Smart-UPS X 3000 - AP9631 Network Card Firmware Upgrade Error

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: Smart-UPS X 3000 - AP9631 Network Card Firmware Upgrade Error
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
lkeyes
Crewman lkeyes
Crewman

Posted: ‎2023-02-10 09:24 AM

0 Likes
2
1920
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-02-10 09:24 AM

Smart-UPS X 3000 - AP9631 Network Card Firmware Upgrade Error

I have the above combination of hardware. When I attempt to log into the Web interface I get "The application was unable to load" error. with a GUI screen. 

I was advised to upgrade the firmware on the unit and attempted to  run the firmware upgrade wizard apc_hw05_aos708_sumx708_bootmon109.exe.  

 

When running upgrade wizard I get t an error.  "Firmware distribution does not match target device platform; this could be due to a corrupt distribution"...  

 

When looking for firmware updates,  I put in the model number SMX300HVNC   and the search says there is no available firmware.   


I can log into the NMC console with SSL and directly via the COM interface.  

Is there a way to recover from the upgrade error above....  or, failing that,  further determine the appropriate firmware.    

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
TOCITRM
Crewman TOCITRM
Crewman

Posted: ‎2023-03-18 05:05 PM . Last Modified: ‎2023-03-18 05:07 PM

0 Likes
0
1866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-18 05:05 PM . Last Modified: ‎2023-03-18 05:07 PM

don't search for the UPS model number, search for the NMC model, (i.e. AP9631).

 

You're not trying to flash the f/w on the UPS but the network management card.

 

You'll be looking here https://www.apc.com/shop/us/en/products/UPS-Network-Management-Card-v7-0-8-Firmware-for-Symmetra-1-P...

 

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
TOCITRM
Crewman TOCITRM
Crewman

Posted: ‎2023-03-18 05:05 PM . Last Modified: ‎2023-03-18 05:07 PM

0 Likes
0
1867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-18 05:05 PM . Last Modified: ‎2023-03-18 05:07 PM

don't search for the UPS model number, search for the NMC model, (i.e. AP9631).

 

You're not trying to flash the f/w on the UPS but the network management card.

 

You'll be looking here https://www.apc.com/shop/us/en/products/UPS-Network-Management-Card-v7-0-8-Firmware-for-Symmetra-1-P...

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

lkeyes
Crewman lkeyes
Crewman

Posted: ‎2023-03-20 07:40 AM

0 Likes
0
1851
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-20 07:40 AM

Excellent...many thanks! 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2024 Schneider Electric, Inc