Smart-UPS X 750 issue

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS X 750 issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Related Products
product field
Schneider Electric
Smart-UPS

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
caseycrowe
Crewman caseycrowe
Crewman

Posted: β€Ž2023-03-24 01:42 PM

0 Likes
7
1815
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2023-03-24 01:42 PM

Smart-UPS X 750 issue

Hey, this is the third time I'm posting a question so I hope it doesn't go to spam this time. πŸ™‚ I'm having an issue with one of these (out of a few on this client's site) randomly turning off outlet groups for no reason. No power issues are logged. Hoping someone can offer a suggestion? Thanks!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
mikeinnyc
Ensign mikeinnyc
Ensign

Posted: β€Ž2023-03-25 05:32 AM . Last Modified: β€Ž2023-03-25 05:33 AM

0 Likes
3
1800
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2023-03-25 05:32 AM . Last Modified: β€Ž2023-03-25 05:33 AM

post log files and also see if you have scheduled shutdowns incorrectly added

Reply

Link copied. Please paste this link to share this article on your social media post.

caseycrowe
Crewman caseycrowe
Crewman

Posted: β€Ž2023-03-25 10:54 AM . Last Modified: β€Ž2023-03-25 10:55 AM

In response to mikeinnyc
0 Likes
0
1642
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2023-03-25 10:54 AM . Last Modified: β€Ž2023-03-25 10:55 AM

I initially posted them but they were marked as spam. A wise person would have just replied to my original comment that was approved and included the logs, but I'm fresh out of those at the moment! πŸ˜‚

I should add that I think this has just started doing this. It's been running solidly for years as far as I know. In fact, the Sonicwall firewall connected to it had a year or so of uptime the last time I looked at it before this started.

OK, here's the logs and the details about the unit (ignore the email messages, I hadn't updated the correct DNS server in there yesterday):

03/24/2023 11:22:11 Device UPS: The output power is now turned on.
03/24/2023 11:22:11 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on.
03/24/2023 11:22:11 Device UPS: The power for the main outlet group, UPS Outlets, is now turned on.
03/24/2023 11:22:06 Device UPS: The output power is turned off.
03/24/2023 11:22:06 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay.
03/24/2023 11:22:06 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.
03/24/2023 11:22:06 Device UPS: Main outlet group, UPS Outlets, has been commanded to shutdown with on delay.
03/24/2023 11:22:06 Device UPS: The power for the main outlet group, UPS Outlets, is now turned off.
03/24/2023 03:47:10 System Email: Could not resolve 'aspmx.l.google.com'.
03/24/2023 03:47:07 System Email: Could not resolve 'aspmx.l.google.com'.
03/24/2023 03:46:48 System Email: Could not resolve 'aspmx.l.google.com'.
03/24/2023 03:46:36 System Email: Could not resolve 'aspmx.l.google.com'.
03/24/2023 03:46:18 System Email: Could not resolve 'aspmx.l.google.com'.
03/24/2023 03:46:05 System Email: Could not resolve 'aspmx.l.google.com'.
03/24/2023 03:45:47 System Email: Could not resolve 'aspmx.l.google.com'.
03/24/2023 03:45:34 System Email: Could not resolve 'aspmx.l.google.com'.
03/24/2023 03:45:20 Device UPS: The output power is now turned on.
03/24/2023 03:45:20 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on.
03/24/2023 03:45:20 Device UPS: The power for the main outlet group, UPS Outlets, is now turned on.
03/24/2023 03:45:15 Device UPS: The output power is turned off.
03/24/2023 03:45:14 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay.
03/24/2023 03:45:14 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.
03/24/2023 03:45:14 Device UPS: Main outlet group, UPS Outlets, has been commanded to shutdown with on delay.
03/24/2023 03:45:14 Device UPS: The power for the main outlet group, UPS Outlets, is now turned off.

 

From the about page:

Model: Smart-UPS X 750
SKU: SMX750
Serial Number: AS1329115630
Firmware Revision: UPS 09.1 (ID20)
Manufacture Date: 07/20/2013

Apparent Power Rating: 750 VA
Real Power Rating: 600 W

Internal Battery SKU: APCRBC116
External Battery SKU: SMX48RMBP2U



Reply

Link copied. Please paste this link to share this article on your social media post.

caseycrowe
Crewman caseycrowe
Crewman

Posted: β€Ž2023-03-25 12:20 PM

In response to mikeinnyc
0 Likes
0
1741
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2023-03-25 12:20 PM

