Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-06-20 06:58 AM
We're getting a p.17 error code and alerts from the unit. We tried to clear the code using the following procedures listed below. We suspect a power surge may have caused the problem. Since its happening again we're assuming the unit could be damaged. PLease advise
The APC UPS 3000 showing a P.17 fault code indicates a bypass relay weld error
Model
Smart-UPS 3000
Location
Unknown
2 Critical Alarms Present
2 Warning Alarms Present
06/19/2025  12:38:21    Device      UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.      0x0135
06/19/2025  12:38:21    Device      UPS: The power for the main outlet group, Unswitched Group, is now turned off.      0x0135
06/19/2025  12:38:21    Device      UPS: Green relay error. 0x01BD
06/19/2025  12:38:20    Device      UPS: The output power is turned off.      0x0114
06/19/2025  12:38:20    Device      UPS: The graceful shutdown period has ended.    0x014F
06/19/2025  12:38:20    Device      UPS: Switched outlet group 1, Outlet Group 1, has been commanded to turn off, sequenced.  0x0174
06/19/2025  12:38:20    Device      UPS: Main outlet group, Unswitched Group, has been commanded to turn off, sequenced.      0x0174
We tried this already on 6/13/25 and 6/20/25 when the error came back that morning.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-06-20 12:52 PM
If the equipment is still under warranty contact APC Technical Support to initiate a RMA. If the unit is not under warranty than it really depends upon what standards your company operates under. If your company follows the most stringent ISO standards than the hardware will need to be replaced.
If its less stringent that you may consider shipping the hardware out to an APC Authorized Repair Facility such as https://coasttec.com/service/repair-and-return/
If you don't follow any ISO standards than you may consider sending the unit out to any electronics facility to have them replace all of the relays in the unit. Don't simply replace the failed welded relay because you're simply living on borrowed time!
Replace all of the relays and obviously have them inspect and test all of the MOV, GDT, Fuse, in the SPD circuit.