switching to be required external to UPS to give us this. Then just a single input to the two UPS.

Yes. The UPS's come with jumpers between the bypass input and the mains input, so if you were to use only 1 source with no external bypass feed then you would leave the jumpers installed.

2. Yes, i'd stumbled across the maintenance service bypass panel: SBPAR10K20H-WP, didn't know these could be customised though, I couldn't find that part code: QPBL78374 for the customisation? I assume this is something we need to ask for when we order, rather than find on the website?

The part I actually quoted to you is a part that is put together by our configuration team in Denmark. In order to be able to purchase one of these, your sales rep will need to have a quotation created by that Danish team. No need for this step if you are purchasing an off the shelf product.

Also how does the maintenance service bypass panel avoid back feeding the other UPS, i.e. one UPS is active and supplying the load, the other UPS is off, how does it stop this power going back, is this done by the maintenance service bypass panel itself?

No. The UPS is designed in such a way that the path back through the UPS is opened in the event of a fault developing. 

Further technical information can be found here: http://www.apcmedia.com/salestools/ALEX-73YKER/ALEX-73YKER_R2_EN.pdf

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of