Smart-UPS RT 3000 XL - UPS Output Power Keeps Turning Off

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS RT 3000 XL - UPS Output Power Keeps Turning Off
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:12 AM . Last Modified: ‎2024-03-13 11:24 PM

0 Likes
4
1210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:12 AM . Last Modified: ‎2024-03-13 11:24 PM

Smart-UPS RT 3000 XL - UPS Output Power Keeps Turning Off

We have a Smart-UPS RT 3000 XL which seems to turn off the output power every time it performs a self-test. The UPS has a 9630 network management card installed.

The logs seem to indicate problem occurs during self-tests - or that the self tests are run after/during the problem - We're not sure.

The UPS is currently online with no alarms present. Battery capacity is at 100% Load at 20%. Can anyone assist? Is this a bug? Hardware problem?

Here are the logs:

 Date Time Event
 10/27/2010 4:06:36 UPS: The output power is turned off.
 10/27/2010 4:15:01 UPS: Started a self-test.
 10/27/2010 4:15:01 UPS: The output power is now turned on.
 10/27/2010 4:15:16 UPS: Passed a self-test.

 11/03/2010 3:30:17 UPS: The output power is turned off.
 11/03/2010 3:34:49 UPS: Started a self-test.
 11/03/2010 3:34:49 UPS: The output power is now turned on.
 11/03/2010 3:35:05 UPS: Passed a self-test.

 11/09/2010 1:24:57 UPS: The output power is turned off.
 11/09/2010 1:31:28 UPS: Started a self-test.
 11/09/2010 1:31:28 UPS: The output power is now turned on.
 11/09/2010 1:31:43 UPS: Passed a self-test.

 11/10/2010 1:21:09 UPS: The output power is turned off.
 11/10/2010 1:25:01 UPS: Started a self-test.
 11/10/2010 1:25:01 UPS: The output power is now turned on.
 11/10/2010 1:25:17 UPS: Passed a self-test.

11/11/2010 2:09:07 UPS: The output power is turned off.
11/11/2010 2:14:06 UPS: Started a self-test.
11/11/2010 2:14:06 UPS: The output power is now turned on.
11/11/2010 2:14:22 UPS: Passed a self-test.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:13 AM . Last Modified: ‎2024-03-13 11:23 PM

0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:13 AM . Last Modified: ‎2024-03-13 11:23 PM

ok. can you provide the firmware versions of both the UPS and the NMC?

it does sound like a UPS issue here but lets just check.

if you log into the NMC, check the UPS tab->About for the UPS firmware and then the NMC firmware is under the Administration tab->General->About.

thanks!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:12 AM . Last Modified: ‎2024-03-13 11:24 PM

0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:12 AM . Last Modified: ‎2024-03-13 11:24 PM

Thanks for the assistance... here is the information.


Model: Smart-UPS RT 3000 XL
Position: TOWER
Firmware Revision: 450.14.W
Manufacture Date: 02/19/06

Model Number: AP9630
Hardware Revision: 05
Manufacture Date: 08/17/2009
MAC Address: 00 C0 B7 4D 9F AD
Management Uptime: 33 Days 9 Hours 6 Minutes


Application Module

Name: sumx
Version: v5.0.3
Date: Aug 6 2009
Time: 21:53:59


APC OS (AOS)

Name: aos
Version: v5.0.3
Date: Aug 4 2009
Time: 13:12:44


APC Boot Monitor

Name: bootmon
Version: v1.0.0
Date: Oct 8 2008
Time: 16:03:02

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:12 AM . Last Modified: ‎2024-03-13 11:24 PM

0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:12 AM . Last Modified: ‎2024-03-13 11:24 PM

you are seeing the messages in the log but is the actual power turning off which is causing your load to turn off?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:12 AM . Last Modified: ‎2024-03-13 11:24 PM

0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:12 AM . Last Modified: ‎2024-03-13 11:24 PM

Yes, the output power is being shut off, causing our network equipment to power down/reload.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:13 AM . Last Modified: ‎2024-03-13 11:23 PM

0 Likes
0
1210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:13 AM . Last Modified: ‎2024-03-13 11:23 PM

ok. can you provide the firmware versions of both the UPS and the NMC?

it does sound like a UPS issue here but lets just check.

if you log into the NMC, check the UPS tab->About for the UPS firmware and then the NMC firmware is under the Administration tab->General->About.

thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore