Testing Email Notifications
I just installed a few of these and have setup Email Notifications within the smart connect web portal but I don't see any means of testing the notification to ensure it is working correctly and that my email isn't marking it as Spam/Junk.
There is not a test option. You can create an on battery event that will send an e-mail by switching the UPS to battery. You should see an e-mail within a minute or so depending on how responsive your SMTP system is.