Symmetra 16000 shows fuel level 0%, batteries are all charged

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra 16000 shows fuel level 0%, batteries are all charged
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
138
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:33 AM . Last Modified: ‎2024-03-19 12:43 AM

0 Likes
8
953
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:33 AM . Last Modified: ‎2024-03-19 12:43 AM

Symmetra 16000 shows fuel level 0%, batteries are all charged

We have a Symmetra 16000 running at 83% load. Recently we noticed that the fuel % level was slowly dropping, even though there weren't any power events recorded. We talked to APC, and they said we might have a bad battery. We tried pulling the batteries and measuring the output voltage on the battery modules, and they were all about 135v. When we put them back in, though, it said the fuel was 0%, and it has very slowly gone up to 5%. Any ideas what might be going sideways?

Message was edited by: ssp2pro

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
  • Tags:
  • 1600
  • apc
  • battery
  • symmetra
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:34 AM . Last Modified: ‎2024-03-19 12:43 AM

0 Likes
0
953
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:34 AM . Last Modified: ‎2024-03-19 12:43 AM

Well, we pulled the batteries out one at a time, and they all measured ~135 statically. And then, when we rebooted the UPS, it went from 7% charge to 98% charge -- which tells me that they weren't actually discharged. Does anyone know where in the unit it finds that battery voltage? I wonder if it's being mis-reported.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:33 AM . Last Modified: ‎2024-03-19 12:43 AM

0 Likes
0
953
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:33 AM . Last Modified: ‎2024-03-19 12:43 AM

have you replaced these batteries recently? in general, yes sometimes a faulty battery that is leaking current can discharge very slowly and the UPS will see this and you'll see the charge drop slowly cause it thinks its on battery. it also usually indicates on the powerview front display that the UPS is on battery.

do you also see the on battery LED illuminated on the front display? also, do you have any external battery frames attached?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:33 AM . Last Modified: ‎2024-03-19 12:43 AM

0 Likes
0
953
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:33 AM . Last Modified: ‎2024-03-19 12:43 AM

The oldest battery pack is 14 months old, no external frames. We do have another Symmetra 16000, and we swapped battery packs with it. The other Symmetra showed 99% charge immediately, while the first Symmetra showed 9% charge on batteries that were fully charged.
We then waited about eight hours, and the unit was jumping between 7% and 10% charge. We put it in manual bypass and did a hard reboot of the ups. It came back up showing 8% charge. We noticed we had two green lights on the master control module, so we unclipped the display on the front, in order to be able to take the plastic cover off to get a closer look. When we plugged the front display back in, it showed 99% charge. Any ideas why?

Message was edited by: ssp2pro

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:33 AM . Last Modified: ‎2024-03-19 12:43 AM

0 Likes
0
953
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:33 AM . Last Modified: ‎2024-03-19 12:43 AM

did you replace the enter SYBATT module or the batteries inside it? Depending on that answer, I can elaborate a little more on additional possibilities.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:33 AM . Last Modified: ‎2024-03-19 12:43 AM

0 Likes
0
954
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:33 AM . Last Modified: ‎2024-03-19 12:43 AM

Well, it's happening again. The fuel level is slowly going down.
Yeah, we swapped one SYBATT with a SYBATT from another Symmetra 16000 unit we have.
I think we're going to try swapping the two panels on the units... hope it doesn't break anything else.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:33 AM . Last Modified: ‎2024-03-19 12:43 AM

0 Likes
0
954
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:33 AM . Last Modified: ‎2024-03-19 12:43 AM

is the "on battery" LED illuminated on the powerview?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:33 AM . Last Modified: ‎2024-03-19 12:43 AM

0 Likes
0
954
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:33 AM . Last Modified: ‎2024-03-19 12:43 AM

Well, we tried swapping the powerview panel, and it didn't make a difference
Nope, battery light is off.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:33 AM . Last Modified: ‎2024-03-19 12:43 AM

0 Likes
0
954
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:33 AM . Last Modified: ‎2024-03-19 12:43 AM

Vin : 204.4
Vout: 209.0
Iout: 42.7

Load w/o redundancy: 83%
Load n+1 redundancy: 82%

Freq.in : 60.00hz
Freq.out: 60.00hz

Batt V: 134.9
Batt Cap: 78%
Runtime: 00hr 06min
No. of Batts: 4
No. of Bad Batts: 0

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:34 AM . Last Modified: ‎2024-03-19 12:43 AM

0 Likes
0
954
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:34 AM . Last Modified: ‎2024-03-19 12:43 AM

Well, we pulled the batteries out one at a time, and they all measured ~135 statically. And then, when we rebooted the UPS, it went from 7% charge to 98% charge -- which tells me that they weren't actually discharged. Does anyone know where in the unit it finds that battery voltage? I wonder if it's being mis-reported.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore