Symmetra PX 80KVA Error: Cannot switch to bypass

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra PX 80KVA Error: Cannot switch to bypass
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 03:38 AM . Last Modified: ‎2024-03-19 01:42 AM

0 Likes
7
928
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:38 AM . Last Modified: ‎2024-03-19 01:42 AM

Symmetra PX 80KVA Error: Cannot switch to bypass

Hello,

Good day.

What does this error mean: *"Cannot switch to bypass; the input voltage or frequency is not within its defined limits"*
Getting this error from a Symmetra PX 80KVA unit.

Thanks

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
  • Tags:
  • bypass
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-26 03:39 AM . Last Modified: ‎2024-03-19 01:42 AM

0 Likes
0
928
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:39 AM . Last Modified: ‎2024-03-19 01:42 AM

This specific error appears at the majority of cases when a power outage has occured or if a generator has a problem(frequency or voltage irregularities due to governors or DVR faults).The meaning of this error is to warn the user/operator that if at that time the ups has an overload then it wouldn't go to bypass so it will drop the load.And of course it's perfectly normal.

Now if that error appears without any signs of power outage or voltage drop or any irregularities then you should check the static bypass module or download the MIM'S history log to help you see some more information

Message was edited by: cosarg

Message was edited by: cosarg

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 03:39 AM . Last Modified: ‎2024-03-19 01:42 AM

0 Likes
0
928
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:39 AM . Last Modified: ‎2024-03-19 01:42 AM

Hi,

I am not a three phase expert but essentially this means that if the UPS were to go to bypass, it'd probably turn off because the mains input voltage or frequency is too high or too low to go to bypass. A lot of times we see this with generators, when they fire up, because they may start putting out a really high or low voltage or a low/high frequency.

Can you find out what your input voltage and frequency is?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 03:39 AM . Last Modified: ‎2024-03-19 01:42 AM

0 Likes
0
928
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:39 AM . Last Modified: ‎2024-03-19 01:42 AM

Thanks for the reply.

Let me check the voltage and frequency input value I have and will reply back again. Just in case, is there a way
for me to adjust the settings on the UPS itself to tolerate whatever actual value I have?

Thanks agaian

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 03:39 AM . Last Modified: ‎2024-03-19 01:42 AM

0 Likes
0
928
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:39 AM . Last Modified: ‎2024-03-19 01:42 AM

I have access to a 40kVA management card and I did not see anything in there...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 03:39 AM . Last Modified: ‎2024-03-19 01:42 AM

0 Likes
0
929
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:39 AM . Last Modified: ‎2024-03-19 01:42 AM

We received the same message during a brownout during a thunderstorm this week.

from wikipedia:

Blackout
where power is lost completely. While the word "blackout" is one of the most common colloquial terms, "Load shedding" or a rolling blackout refers specifically to a controlled way of rotating available generation capacity between various districts or customers, thus avoiding wide area total blackouts.

Brownout
where the voltage level is below the normal minimum level specified for the system. Systems supplied with three-phase electric power also suffer brownouts if one or more phases are absent, at reduced voltage, or incorrectly phased. Such malfunctions are particularly damaging to electric motors. Some brownouts, called voltage reductions, are made intentionally to prevent a full power outage.

Dropout
where the loss of power is only momentary (milliseconds to seconds).

Reply

Link copied. Please paste this link to share this article on your social media post.

K-Dog_apc
Lieutenant JG K-Dog_apc
Lieutenant JG

Posted: ‎2021-06-26 03:39 AM . Last Modified: ‎2024-03-19 01:42 AM

0 Likes
0
929
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:39 AM . Last Modified: ‎2024-03-19 01:42 AM

This message is normal when there is a power outage or brown out. The unit should also show a fault light on. This does not mean there is necessarily something wrong with the UPS but that something is wrong overall. In this case the fault indicates the input voltage being low..usually zero for freq and voltage. If the outage or power event is more than a blip you will see the yellow "On Battery" light illuminated on the UPS Power View until input power returns to normal.

The message indicates you cant xfer the load to utility (go to bypass) because there is partial or no bypass voltage.

You can check input voltage from the PowerView displays on the XPDU and the UPS. Its possible a voltage sense board can go bad or need to be calibrated if your input voltage is actually within limits.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 03:39 AM . Last Modified: ‎2024-03-19 01:42 AM

0 Likes
0
929
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:39 AM . Last Modified: ‎2024-03-19 01:42 AM

I would suggest to check quality of the power line by a good tool like current clamp.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 03:39 AM . Last Modified: ‎2024-03-19 01:42 AM

0 Likes
0
929
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:39 AM . Last Modified: ‎2024-03-19 01:42 AM

This specific error appears at the majority of cases when a power outage has occured or if a generator has a problem(frequency or voltage irregularities due to governors or DVR faults).The meaning of this error is to warn the user/operator that if at that time the ups has an overload then it wouldn't go to bypass so it will drop the load.And of course it's perfectly normal.

Now if that error appears without any signs of power outage or voltage drop or any irregularities then you should check the static bypass module or download the MIM'S history log to help you see some more information

Message was edited by: cosarg

Message was edited by: cosarg

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of