SmartUPS 2200 sufficient for new IT upgrade

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SmartUPS 2200 sufficient for new IT upgrade
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-25 10:42 PM . Last Modified: ‎2024-03-19 03:34 AM

0 Likes
1
898
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 10:42 PM . Last Modified: ‎2024-03-19 03:34 AM

SmartUPS 2200 sufficient for new IT upgrade

We have a SUA2200 with serial expansion slot protecting two servers (glorified PC's on steroids) and one workstation. We are now contemplating getting the following equipment but are unsure if the current UPS would be sufficent for safe shutdown procedures.

Four (4) HP Proliant DL360 servers - each with 2 X 700W power supplies, there will also be an external tape drive, ADSL modem and a router.

The four servers would be connected to a rack mounted PDU (HP). The PDU would then connect to the NEMA plug on the 2200 UPS.

I would appreciate any comments or suggestions.

Thanks

Labels
  • Labels:
  • Server Room & Data Center Design Best Practices
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Cap1_apc
Lt. Commander Cap1_apc
Lt. Commander

Posted: ‎2021-06-25 10:42 PM . Last Modified: ‎2024-03-19 03:34 AM

0 Likes
0
898
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 10:42 PM . Last Modified: ‎2024-03-19 03:34 AM

Two issues you have:
1. The UPS is rated for 1980 watts. The new load (4x 700w) exceeds that in itself.
2. Graceful shutdown - If you are currently using serial cables for shutdown, you're at capacity with your Interface expander card at 3 connections...

I think you're best option is to get a new UPS (perhaps another 2200) with a Network Management Card. The network card (AP9617) can perform graceful shutdowns of up to 50 servers over your network if you use the Powerchute Network Shutdown software (free).

In regards to load, the servers are likely not going to pull 700 watts of the rated power supply, so you may want to do some functional testing, but I would imagine a 2200 can handle that load. Also, with dual power supplies, you may want to look into plugging each PS into a different UPS for redundancy.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Cap1_apc
Lt. Commander Cap1_apc
Lt. Commander

Posted: ‎2021-06-25 10:42 PM . Last Modified: ‎2024-03-19 03:34 AM

0 Likes
0
899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-25 10:42 PM . Last Modified: ‎2024-03-19 03:34 AM

Two issues you have:
1. The UPS is rated for 1980 watts. The new load (4x 700w) exceeds that in itself.
2. Graceful shutdown - If you are currently using serial cables for shutdown, you're at capacity with your Interface expander card at 3 connections...

I think you're best option is to get a new UPS (perhaps another 2200) with a Network Management Card. The network card (AP9617) can perform graceful shutdowns of up to 50 servers over your network if you use the Powerchute Network Shutdown software (free).

In regards to load, the servers are likely not going to pull 700 watts of the rated power supply, so you may want to do some functional testing, but I would imagine a 2200 can handle that load. Also, with dual power supplies, you may want to look into plugging each PS into a different UPS for redundancy.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore