Smart-UPS SRT 6000 - Bypass not in range ; either frequency or voltage.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS SRT 6000 - Bypass not in range ; either frequency or voltage.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
T-H
Crewman T-H
Crewman

Posted: ‎2024-04-04 10:54 PM

0 Likes
5
775
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-04 10:54 PM

Smart-UPS SRT 6000 - Bypass not in range ; either frequency or voltage.

Hello everyone,
We have several locations Smart-UPS SRT installed. However, we have always had these messages at the main location for a long time.


UPS: Bypass not in range ; either frequency or voltage.
A few seconds later:
UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.

 

Where can I find out in which log where I see frequency or voltage problem?

 

We have already customised a lot. See Screenshot1.png.
However, any adjustment does not help.
You may have the best setting.

 


I have also added the data log (Last 8 hours). See Datalog.txt.

For your information, we have already installed the 4th APC in total on this location, as we received the information from support serverl times,

 

- disconnect the load from the UPS (the server/PCs may have to be shut down first)

- Switch off the UPS - On/Off button

- Disconnect the battery

- Disconnect all cable connections from the UPS (power cable, communication cable, load)

- press the button to switch on again for 5 seconds.

You may hear a beep, a switching sound or nothing at all.

- Please reconnect the UPS and connect it to the load as at the beginning

- Switch on the UPS

 

Here are also links to this topic on our website:

 

Smart UPS: https://www.apc.com/us/en/faqs/FA156611/

 

Please let us know if this procedure has brought any improvement. If not :

 

In order to arrange a replacement under warranty, I need the following information from you:

....

We followed the steps but nothing helped.

 

Many thanks in advance

Attachments
  • Tags:
  • Bypass not in range
  • either frequency or voltage
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
Teken
Janeway Teken
Janeway

Posted: ‎2024-04-05 05:05 AM

1 Like
2
745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-05 05:05 AM

Based on the information you have provided I’m not quite sure what the problem is? 🤔

 

The Data Log shows both frequency and voltage captured by the system. The frequency at your location has been rock solid. The voltage had some variations but nothing too significant to even mention.

 

The bypass values you selected could be adjusted better to reduce the amount of time the system transferred over though. But that is up to your site’s requirements and the quality of power seen at that location.

 

As it relates to completing the Brain Dead procedure it’s normally as follows:

 

Shut down and disconnect all loads. Remove AC Mains, Disconnect Battery, Press and hold the power button.

 

You may hear a click & beep once this procedure is completed. You may not hear anything at all. 

Reconnect everything and power up the system. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

T-H
Crewman T-H
Crewman

Posted: ‎2024-04-10 10:34 PM

In response to Teken
0 Likes
1
699
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-10 10:34 PM

I did this, but there was no improvement.
It would simply be important for me to find the place in the logs where this is documented.
Because I can't imagine that this message is created without a log.
Thanks for your answer.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Janeway Teken
Janeway

Posted: ‎2024-04-11 05:26 AM

In response to T-H
0 Likes
0
689
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-11 05:26 AM

The active faults / errors can be seen using the LCD for logs. The NMC upon first login shows the past / current transfer(s) in (human readable form) under Recent Device Events which are the logs you’re asking about.


Logs -> Events -> Logs: This captures the same information as the Recent Device Events, in longer duration based on the log size you have defined and interval.

 

Logs -> Data -> Logs: This captures and displays all of the numeric values seen by the system. It spans line voltage, frequency, battery voltage, current, temperature, humidity, etc. Generally speaking it’s this information that a person will review that relates to the human readable active faults / transfer errors.

 

This is the same information you have provided here. Based on the small data sample all appear to be fine. 

It goes without saying you can see transfer errors when the system has been programmed to use a very tight power regulation.

 

It’s up to you to confirm if the power quality is excellent, good, or bad. Once known your site will determine what is acceptable and how the UPS will be programmed to offer the cleanest power to, OK power.

 

As suggested earlier you can adjust the upper / lower transfer voltage to see how the system reacts. 

 

It should be noted even though the system does not always display and capture all line conditions in its data logs.

 

Because it’s not real time but restricted by the defined interval of the NMC system.

 

The UPS does indeed monitor and reacts in real time to line conditions.

Reply

Link copied. Please paste this link to share this article on your social media post.

dpierce4776
Lieutenant dpierce4776
Lieutenant

Posted: ‎2024-04-12 06:33 AM

0 Likes
0
669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-12 06:33 AM

Personally since you have looked at the logs and checked inuput voltages at the outlet. I am thinking on one of these is the issue

 

  1. Loose ground.
  2. Feed back or neutral carrying more than 5 volts from another device on the same circuit.
  3. Neutral not bonded correctly at the main panel.

All of these will cause UPSs to throw all kinds of various alerts. Including over draws on the UPS, inverter issue alerts, and bypass alerts

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Janeway Teken
Janeway

Posted: ‎2024-04-12 08:24 AM

0 Likes
0
662
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-12 08:24 AM

Let me add in one more thing to consider just to be thorough. 🤣 In the OPS image capture it shows 230 VAC.

 

Im going to assume this is correct?!? 🤔

 

If not, and your input line voltage is 240 this would cause an issue! ☝️ Please confirm your region and line voltage for us. 

Because just this simple mistake impacts what the upper / lower transfer voltage are available to use. 

NOTE: The UPS must be turned off to make the input voltage change. So plan and schedule accordingly to make that happen. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of