OK, every time I go to post the logs I get flagged for spam. Maybe my message is too long. I'll try to break it up a bit. Here's the logs (I've since fixed the mail issue)
03/24/2023 11:22:11 Device UPS: The output power is now turned on.
03/24/2023 11:22:11 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on.
03/24/2023 11:22:11 Device UPS: The power for the main outlet group, UPS Outlets, is now turned on.
03/24/2023 11:22:06 Device UPS: The output power is turned off.
03/24/2023 11:22:06 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay.
03/24/2023 11:22:06 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.
03/24/2023 11:22:06 Device UPS: Main outlet group, UPS Outlets, has been commanded to shutdown with on delay.
03/24/2023 11:22:06 Device UPS: The power for the main outlet group, UPS Outlets, is now turned off.
03/24/2023 03:47:10 System Email: Could not resolve 'aspmx.l.google.com'.
03/24/2023 03:47:07 System Email: Could not resolve 'aspmx.l.google.com'.
03/24/2023 03:46:48 System Email: Could not resolve 'aspmx.l.google.com'.
03/24/2023 03:46:36 System Email: Could not resolve 'aspmx.l.google.com'.
03/24/2023 03:46:18 System Email: Could not resolve 'aspmx.l.google.com'.
03/24/2023 03:46:05 System Email: Could not resolve 'aspmx.l.google.com'.
03/24/2023 03:45:47 System Email: Could not resolve 'aspmx.l.google.com'.
03/24/2023 03:45:34 System Email: Could not resolve 'aspmx.l.google.com'.
03/24/2023 03:45:20 Device UPS: The output power is now turned on.
03/24/2023 03:45:20 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on.
03/24/2023 03:45:20 Device UPS: The power for the main outlet group, UPS Outlets, is now turned on.
03/24/2023 03:45:15 Device UPS: The output power is turned off.
03/24/2023 03:45:14 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay.
03/24/2023 03:45:14 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.
03/24/2023 03:45:14 Device UPS: Main outlet group, UPS Outlets, has been commanded to shutdown with on delay.
03/24/2023 03:45:14 Device UPS: The power for the main outlet group, UPS Outlets, is now turned off.

Reply

Link copied. Please paste this link to share this article on your social media post.

caseycrowe
Crewman caseycrowe
Crewman

Posted: β€Ž2023-03-25 12:25 PM . Last Modified: β€Ž2023-03-25 12:25 PM

In response to mikeinnyc
0 Likes
0
1787
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2023-03-25 12:25 PM . Last Modified: β€Ž2023-03-25 12:25 PM

Sorry, I keep replying but my replies are marked as spam. So, trying this again.


03/24/2023 11:22:11 Device UPS: The output power is now turned on.
03/24/2023 11:22:11 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on.
03/24/2023 11:22:11 Device UPS: The power for the main outlet group, UPS Outlets, is now turned on.
03/24/2023 11:22:06 Device UPS: The output power is turned off.
03/24/2023 11:22:06 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay.
03/24/2023 11:22:06 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.
03/24/2023 11:22:06 Device UPS: Main outlet group, UPS Outlets, has been commanded to shutdown with on delay.
03/24/2023 11:22:06 Device UPS: The power for the main outlet group, UPS Outlets, is now turned off.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

caseycrowe
Crewman caseycrowe
Crewman

Posted: β€Ž2023-03-25 12:28 PM

0 Likes
0
1786
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2023-03-25 12:28 PM

Here's another event:

 

03/24/2023 03:45:20 Device UPS: The output power is now turned on.
03/24/2023 03:45:20 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on.
03/24/2023 03:45:20 Device UPS: The power for the main outlet group, UPS Outlets, is now turned on.
03/24/2023 03:45:15 Device UPS: The output power is turned off.
03/24/2023 03:45:14 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay.
03/24/2023 03:45:14 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.
03/24/2023 03:45:14 Device UPS: Main outlet group, UPS Outlets, has been commanded to shutdown with on delay.
03/24/2023 03:45:14 Device UPS: The power for the main outlet group, UPS Outlets, is now turned off.
Reply

Link copied. Please paste this link to share this article on your social media post.

caseycrowe
Crewman caseycrowe
Crewman

Posted: β€Ž2023-03-25 12:45 PM

0 Likes
0
1781
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2023-03-25 12:45 PM

And then the details of the unit:

 

Model: Smart-UPS X 750
SKU: SMX750
Serial Number: AS1329115630
Firmware Revision: UPS 09.1 (ID20)
Manufacture Date: 07/20/2013

Apparent Power Rating: 750 VA
Real Power Rating: 600 W

Internal Battery SKU: APCRBC116
External Battery SKU: SMX48RMBP2U

Reply

Link copied. Please paste this link to share this article on your social media post.

caseycrowe
Crewman caseycrowe
Crewman

Posted: β€Ž2023-03-28 09:45 AM

0 Likes
0
1738
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2023-03-28 09:45 AM

I checked the scheduled shutdown settings, and there are none for the UPS or the outlet groups, only the option to create them. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore