Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
The APC UPS 3000 showing a P.17 fault code indicates a bypass relay weld error
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-06-2006:58 AM
The APC UPS 3000 showing a P.17 fault code indicates a bypass relay weld error
We're getting a p.17 error code and alerts from the unit. We tried to clear the code using the following procedures listed below. We suspect a power surge may have caused the problem. Since its happening again we're assuming the unit could be damaged. PLease advise
The APC UPS 3000 showing a P.17 fault code indicates a bypass relay weld error
Model
Smart-UPS 3000
Location
Unknown
2 Critical Alarms Present
Green relay error.
The output power is turned off.
2 Warning Alarms Present
The power for the main outlet group, Unswitched Group, is now turned off.
The power for switched outlet group 1, Outlet Group 1, is now turned off.
06/19/2025  12:38:21    Device      UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.      0x0135
06/19/2025  12:38:21    Device      UPS: The power for the main outlet group, Unswitched Group, is now turned off.      0x0135
06/19/2025  12:38:21    Device      UPS: Green relay error. 0x01BD
06/19/2025  12:38:20    Device      UPS: The output power is turned off.      0x0114
06/19/2025  12:38:20    Device      UPS: The graceful shutdown period has ended.    0x014F
06/19/2025  12:38:20    Device      UPS: Switched outlet group 1, Outlet Group 1, has been commanded to turn off, sequenced.  0x0174
06/19/2025  12:38:20    Device      UPS: Main outlet group, Unswitched Group, has been commanded to turn off, sequenced.      0x0174
We tried this already on 6/13/25 and 6/20/25 when the error came back that morning.
Clear the Fault Code
From the LCD menu, navigate to Diagnostics or Event Log and use the “Clear” or “Reset” option.
If unsuccessful, power-cycle the UPS: fully shut down, wait 30 seconds, reconnect, and power up.
Run a “Brain Dead” Reset
Also known as a hard reset or cold start, this clears any residual internal faults. On many models:
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-06-2012:52 PM
If the equipment is still under warranty contact APC Technical Support to initiate a RMA. If the unit is not under warranty than it really depends upon what standards your company operates under. If your company follows the most stringent ISO standards than the hardware will need to be replaced.
If you don't follow any ISO standards than you may consider sending the unit out to any electronics facility to have them replace all of the relays in the unit. Don't simply replace the failed welded relay because you're simply living on borrowed time!
Replace all of the relays and obviously have them inspect and test all of the MOV, GDT, Fuse, in the SPD circuit.