Timers or scheduling equipment shutdowns and start ups

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Timers or scheduling equipment shutdowns and start ups
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 04:58 AM . Last Modified: β€Ž2024-03-18 03:55 AM

0 Likes
3
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 04:58 AM . Last Modified: β€Ž2024-03-18 03:55 AM

Timers or scheduling equipment shutdowns and start ups

We have a wiring closet that has about a 1/2 dozen switches that runs fairly warm during business hours. After hours our facilities department turns off the air conditioning which only makes the room hot from 11PM to 7AM. This is less than ideal and will likely shorten the lifespan of the switches in that closet. We could put the switches on simple timers but our desktop support group runs maintenance in the middle of the night.

Is there an APC product that can schedule turning off the power outlets as well as turning them back on? Ideally this product would allow for different schedules on different days or even multiple shutdowns and power ups in a day.

thank you.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 04:58 AM . Last Modified: β€Ž2024-03-18 03:54 AM

0 Likes
0
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 04:58 AM . Last Modified: β€Ž2024-03-18 03:54 AM

Thanks but that all seems to be shut down and reboot related. We will need something more like a timer to power off/on all of the switches in the closet

Monday through Saturday
2AM: turn power on: PC updates start
3AM: turn power off, End of PC maintenance
6AM: turn power on: Start of business day
10PM: turn power off: End of business day
Sunday: off all day.

Maybe we could set up something with environmental monitoring but that would be less predictable. Doing a network based shutdown might be ok but how do you turn on the LAN switches remotely when the network is what we just turned off? πŸ™‚

I am also going to look into industrial rated switches that may handle the heat better.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 04:58 AM . Last Modified: β€Ž2024-03-18 03:55 AM

0 Likes
0
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 04:58 AM . Last Modified: β€Ž2024-03-18 03:55 AM

We have a wiring closet that has about a 1/2 dozen switches that runs fairly warm during business hours. After hours our facilities department turns off the air conditioning which only makes the room hot from 11PM to 7AM. This is less than ideal and will likely shorten the lifespan of the switches in that closet. We could put the switches on simple timers but our desktop support group runs maintenance in the middle of the night.

Is there an APC product that can schedule turning off the power outlets as well as turning them back on? Ideally this product would allow for different schedules on different days or even multiple shutdowns and power ups in a day.

thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: β€Ž2021-06-28 04:58 AM . Last Modified: β€Ž2024-03-18 03:54 AM

0 Likes
0
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 04:58 AM . Last Modified: β€Ž2024-03-18 03:54 AM

You can use a Switched Rack PDU for this purpose. You can set up a one-time, daily, or weekly event for various actions such as "off immediate, off delayed, on immediate, reboot", etc. There can be more than one event a day, and you can also customize which outlets receive these commands. You can also make outlet groups among more than one PDU.

An alternative would be using a network card in a UPS. This would allow for general UPS shutdowns, and if you get an environmental card, it will support shutdowns based on temperature alarms. The latter feature will require a PC that is capable of running our PowerChute Network Shutdown software (compatible with the majority of Windows Versions, including 2008, Vista, Win7, and Hyper-V).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 04:58 AM . Last Modified: β€Ž2024-03-18 03:54 AM

0 Likes
0
986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 04:58 AM . Last Modified: β€Ž2024-03-18 03:54 AM

Thanks but that all seems to be shut down and reboot related. We will need something more like a timer to power off/on all of the switches in the closet

Monday through Saturday
2AM: turn power on: PC updates start
3AM: turn power off, End of PC maintenance
6AM: turn power on: Start of business day
10PM: turn power off: End of business day
Sunday: off all day.

Maybe we could set up something with environmental monitoring but that would be less predictable. Doing a network based shutdown might be ok but how do you turn on the LAN switches remotely when the network is what we just turned off? πŸ™‚

I am also going to look into industrial rated switches that may handle the heat better.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore