Symmetra RM Full 6kva output Hit 101% overload

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra RM Full 6kva output Hit 101% overload
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
121
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:56 AM . Last Modified: ‎2024-03-13 11:38 PM

0 Likes
2
618
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:56 AM . Last Modified: ‎2024-03-13 11:38 PM

Symmetra RM Full 6kva output Hit 101% overload

I have recently purchased 2 Symmetra RM 6kv UPS with step-down converter and working on getting things going. I do have each of them wired to a dedicate 30 amp 240 circuit with the power cable but I hit the 101% and I wasn't expecting that. I do have 4 - 2kva power modules in each one. I used killawatt on each 15 amp connection and should be at 3600 watts and I hit 101% and the overload. At 2700 watts i'm at about 87%. Did I hit the overload on the 30 amp input or on the stepdown converter.

There is a KB article about using a 40 amp breaker with and hardwire you can get the full 6kva.

http://emea-en.apc.com/app/answers/detail/a_id/1142

My question is what is the limiting factor with the full 6kva setup. will I run into overload on a single step-down converter since it's only a 30 cable. Can I have two stepdown converters.

Thanks in advance.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:56 AM . Last Modified: ‎2024-03-13 11:38 PM

0 Likes
0
618
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:56 AM . Last Modified: ‎2024-03-13 11:38 PM

I have recently purchased 2 Symmetra RM 6kv UPS with step-down converter and working on getting things going. I do have each of them wired to a dedicate 30 amp 240 circuit with the power cable but I hit the 101% and I wasn't expecting that. I do have 4 - 2kva power modules in each one. I used killawatt on each 15 amp connection and should be at 3600 watts and I hit 101% and the overload. At 2700 watts i'm at about 87%. Did I hit the overload on the 30 amp input or on the stepdown converter.

There is a KB article about using a 40 amp breaker with and hardwire you can get the full 6kva.

http://emea-en.apc.com/app/answers/detail/a_id/1142

My question is what is the limiting factor with the full 6kva setup. will I run into overload on a single step-down converter since it's only a 30 cable. Can I have two stepdown converters.

Thanks in advance.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:56 AM . Last Modified: ‎2024-03-13 11:38 PM

0 Likes
0
618
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:56 AM . Last Modified: ‎2024-03-13 11:38 PM

This link helps for multiple 30 amp plugs, I may need to go that direction because I can't use the 20 amp 220 on there now.

I didn't trip the 30amp breaker just hit the overload at 101%. I didn't check what the output was but I should have been at 3600 watt. Which I thought I had a lot more room then that. I am using #6 wire so I could go to 40amp.

Maybe my math is off, but I should be able to get 5700 watts right.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:56 AM . Last Modified: ‎2024-03-13 11:38 PM

0 Likes
0
619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:56 AM . Last Modified: ‎2024-03-13 11:38 PM

I have recently purchased 2 Symmetra RM 6kv UPS with step-down converter and working on getting things going. I do have each of them wired to a dedicate 30 amp 240 circuit with the power cable but I hit the 101% and I wasn't expecting that. I do have 4 - 2kva power modules in each one. I used killawatt on each 15 amp connection and should be at 3600 watts and I hit 101% and the overload. At 2700 watts i'm at about 87%. Did I hit the overload on the 30 amp input or on the stepdown converter.

There is a KB article about using a 40 amp breaker with and hardwire you can get the full 6kva.

http://emea-en.apc.com/app/answers/detail/a_id/1142

My question is what is the limiting factor with the full 6kva setup. will I run into overload on a single step-down converter since it's only a 30 cable. Can I have two stepdown converters.

Thanks in advance.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of