Smart-UPS C Output Voltage

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS C Output Voltage
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:11 AM . Last Modified: ‎2024-03-18 03:43 AM

0 Likes
5
2941
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:11 AM . Last Modified: ‎2024-03-18 03:43 AM

Smart-UPS C Output Voltage

Hi,

I have an SMC3000I UPS. The issue is that I can't seem to fix the output voltage at 230V.

Input voltage at the facility is usually on the high side 245VAC 50hz in the day & 251VAC 50hz at night.

Using the default settings, it seemed like UPS is not regulating the output at all:

Sensitivity: Medium ; Green Mode: 1 (Enabled) ; Output Setting: 230V
UPS INPUT: 245VAC ; UPS OUTPUT: 245VAC

Test #1:

Sensitivity: Medium ; Green Mode: 0 (Disabled) ; Output Setting: 230V
INPUT: 245VAC ; OUTPUT: 245VAC ; AVR: none

Test #2:

Sensitivity: High; Green Mode: 0 (Disabled) ; Output Setting: 230V
INPUT: 245VAC ; OUTPUT: 245VAC ; AVR: none

Test #3:

Sensitivity: High; Green Mode: 0 (Disabled) ; Output Setting: 220V
INPUT: 245VAC ; OUTPUT: 217VAC ; AVR compensating for high input
voltage

During Test #3 the UPS output reading was 221V without load, 217V with load. I was hoping I can at least get it to output at 220V, +/- 1V but voltage dropped when equipments are powered up.

I would like to know if there's an issue with the UPS or is there some configurations I missed. The requirement is to have a 230V output at all times.

UPS INPUT

UPS Output

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 230v
  • c
  • output
  • smart-ups
  • smc
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:12 AM . Last Modified: ‎2024-03-18 03:43 AM

0 Likes
0
2940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:12 AM . Last Modified: ‎2024-03-18 03:43 AM

Thanks to both of you. Very informative.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 05:12 AM . Last Modified: ‎2024-03-18 03:43 AM

0 Likes
0
2940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:12 AM . Last Modified: ‎2024-03-18 03:43 AM

If you want (need) voltage regulation then you've bought the wrong UPS.

That unit will boost and trim as required to keep the voltage nominal, and it'll give you a solid 230V on battery, but what you appear to need is an RT series ups. Full on-line double conversion. Something like a SURTD3000XLI.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 05:12 AM . Last Modified: ‎2024-03-18 03:43 AM

0 Likes
0
2940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:12 AM . Last Modified: ‎2024-03-18 03:43 AM

Brad's right -- getting +/- 1V requires a double-conversion UPS. The line-interactive UPS you have runs its inverter only when needed. Boost and trimming the voltage is done with fixed transformer taps which raise or lower the voltage by 10% or 20%. Page 5 of the manual for your UPS (link) describes the voltage range it will provide at each sensitivity level.

Double conversion UPSes always operate their inverters. It's less efficient, more expensive, but tolerates dirtier power and generate a specific voltage.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:12 AM . Last Modified: ‎2024-03-18 03:43 AM

0 Likes
0
2940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:12 AM . Last Modified: ‎2024-03-18 03:43 AM

Voidstar & Brad, Thanks for your input. This is a bitter pill to hard to swallow.

So does that mean the other Line Interactive models (SMT & SMX) will function the same way ?

Since I configured the sensitivity to High, does that mean the AVR will only regulate output to 230V when input voltages dropped below 207V & rises above 253V ? But I had always assumed the sensitivity settings is a threshold for UPS run on battery when input is out of range.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 05:12 AM . Last Modified: ‎2024-03-18 03:43 AM

0 Likes
0
2940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:12 AM . Last Modified: ‎2024-03-18 03:43 AM

Yes, most line-interactive models behave the same way. There are a few sold as "line interactive" that are really double-conversion, but it's best to get one advertised as double-conversion if you need the feature.

On 11/15/2016 5:09 AM, $pecialist said:

Since I configured the sensitivity to High, does that mean the AVR will only regulate output to 230V when input voltages dropped below 207V & rises above 253V ? But I had always assumed the sensitivity settings is a threshold for UPS run on battery when input is out of range.

The UPS performs course voltage adjustments using the AVR transformer without needing to go on battery. This doesn't create exactly 230V. The output voltage range is based on what equipment today should be able to handle -- I assume you have some specialized devices that cannot.

Based on the tech spec on APC's website I've diagrammed it below for 230V nominal:

               0V         ~170V           207V     230V     253V    300V
Input voltage: | |--------------|========|========|-------| >
\ / \ / \ /\ / \ /
On Battery AVR Boost On Line AVR Trim On Battery (out: 230V)
(output 230V) (out: 207V-253V) (out = in) (out: 207V-253V)

The UPS will boost the voltage if it falls below 207V and trim it if it rises above 253V. That puts the output voltage back in the 207V-253V range; it doesn't produce exactly 230V. When the UPS can no longer keep the output voltage within that range by boosting or trimming then it will go to battery.

Sensitivity also affects how a line-interactive UPS responds to distorted voltage. The UPS must react before attached equipment notices a power loss, so any slight disturbance will cause the UPS to temporarily transfer to battery. Not all voltage distortions become a loss of power -- when the UPS transfers in absence of a power failure we call that a "nuisance transfer". High sensitivity causes the UPS to react faster at the expense of more nuisance transfers. Double-conversion UPSes always run their inverters so they don't have to react which is why they can accept dirtier power than line-interactive UPSes.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:12 AM . Last Modified: ‎2024-03-18 03:43 AM

0 Likes
0
2941
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:12 AM . Last Modified: ‎2024-03-18 03:43 AM

Thanks to both of you. Very informative.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore