Symmetra PX operational safety of tests

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra PX operational safety of tests
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
ojfsdi
Ensign ojfsdi
Ensign

Posted: ‎2021-10-20 08:01 PM . Last Modified: ‎2022-10-19 01:21 AM

0 Likes
3
1619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-20 08:01 PM . Last Modified: ‎2022-10-19 01:21 AM

Symmetra PX operational safety of tests

I inherited a PX that I was warned by the previous owner was unreliable.  It recently left our load OFFLINE! following a power outage too, see https://community.se.com/t5/Datacenter-Forum/PX-Leaving-load-offline-until-manual-startup/td-p/37259...

 

I want to do a UPS Self Test, and a Runtime Calibration, to exercise the unit and gain information on any faults discovered.

When I look at the diagnostic page on its web interface though, I see:

 

Diagnostic Tests
 
Self-Test:Failed on February 24, 2018
Calibration:Not Available on Unknown
 
Initiate:UPS Self-Test
Runtime Calibration
 

 

So.  It definitely failed last time it was run.  which was a log time ago.  And it left us in the dark recently.

 

Yet I know we've used the PX before with success to buffer power while we went on generator for a day when the utility company was doing work that took the building offline.  And since setting up logging I've gotten several notices of the UPS switching to battery and back to AC, presumably because of a momentary blink in power.

 

What are the chances of the Symmetra PX dropping load during a runtime calibtarion, or during a self-test?  Is one safer than the other?

 

If the batteries can't hold up, does it seamlessly abort the test and go to internal bypass?

 

For example:  If I ran a self-test, and isolated the battery cabinet at its DC breaker, would the PX be able to switch to bypass mode fast enough to avoid disruption of the load? 

Labels
  • Labels:
  • Datacenter UPS
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
al_buffington
Lieutenant JG al_buffington Lieutenant JG
Lieutenant JG

Posted: ‎2021-10-25 08:06 AM

0 Likes
2
1598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-25 08:06 AM

Hi.

 

The odds of dropping the load during one of these tests is remote. There is really no difference in risk between the two. The difference between the tests is related to duration and purpose. The calibration is meant to adjust the displayed runtime. The runtime value on the display requires a deep discharge of the batteries in order to update based on battery health,  For example if you had a UPS that never went to battery, or only experienced very brief outages, the runtime would display the same regardless of the age of the batteries (assuming load and # of batteries remained constant). A calibration would typically be run annually or after a full battery replacement,  It requires the charge level to be at 100% and will discharge the batteries down to 25% capacity.

 

The standard battery test will transfer the UPS to battery for up to one minute and is designed to check for battery faults.  If during either test the batteries are unable to support the load the UPS should transfer back to the inverter rather than transfer to bypass. 

 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
al_buffington
Lieutenant JG al_buffington Lieutenant JG
Lieutenant JG

Posted: ‎2021-10-25 08:06 AM

0 Likes
2
1599
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-25 08:06 AM

Hi.

 

The odds of dropping the load during one of these tests is remote. There is really no difference in risk between the two. The difference between the tests is related to duration and purpose. The calibration is meant to adjust the displayed runtime. The runtime value on the display requires a deep discharge of the batteries in order to update based on battery health,  For example if you had a UPS that never went to battery, or only experienced very brief outages, the runtime would display the same regardless of the age of the batteries (assuming load and # of batteries remained constant). A calibration would typically be run annually or after a full battery replacement,  It requires the charge level to be at 100% and will discharge the batteries down to 25% capacity.

 

The standard battery test will transfer the UPS to battery for up to one minute and is designed to check for battery faults.  If during either test the batteries are unable to support the load the UPS should transfer back to the inverter rather than transfer to bypass. 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

ojfsdi
Ensign ojfsdi
Ensign

Posted: ‎2021-10-27 06:52 PM

In response to al_buffington
0 Likes
1
1571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-27 06:52 PM

When you say "standard battery test", can you confirm that means the "UPS Self-Test" that is on the "Diagnostic Tests" screen?

 

I believe the UPS can be scheduled to perform this test autonomously every 2 weeks, which I will consider, though I'd prefer putting it on an employee calendar and having eyes on the equipment in person during the test.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

al_buffington
Lieutenant JG al_buffington Lieutenant JG
Lieutenant JG

Posted: ‎2021-10-28 05:48 AM

In response to ojfsdi
0 Likes
0
1566
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-28 05:48 AM

Hi,

 

Yes, I was referring to the self test from the diag menu. You're right that the test can be automatically set to run every two weeks, but it cannot be scheduled for a specific date/time. Many users choose to run this manually so it can be run at a desired time. I hope this clears things up. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of