SmartUPS 3000VA rack, battery depleting quickly during runtime calibration

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SmartUPS 3000VA rack, battery depleting quickly during runtime calibration
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:12 AM . Last Modified: ‎2024-03-11 03:09 AM

0 Likes
12
1307
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:12 AM . Last Modified: ‎2024-03-11 03:09 AM

SmartUPS 3000VA rack, battery depleting quickly during runtime calibration

Have a SmartUPS 3000VA rackmount here. Recently started giving a "replace battery" error.

Purchased a new APC RBC43 battery and installed. Ran a self-test but the test failed, saying one or more batteries was bad. We let it charge back to 100%, then ran the self-test again - which passed.

I noticed it was showing a 8 minute runtime with 48% load, which didn't seem right. I started a runtime calibration, and the battery dropped to under 50% in 10 seconds or less so I cancelled the runtime calibration.

Could I have another bad battery out of the box, or could something else be wrong?

Any suggestions?

Thanks!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:13 AM . Last Modified: ‎2024-03-11 03:09 AM

0 Likes
0
1306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:13 AM . Last Modified: ‎2024-03-11 03:09 AM

OK, I PMed you my address.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:12 AM . Last Modified: ‎2024-03-11 03:09 AM

0 Likes
0
1308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:12 AM . Last Modified: ‎2024-03-11 03:09 AM

If you put new batteries in, you just need to do a self test to clear a solid replace battery LED as the UPS won't do it on its own. If you did, make sure to let the batteries charge for at least a day and re-do a self test. A solid replace battery LED is not a situation where you'd be doing a calibration of any type.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:12 AM . Last Modified: ‎2024-03-11 03:09 AM

0 Likes
0
1308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:12 AM . Last Modified: ‎2024-03-11 03:09 AM

Have a SmartUPS 3000VA rackmount here. Recently started giving a "replace battery" error.

Purchased a new APC RBC43 battery and installed. Ran a self-test but the test failed, saying one or more batteries was bad. We let it charge back to 100%, then ran the self-test again - which passed.

I noticed it was showing a 8 minute runtime with 48% load, which didn't seem right. I started a runtime calibration, and the battery dropped to under 50% in 10 seconds or less so I cancelled the runtime calibration.

Could I have another bad battery out of the box, or could something else be wrong?

Any suggestions?

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:12 AM . Last Modified: ‎2024-03-11 03:09 AM

0 Likes
0
1308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:12 AM . Last Modified: ‎2024-03-11 03:09 AM

i sent you some additional information via private message.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:12 AM . Last Modified: ‎2024-03-11 03:09 AM

0 Likes
0
1308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:12 AM . Last Modified: ‎2024-03-11 03:09 AM

did the battery you bought have a serial number on it? also, is it possible to let the UPS discharge completely with a stable load of > 35% and turn off (meaning can you do a manual runtime calibration) and then let it charge back up? your load would need to come down though so i might suggest using a non critical load if this sounds like an option.

a software calibration would only deplete the battery to between 10-20% by design and not turn the UPS off and attached load. if it were me, i'd suggest letting it go and charge back up because i dont think we will be able to tell if there is a problem until we see the results. i understand if you were a little nervous based on the behavior during the calibration.

before tgoing further though, let me know what you have for a battery serial number and it might not hurt to check with a voltmeter or on the data logs to see what the battery voltage was/is.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:12 AM . Last Modified: ‎2024-03-11 03:09 AM

0 Likes
0
1308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:12 AM . Last Modified: ‎2024-03-11 03:09 AM

According to the invoice, the serial # is S7A1209L24464 though I'm not physically looking at the battery. Does that help?

I could let the UPS discharge, but obviously this isn't idea as it would cause me a bunch of downtime. If there's any way around that I'd like to pursue it. Not sure what I have for a load to put on it that I can use to test.

It is taking a while for it to charge back up from the runtime calibration I tried (over an hour now and at 80%). I can try to let the runtime calibration go to completion, just trying to avoid any server outages. Estimated runtime is curently very low still (6 min).

On the Data Log it is showing 54.54 under the Vbat column, pretty much all the way down It was showing 54.54 even with the old battery (yesterday).

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:12 AM . Last Modified: ‎2024-03-11 03:09 AM

0 Likes
0
1308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:12 AM . Last Modified: ‎2024-03-11 03:09 AM

I completed a runtime calibration this AM. It took less than 2 minutes to complete, and is now charging back up.

Also I confirmed the serial # is correct.

Any further suggestions greatly appreciated.

Message was edited by: Kremlar

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:12 AM . Last Modified: ‎2024-03-11 03:09 AM

0 Likes
0
1308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:12 AM . Last Modified: ‎2024-03-11 03:09 AM

Charge is complete and now it shows an estimated runtime of 4 minutes.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:12 AM . Last Modified: ‎2024-03-11 03:09 AM

0 Likes
0
1308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:12 AM . Last Modified: ‎2024-03-11 03:09 AM

can you get me the exact model number of the UPS off the sticker on the back of the UPS?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:12 AM . Last Modified: ‎2024-03-11 03:09 AM

0 Likes
0
1308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:12 AM . Last Modified: ‎2024-03-11 03:09 AM

SUA3000RM2U

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:13 AM . Last Modified: ‎2024-03-11 03:09 AM

0 Likes
0
1308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:13 AM . Last Modified: ‎2024-03-11 03:09 AM

Got your PM, but no instructions in there?

Is this just as effective as recalibrating manually? Hooking a laptop via serial isn't the end of the world for me, but if the other method is better I'd rather just do that.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:13 AM . Last Modified: ‎2024-03-11 03:09 AM

0 Likes
0
1308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:13 AM . Last Modified: ‎2024-03-11 03:09 AM

oh hm. let me email it to you if thats OK using the email on your profile? if you can do it via serial cable, i'd try that way before wasting a discharge on the battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:13 AM . Last Modified: ‎2024-03-11 03:09 AM

0 Likes
0
1307
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:13 AM . Last Modified: ‎2024-03-11 03:09 AM

OK, I PMed you my address.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore