APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-06-28 04:55 AM . Last Modified: 2024-03-18 03:59 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:55 AM . Last Modified: 2024-03-18 03:59 AM
We have four of these UPS. Recently we replaced all of their batteries and I am trying to fix the battery constant issue.
I did it successfully on one of them. Press Shift+Y, I got "SM", and press 1 twice with a few seconds in between, I got "PROG", then i changed the battery constant successfully.
On the other three UPS, I can get "SM", but I cannot get "PROG", no matter how I press "1".
Actually after "SM", I can use some commands. such as "0" to see its current battery constant, press "a" to see some response, etc. Here is the response I got after shift+Y, 0, -, a
SM
3C
NO
4.!$%+?=#|. ')+-/789<>@ABCDEFGKLMNOPQRSUVWXYZ\^abcefgjklmnopqrsuwxyz~.�:������
The problem is, how can I see "PROG" to change the battery constant? please help me!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:55 AM . Last Modified: 2024-03-18 03:59 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:55 AM . Last Modified: 2024-03-18 03:59 AM
Just figured it out.
To make "PROG" show up, the network management card must be taken out.
The one I succeeded at first had a dead network management card. After I removed the network management cards from the other three UPS, I can press "1" twice to get "PROG" .
By the way, the card can be removed while the UPS is in operation.
uppercase for people who are not patient.
REMOVE THE NETWORK MANAGEMENT CARD FIRST!!!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:55 AM . Last Modified: 2024-03-18 03:59 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:55 AM . Last Modified: 2024-03-18 03:59 AM
Just figured it out.
To make "PROG" show up, the network management card must be taken out.
The one I succeeded at first had a dead network management card. After I removed the network management cards from the other three UPS, I can press "1" twice to get "PROG" .
By the way, the card can be removed while the UPS is in operation.
uppercase for people who are not patient.
REMOVE THE NETWORK MANAGEMENT CARD FIRST!!!
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.