The APC UPS 3000 showing a P.17 fault code indicates a bypass relay weld error

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • The APC UPS 3000 showing a P.17 fault code indicates a bypass relay weld error
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
123
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
chargr
chargr
Cadet

Posted: ‎2025-06-20 06:58 AM

0 Likes
1
164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-20 06:58 AM

The APC UPS 3000 showing a P.17 fault code indicates a bypass relay weld error

We're getting a p.17 error code and alerts from the unit.  We tried to clear the code using the following procedures listed below. We suspect a power surge may have caused the problem. Since its happening again we're assuming the unit could be damaged. PLease advise

 

The APC UPS 3000 showing a P.17 fault code indicates a bypass relay weld error

 

Model

Smart-UPS 3000

Location

Unknown

 2 Critical Alarms Present

  • Green relay error.
  • The output power is turned off.

 2 Warning Alarms Present

  • The power for the main outlet group, Unswitched Group, is now turned off.
  • The power for switched outlet group 1, Outlet Group 1, is now turned off.

 

06/19/2025  12:38:21    Device      UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.      0x0135

06/19/2025  12:38:21    Device      UPS: The power for the main outlet group, Unswitched Group, is now turned off.      0x0135

06/19/2025  12:38:21    Device      UPS: Green relay error. 0x01BD

06/19/2025  12:38:20    Device      UPS: The output power is turned off.      0x0114

06/19/2025  12:38:20    Device      UPS: The graceful shutdown period has ended.    0x014F

06/19/2025  12:38:20    Device      UPS: Switched outlet group 1, Outlet Group 1, has been commanded to turn off, sequenced.  0x0174

06/19/2025  12:38:20    Device      UPS: Main outlet group, Unswitched Group, has been commanded to turn off, sequenced.      0x0174

 

 

 

 

We tried this already on 6/13/25 and 6/20/25 when the error came back that morning. 

 

  1. Clear the Fault Code
    • From the LCD menu, navigate to Diagnostics or Event Log and use the â€śClear” or “Reset” option.
    • If unsuccessful, power-cycle the UPS: fully shut down, wait 30 seconds, reconnect, and power up.
  2. Run a “Brain Dead” Reset
    • Also known as a hard reset or cold start, this clears any residual internal faults. On many models:
      • Disconnect both input & output power.
      • Remove the battery.
      • Wait ~1–2 minutes.
      • Reinstall battery, reconnect power, and restart UPS.community.se.com+1apc.com+1
  3. Inspect or Replace Bypass Relay Assembly
    • If the fault persists or recurs soon after reset, the bypass relay hardware may be physically welded.
    • Contact APC/Schneider or a certified service center for relay inspection or replacement.
  4. Test Thoroughly Post-Repair
    • After clearing the fault, perform a Full Self-Test via the LCD: confirm the unit switches cleanly and no new errors appear.
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Teken
Spock Teken
Spock

Posted: ‎2025-06-20 12:52 PM

0 Likes
0
151
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-20 12:52 PM

If the equipment is still under warranty contact APC Technical Support to initiate a RMA. If the unit is not under warranty than it really depends upon what standards your company operates under. If your company follows the most stringent ISO standards than the hardware will need to be replaced.

 

If its less stringent that you may consider shipping the hardware out to an APC Authorized Repair Facility such as https://coasttec.com/service/repair-and-return/

 

If you don't follow any ISO standards than you may consider sending the unit out to any electronics facility to have them replace all of the relays in the unit. Don't simply replace the failed welded relay because you're simply living on borrowed time!

 

Replace all of the relays and obviously have them inspect and test all of the MOV, GDT, Fuse, in the SPD circuit.

 

Questions Ask . . . đź‘Ť

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of