Smart UPS 750VA doesn't come with AVR - do I need one seperately?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS 750VA doesn't come with AVR - do I need one seperately?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:38 AM

0 Likes
15
2877
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:38 AM

Smart UPS 750VA doesn't come with AVR - do I need one seperately?

I currently have a surge protector but shopping for a UPS with AVR preferably. I love these APC UPS and happen to get a good deal for Smart UPS 750VA. However, I learn that it doesn't come with built-in AVR. Any ideas why they don't include that since it's such an expensive UPS? I would be using it for my home PC so do I need to get a seperate AVR in this case or the UPS alone is sufficient?

Any help or thoughts is appreciated.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:36 AM

0 Likes
0
2876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:36 AM

The discharge of the battery is normal. The topology of the UPS is to constantly provide power to the receptacles, but at the same time, trickle charging the battery. When you use the UPS as a master on/off or turn it off when not in use, and the battery stays connected, it will begin a discharge process. It may just be that it drops from 100% to say 98 or 97%, and that's why the 5 LED's are not full when you turn it back on.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 15
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:38 AM

0 Likes
0
2876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:38 AM

Thanks for your help. I was browsing through the product link and I can't seem to see anywhere it says the AVR is included:
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SUA750I

Btw, how reliable is this UPS? Does it break down easily and can it be repaired in future if there are no more wararnty?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:37 AM

0 Likes
0
2876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:37 AM

If your refering to the SUA750, this unit definitely has AVR with boost and trim. I did see that it isn't mentioned on the APC website under technical specifications or product info, but if you check pages 3 and 6 of the manual found here:

http://www.apcmedia.com/salestools/ASTE-6Z8LLF_R1_EN.pdf

it refers to the AVR boost and trim leds as well the high and low transfer points for AVR, sorry that this wasn't made more clear.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:37 AM

0 Likes
0
2876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:37 AM

While I cant speake directly for the international models (we are in the US), the smart up SUA750 is very reliable and will give you years of service. It usually only needs a battery replacement after a few years.

There are no parts available for it as it is not a modular UPS, or contain field-repalceable items like our larger ups' do.

Most of our computer users have the previous version, the SU700, underneath our desks for years now. Some units are as old as 10 years old!!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:37 AM

0 Likes
0
2876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:37 AM

Hey guys, I just got my Smart UPS 750. However, I have some questions:

1. I am using it on my desktop PC only so which Powerchute software should I install? I believe I don't need to install the Agent software?
2. I hook up my LCD and CPU so how much runtime would it be able to give me in case of a power failure? Is there a way to tell?
3. How long does it take for the battery to be fully charged?
4. Can I use my Belkin surge protector together with this UPS? Wall plug to Surge protector then to UPS?

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:37 AM

0 Likes
0
2876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:37 AM

Hi Powerguy...

You would need to actually install JUST the Agent of PowerChute Business Edition, if you don't want to install the Server/Console (graphical GUI).

To access the agent for configuration and information, it would be:
http://127.0.0.1:3052

That will also tell you what your load and runtime available is.

And no, you cannot put a surge protector upstream from the UPS. You would need a residential panelmount surge in order for that to be valid. You can only use an APC Surge protector downstream of the UPS, so that in the event of equipment damage, if it occurs, APC is the only brand you are using, and noone points fingers at the other.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:37 AM

0 Likes
0
2876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:37 AM

Thanks Notorious K πŸ™‚ I've learned a lot from you certainly. I believe there's no harm in turning the UPS on/off everyday as I wouldn't want to leave it on all the time. It makes some noise when I turn it on sometimes so just wanted to make sure it does no harm in the long run as I know UPS is meant to stay up 24x7.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:37 AM

0 Likes
0
2876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:37 AM

Wow, thanks for the great help Notorious K πŸ™‚
I've installed the Agent and patched it for my Vista32 but Internet Explorer doesn't like it. I've included it in my safe list but I still can't logon as the bottom status bar of IE says there an "Error in the page". I guess I need to install the console somehow?

You mean I can install a surge protector of other brands before my UPS but it will be at my own risk? I just need to know if it does any danger by doing so?

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:37 AM

0 Likes
0
2876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:37 AM

The error on page is usually a Java issue....you could update java and see if that fixes it.

As far as the surge protector, the only problem with it is that because it's a protector, not a distributor, if you have other devices plugged in as well, they're all competing for the same power.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:37 AM

0 Likes
0
2876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:37 AM

Thanks again. I also happen to notice there are some electric buzzing sound coming out from the UPS. Is this normal?

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:37 AM

0 Likes
0
2876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:37 AM

Is the buzzing while the UPS is online, on battery, or while it's been charging the battery?

Is there anything within 3 feet of it like a monitor or tower that could cause some EMI?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:37 AM

0 Likes
0
2876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:37 AM

It seems to be alright now but had some buzzing during battery recharge. Is this normal?
I have my subwoofer about 5 inches at the side of my UPS. Could that cause EMI?

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:37 AM

0 Likes
0
2876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:37 AM

Usually the recommended distance is 36 inches. I'm sure you made a nice investment in the speaker setup powered by the UPS, so chances are yes, there is something causing EMI from the subwoofer to the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:37 AM

0 Likes
0
2876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:37 AM

The noise it makes at startup is the transfer switch kicking in for the self-test, then you hear the hum while it's on battery, then the transfer switch going back to an online state.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:37 AM

0 Likes
0
2877
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:37 AM

Thanks a lot πŸ™‚ You've been really helpful to be honest. I have a small table so maybe I need to figure out where can I put this UPS (far from my Klipsch Promedia GMX).
Btw, I turn my UPS and wall plug power off everytime I shut down my PC. When I turn the UPS back on after the wall plug, it will always discharge a little of it's battery. Is this normal? Is it better to leave the UPS on 24x7 or will turning off/on makes it have a shorter lifespan?

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:36 AM

0 Likes
0
2877
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 05:24 AM . Last Modified: β€Ž2024-03-08 02:36 AM

The discharge of the battery is normal. The topology of the UPS is to constantly provide power to the receptacles, but at the same time, trickle charging the battery. When you use the UPS as a master on/off or turn it off when not in use, and the battery stays connected, it will begin a discharge process. It may just be that it drops from 100% to say 98 or 97%, and that's why the 5 LED's are not full when you turn it back on.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore