Trouble shooting SYTF2

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Trouble shooting SYTF2
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-25 10:47 PM . Last Modified: ‎2024-03-19 03:29 AM

0 Likes
2
576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 10:47 PM . Last Modified: ‎2024-03-19 03:29 AM

Trouble shooting SYTF2

This unit does not appear to work. There is nothing obvious on the exterior. Are there any tests I can do exterior or interior to try and get some idea of what might be wrong.

Mike

Labels
  • Labels:
  • Server Room & Data Center Design Best Practices
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-25 10:47 PM . Last Modified: ‎2024-03-19 03:29 AM

0 Likes
0
576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 10:47 PM . Last Modified: ‎2024-03-19 03:29 AM

Found the problem, simple fix for once.

One of the leads had come off internally. It appears that it may have been a bit loose right from the factory. I say this because I could see the blackness of where it must have arched until it finally popped right off of the connector.

I put it back on making sure that it was in as far as it could go, fired everything back up and it all went up no problems.

Now, to see if anyone replied to my asking if there are any 240VAC to 208VAC step-down models made by APC :).


Mike

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-25 10:47 PM . Last Modified: ‎2024-03-19 03:29 AM

0 Likes
0
576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 10:47 PM . Last Modified: ‎2024-03-19 03:29 AM

oh boy, so you got it this and it doesnt work? you should be able to just plug it in and then get output from the outlets? check the input circuit breaker if it has one near the input cord and then then the outlet breakers. that is all you can check really..of course make sure it has good input voltage from your UPS 😉

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-25 10:47 PM . Last Modified: ‎2024-03-19 03:29 AM

0 Likes
0
577
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 10:47 PM . Last Modified: ‎2024-03-19 03:29 AM

Found the problem, simple fix for once.

One of the leads had come off internally. It appears that it may have been a bit loose right from the factory. I say this because I could see the blackness of where it must have arched until it finally popped right off of the connector.

I put it back on making sure that it was in as far as it could go, fired everything back up and it all went up no problems.

Now, to see if anyone replied to my asking if there are any 240VAC to 208VAC step-down models made by APC :).


Mike

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of