Symmetra LX 16000 stuck in bypass

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra LX 16000 stuck in bypass
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
cbwapc
cbwapc
Cadet

Posted: ‎2025-01-27 12:02 PM

0 Likes
1
228
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-27 12:02 PM

Symmetra LX 16000 stuck in bypass

Hi,

 

I have a Symmetra LX 16000 that has been in a strange state since we had a 30 second power outage.  During that outage, all power failed to the servers it was supplying power to, despite the fact that the batteries power should have been sufficient and the unit was not showing any faults at that time.  When the power came back, the UPS did not.  By toggling the back "System" switch, I was able to get the UPS back up and then place it into bypass mode to return power to our servers.

 

However, at that point the UPS started showing 3 critical alarms.

 

3 Critical Alarms Present

The output voltage is outside its defined limits.
A battery fault exists.
At least one faulty battery exists.

 

Additionally, the logs would report a battery failure followed quickly by a recovery and the same failure/recovery for a power module.  However, the logs would not point to a specific battery or power module, and a "status" check showed all power modules and batteries to be "OK".

 

After upgrading all firmware to the latest versions, the failures in the logs stopped, but the alarms remained.  When I tried to run a self-test, I was informed that that could not be done while the unit was in bypass mode.  When I attempted to have it leave bypass mode, the front panel shows the error:

 

"UPS unable to exit bypass due to overload or fault"

 

On the assumption that I may have some kind of "silent" failure on a module, I attempted to sequentially pull each battery and power module to see if I could clear the error and get the UPS out of bypass mode, but did have any effect. 

 

At this point, the logs are not showing any issues.

 

I feel like the next step is to have a technician come out and service the unit, but if there are any other steps I should be performing to resolve this situation before then I'd very appreciate any advice.  I'm happy to provide any files/logs.

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-01-28 01:45 AM

0 Likes
0
211
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-28 01:45 AM

Dear,

 

This error is displayed when the intelligence modules detect that the bypass contactor(s) is not in the
position that it should be in. This will only be displayed while the UPS is in bypass or after the UPS has
been in bypass. This fault would not affect the ability to transfer to maintenance bypass; however, keep
in mind that when the UPS exits maintenance bypass it initially transfers to automatic bypass before it
goes online. It is possible to drop the customers load if there is a bypass contactor fault while
attempting to exit maintenance bypass. It is recommended that you inform the customer of this risk
before attempting any troubleshooting.

 

-There are several bypass related faults that may appear in
either the IM failure sections or System failures sections
-Ensure that the intelligence modules have a serial datecode of 0840 or later. Intelligence modules
manufactured before that can cause bypass related issues. See FA157651 for details

-If the UPS is already in maintenance bypass, install the intelligence modules one at a time, cycling the
system enable switch after each one is installed.

- If possible, visually inspect the AC slide tray to see if the bypass contactor(s) is stuck or there are any
loose connections. Replace the slidetray if it is suspected that the contactor is bad.

- Bypass control and sense wires are connected to the AC slide tray and backplane via a Molex
connector. It is possible that this connection is loose or not making good contact, reseat the slide tray in
order to verify that the connection is OK. This will require a total power off of the Symmetra LX

 

so if the issue still not resolved the AC tray might need to be replaced after verifying the raw status data by the CCC team and performing the troubleshooting above

 

Regards,

 

Karim

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-01-28 01:45 AM

0 Likes
0
212
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-28 01:45 AM

Dear,

 

This error is displayed when the intelligence modules detect that the bypass contactor(s) is not in the
position that it should be in. This will only be displayed while the UPS is in bypass or after the UPS has
been in bypass. This fault would not affect the ability to transfer to maintenance bypass; however, keep
in mind that when the UPS exits maintenance bypass it initially transfers to automatic bypass before it
goes online. It is possible to drop the customers load if there is a bypass contactor fault while
attempting to exit maintenance bypass. It is recommended that you inform the customer of this risk
before attempting any troubleshooting.

 

-There are several bypass related faults that may appear in
either the IM failure sections or System failures sections
-Ensure that the intelligence modules have a serial datecode of 0840 or later. Intelligence modules
manufactured before that can cause bypass related issues. See FA157651 for details

-If the UPS is already in maintenance bypass, install the intelligence modules one at a time, cycling the
system enable switch after each one is installed.

- If possible, visually inspect the AC slide tray to see if the bypass contactor(s) is stuck or there are any
loose connections. Replace the slidetray if it is suspected that the contactor is bad.

- Bypass control and sense wires are connected to the AC slide tray and backplane via a Molex
connector. It is possible that this connection is loose or not making good contact, reseat the slide tray in
order to verify that the connection is OK. This will require a total power off of the Symmetra LX

 

so if the issue still not resolved the AC tray might need to be replaced after verifying the raw status data by the CCC team and performing the troubleshooting above

 

Regards,

 

Karim

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of