Symmetra PX 30kVA: Runtime calibration canceled

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra PX 30kVA: Runtime calibration canceled
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 02:28 AM . Last Modified: ‎2024-03-19 02:20 AM

0 Likes
8
1749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:28 AM . Last Modified: ‎2024-03-19 02:20 AM

Symmetra PX 30kVA: Runtime calibration canceled

We are running a PX 1 with 3 pcs. 10kVA Power modules, extended Battery cabinet (overall 8 pcs. SYBT4).

Runtime after runtime calibration last year was 2h 3min. Load did not change since last year.

Last Monday we started runtime calibration using the display in the front of PX (not by management card).

After 1 h and 50 min. rutime calibration stopped. Info within log: Runtime calibration canceled.

After waiting 24 h and 100% charged batteries, we started  Runtime calibration again.

Rusult: Again, after 1 h and 50 min it stopped. Again the same remark in the logs: Runtime calibration canceled.

Load is allways between 36,4 and 38 %. 

What could help to finish Runtime calibration ?

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-26 02:28 AM . Last Modified: ‎2024-03-19 02:20 AM

0 Likes
0
1750
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:28 AM . Last Modified: ‎2024-03-19 02:20 AM

Hi Walter,

They are indeed standing in a cool room. We will replace the batteries soon or replace the UPS units all together. They are quite old too.

Thanks for all your info!

Regards,
Rob

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Anonymous user
Not applicable

Posted: ‎2021-06-26 02:28 AM . Last Modified: ‎2024-03-19 02:20 AM

0 Likes
0
1750
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:28 AM . Last Modified: ‎2024-03-19 02:20 AM

We have a Matrix 5000 (with 2 XR batteries connected) which does the same thing every time it runs.

A runtime calibration stops at 30% battery capacity with a remark in the log: "Device   UPS: Runtime calibration cancelled".

Is there a way to find out why this happens? The battery test says they are OK.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 02:28 AM . Last Modified: ‎2024-03-19 02:20 AM

0 Likes
0
1750
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:28 AM . Last Modified: ‎2024-03-19 02:20 AM

Meanwhile we replaced the Symmetra PX 1 with a PX2. Old PX1 is sold.....
It seems, nobody is interessted or able to help.

Rob: How old are the batteries? If they are really o.k. i would try a restart of the UPS. You can check status of batteries, using front panel of the MATRIX. 

Manual: https://excessups.com/manuals/Matrix-Manual.pdf

Section: 5.0 Operation

If there is one ore more 'bad batteries': batteries have to be changed and XR is to be resetet (if so, ask me. I will help!)

Best regards

Walter

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 02:28 AM . Last Modified: ‎2024-03-19 02:20 AM

0 Likes
0
1750
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:28 AM . Last Modified: ‎2024-03-19 02:20 AM

They are quite old, from 2010. But a battery test is always OK and physically they look fine.

We have three Matrix 5000 units and the other two have the same battery age without any problems, the calibration tests are running fine on these units.

Is there some forensic logging possible on these units to figure out what's going on?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 02:28 AM . Last Modified: ‎2024-03-19 02:20 AM

0 Likes
0
1748
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:28 AM . Last Modified: ‎2024-03-19 02:20 AM

In addition: The unit has an AP9630 NMC running with the latest firmware version.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 02:28 AM . Last Modified: ‎2024-03-19 02:20 AM

0 Likes
0
1750
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:28 AM . Last Modified: ‎2024-03-19 02:20 AM

As a local distributor for a well known battery manufacturer, i can say: 8 year old Batteries in a APC UPS are more than dead.

Look for 8 pcs. GPL12750 in your region (4 pcs. per external XR), reuse old cabeling (with the yellow Anderson connectors)  at news batteries and have runtime again at your MATRIX.

If calibration error does not disappear, restart (cold start) the MATRIX.

Is there some forensic logging possible on these units to figure out what's going on?

Post event- and data logs. Maybe, there is more information. 

Best regards

Walter

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 02:28 AM . Last Modified: ‎2024-03-19 02:20 AM

0 Likes
0
1748
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:28 AM . Last Modified: ‎2024-03-19 02:20 AM

Hi Walter,

Thanks for your reply. We are indeed amazed by the fact that they are that old and still a battery test on the Matrix says they are OK and a runtime test can last at least 1:30 with 80% load connected on a Matrix with 4 XR cells.

What is a normal lifetime of these kind of batteries?

Best regards,

Rob

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 02:28 AM . Last Modified: ‎2024-03-19 02:20 AM

0 Likes
0
1748
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:28 AM . Last Modified: ‎2024-03-19 02:20 AM

Hi Rob,

at 4 Smartcell-XR and 80 & Load, a 3000VA MATRIX should have a runtime around 6 hrs 28 min.
and a 5000VA Matrix should have 3 hrs 40 mins

Source: http://www.bomara.com/APC/matrix-ups_runtime.htm

As technican, I never trust data sheets: The higher service life in a datasheet, the cheaper are the batteries from a (cheap) manufacturer. If you should have 4 pcs. GPL12750 in your Matrix XR: Service life is up to 8 years (in a lab). When they last up to 6 or 7 years, you had luck and/or your UPS is in a cool room.

Order new batteries. Do not wait, till your batteries are dying the thermal runaway.

Best regards

Walter

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 02:28 AM . Last Modified: ‎2024-03-19 02:20 AM

0 Likes
0
1751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 02:28 AM . Last Modified: ‎2024-03-19 02:20 AM

Hi Walter,

They are indeed standing in a cool room. We will replace the batteries soon or replace the UPS units all together. They are quite old too.

Thanks for all your info!

Regards,
Rob

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore