Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Symmetra LX 16000 RM battery fault - how to identify faulty battery?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra LX 16000 RM battery fault - how to identify faulty battery?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
138
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:17 AM . Last Modified: ‎2024-03-12 04:35 AM

0 Likes
0
1523
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:17 AM . Last Modified: ‎2024-03-12 04:35 AM

Symmetra LX 16000 RM battery fault - how to identify faulty battery?

I'm looking for help with Symmetra LX which is reporting a faulty battery module but I'm struggling to find which one it is that needs replaced.  There was an external power problem which the UPS logged as 'Unacceptable utility voltage rate of change', all the UPS's showed changing to battery power very briefly before changing back to mains power and running normally.  The Symmetra LX didn't return to normal and switched to bypass mode, the display shows a 'battery module fault' and to replace batteries, the web interface shows the same with two critical alerts (and no others) - Battery Fault and Replacement Battery Needed.  It shows the battery capacity at just 41% (and hasn't risen in the last couple of days) and it won't come out of bypass mode.

The unit has four batteries in the main frame and two frames attached with three batteries in each (10 in total) but the web interface shows all 10 batteries to be good and the interface on the device also shows each battery to be ok.  I've removed each battery and checked the status to see if it changed but while the unit recognised each time a battery had been removed it still showed the battery module fault each time even when all the battery modules had been removed (although that may be an error generated by the fact there are no battery modules present).  The raw data looks quite different for the second frame:

Battery Frame
Main Frame:00 0000 04/04 000F 0000 0000 0000 00 00 000.0 00.0 0000 0000
Battery Frame 1:00 0000 04/04 000F 0000 0000 0000 00 00 000.0 00.0 0000 0000
Battery Frame 2:

00 0000 03/03 0007 0000 0000 0000 00 00 077.3 -0.2 0666 1951

While I don't know what the raw status codes mean the second battery frame looks suspiciously different so I tried removing its communication cable which the main unit recognised (showing the number of battery frames had decreased) but it still showed the battery module error.  I tried swapping over the communications cables so only the other one was connected then tried removing both but the system still showed the battery module error so I'm stumped what to check next. I've found a couple of other users who sound like they've had the same issue with this unit but there were no confirmed solutions on those threads.

Any other suggestions to narrow down the faulty battery would be appreciated.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • battery_module_fault
  • replace_battery
  • symmetra_lx
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore