Symmetra LX SYAF16KRMT Battery Module Fault/New Batteries

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra LX SYAF16KRMT Battery Module Fault/New Batteries
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
119
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:41 AM . Last Modified: ‎2024-03-12 11:09 PM

0 Likes
1
1241
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:41 AM . Last Modified: ‎2024-03-12 11:09 PM

Symmetra LX SYAF16KRMT Battery Module Fault/New Batteries

HI,

We have a Symmetra LX system that will not come out of bypass mode because of a "Battery Module Fault". Originally the unit said it went into bypass mode because of a system overload, Failed MIM, Failed RIM, failed Power module, and failed Battery Module. The batteries in the system were just replaced with spares this morning and the fault is still present. the MIM, RIM, and Power Modules were also replaced today. I have also attempted to go into maintenance bypass mode and restart the unit. The system diags say that all the installed batteries are in "OK" status so why is the Power Module Fault still present? how do i get the unit out of bypass? any suggestions would be awesome. Oh! and before i'm asked below you will find the info from each battery (SN's Withheld).

Battery 1   Battery 2Battery 3Battery 4

FW REV: 10

SN: N/A

FW REV: 10

SN: N/A

FW REV: 10

SN: N/A

FW REV: 10

SN: N/A

Model: SYBT5

Model: SYBT5Model: SYBT5Model: SYBT5
MFG: 03/12MFG: 11/10MFG: 08/05MFG: 08/05

-0.00 1.97 864

4000 0 28 21

-00.0 2.16 864

4000 0 27 40

-00.1 2.11 864

4000 0 26 26

-0.00 1.98 864

4000 0 24 24

11FFFT

1.00 0705.7

0800.8 0000.0

11FFFT

1.00 0705.7

0800.8 0000.0

11FFFT

1.00 0704.8

0800.4 0000.0

11FFFT

1.00 0705.5

0800.5 0000.0

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • bypass
  • power_module_fault
  • sybt5
  • symmetra_lx
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:41 AM . Last Modified: ‎2024-03-12 11:09 PM

0 Likes
0
1240
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:41 AM . Last Modified: ‎2024-03-12 11:09 PM

Was just noticing you appear to have a 50/50 mix of newer ( 2010/2012) and very old (2005) battery modules, which is not best practice and is not recommended by any UPS manufacturer. If the older cells have deteriorated and are showing higher impedance that may actually cause the system battery bus voltage to be lower than it should be.  If this were my system I would immediately pull battery 3 and 4 and see if that improves things....

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:41 AM . Last Modified: ‎2024-03-12 11:09 PM

0 Likes
0
1241
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:41 AM . Last Modified: ‎2024-03-12 11:09 PM

Was just noticing you appear to have a 50/50 mix of newer ( 2010/2012) and very old (2005) battery modules, which is not best practice and is not recommended by any UPS manufacturer. If the older cells have deteriorated and are showing higher impedance that may actually cause the system battery bus voltage to be lower than it should be.  If this were my system I would immediately pull battery 3 and 4 and see if that improves things....

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of