Testing Refurbished SmartUPS 3000 RM XL

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Testing Refurbished SmartUPS 3000 RM XL
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:28 PM . Last Modified: ‎2024-03-14 04:28 AM

0 Likes
1
785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:28 PM . Last Modified: ‎2024-03-14 04:28 AM

Testing Refurbished SmartUPS 3000 RM XL

I recently had 12 SmartUPS 3000 RM XL's refurbished. They do not have network cards. What would be a good test to determine if they are runnnig like a new UPS? I only have the free version of Powerchute installed on a laptop and can see certain statistics but would like to know what people think is the most important stats or tests to run.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:28 PM . Last Modified: ‎2024-03-14 04:28 AM

0 Likes
0
785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:28 PM . Last Modified: ‎2024-03-14 04:28 AM

Bill,

Do you see any abnormal lights in the front of the UPS? If the front lights show normal indication, then it means that the unit is fine and ready to be used. The unit performs a self test at start up and every 14 days to check its battery integrity. You can also initiate a self test to make sure if the batteries are in the unit are good. You can either perform the Self test through Management Software or Manually. To perform the Self test manually to check the battery condition, press and hold the on/Test button until you hear two "chirps" with some percentage of load attached. You may now release the button.
After pressing the button, you will observe the following events:
1. The green On Line indicator will flash.
2. The yellow On Battery indicator will light while the battery test is performed.

If the UPS passes the Self-Test, the green On Line indicator will be lit and solid. If it fails the test, the red Replace Battery indicator will be lit as well as the green On Line LED. If the UPS fails the test, then the batteries need to be replaced.

If the unit passes the self test, I would verify if the run time of the UPS which can be seen on Management Software is same as the expected run time.
Click on the below link to view APC Smart UPS runtime chart:
http://www.apc.com/products/runtime_for_extendedruntime.cfm?upsfamily=164

If the UPS front lights and the Management Software show that everything is normal, then the unit is ready to be used to protect your equipment.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:28 PM . Last Modified: ‎2024-03-14 04:28 AM

0 Likes
0
786
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:28 PM . Last Modified: ‎2024-03-14 04:28 AM

Bill,

Do you see any abnormal lights in the front of the UPS? If the front lights show normal indication, then it means that the unit is fine and ready to be used. The unit performs a self test at start up and every 14 days to check its battery integrity. You can also initiate a self test to make sure if the batteries are in the unit are good. You can either perform the Self test through Management Software or Manually. To perform the Self test manually to check the battery condition, press and hold the on/Test button until you hear two "chirps" with some percentage of load attached. You may now release the button.
After pressing the button, you will observe the following events:
1. The green On Line indicator will flash.
2. The yellow On Battery indicator will light while the battery test is performed.

If the UPS passes the Self-Test, the green On Line indicator will be lit and solid. If it fails the test, the red Replace Battery indicator will be lit as well as the green On Line LED. If the UPS fails the test, then the batteries need to be replaced.

If the unit passes the self test, I would verify if the run time of the UPS which can be seen on Management Software is same as the expected run time.
Click on the below link to view APC Smart UPS runtime chart:
http://www.apc.com/products/runtime_for_extendedruntime.cfm?upsfamily=164

If the UPS front lights and the Management Software show that everything is normal, then the unit is ready to be used to protect your equipment.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore