Smart-UPS 3000XLM + Network Management Card EM

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 3000XLM + Network Management Card EM
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:21 PM . Last Modified: ‎2024-03-14 04:36 AM

0 Likes
5
2850
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:21 PM . Last Modified: ‎2024-03-14 04:36 AM

Smart-UPS 3000XLM + Network Management Card EM

Hello,

I have a number of APC Smart-UPS 3000XLM (SUM3000RMXL2U) units, each with an APC Smart Slot Network Management Card EM (AP9619).

All of the Network Management Cards I have been able to configure using the Wizard on the CD, except for one.
It doesn't seem to ever get detected.

I've tried arp and manually setting the IP address that way to no avail.
I've also tried resetting the unit using the button on the back, but it didn't seem to do anything. (I think this just resets passwords anyway).

I've used a couple of subnet scanning utilities to see if I could find out if the machine was automatically getting an IP from somewhere but it doesnt look like it. The speed indicator light is a blinking orange to indicate 100MB, and the status indicator light is a solid green.

My AP9619 management card has no serial or console port, so I cannot manually set the address. The 3000XLM unit has a network management port (rj45) that I have tried to connect to but it doesn't seem to work either. I've tried this port with both an rj45 management to serial, and rj45 to usb cables.

Does anyone have any ideas?

Thanks,
-sc84

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • _card
  • ap9619
  • apc
  • configuration
  • ip
  • network_management
  • sum3000rmxl2u
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:21 PM . Last Modified: ‎2024-03-14 04:36 AM

0 Likes
0
2850
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:21 PM . Last Modified: ‎2024-03-14 04:36 AM

no problem!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:21 PM . Last Modified: ‎2024-03-14 04:36 AM

0 Likes
0
2849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:21 PM . Last Modified: ‎2024-03-14 04:36 AM

a solid green status LED indicates it has a valid IP address.

the RJ-45 port on the network management card itself is for the LAN connection of course and then the UPS itself should have a DB9 serial connection on it. next to that DB9 serial port is a RJ-45 port used for USB communication with a supplied RJ-45 to USB cable. this is not used for anything else. using the APC serial cable only (that shipped with the UPS - 940-1524 i believe), you should be able to try to use a terminal program to access the card directly via the serial port on the UPS. the port speed settings would be - 2400, 8, N, 1, No flow control.

if you can use the serial connection method local to the card, this would be the easiest method of trying to figure this out. upon accessing the card, you can use the default username and password (apc/apc) as i am sure you already figured out from the other cards and go in and check the settings.

you HAVE to use the serial cable to configure the network management card. you main need to reseat the power module (by going to bypass first) to reset the serial port if you cant get it working since you used the USB port which may or may not kill the serial port on this.

hope this helps!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:21 PM . Last Modified: ‎2024-03-14 04:36 AM

0 Likes
0
2849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:21 PM . Last Modified: ‎2024-03-14 04:36 AM

Thanks for the reply.

How do I connect to the apc unit using the rj45 -> USB cable? (My APC unit does not have a regular serial port, so this is my only option)
Is there some driver I need to enable that connection over a COM port?

Whenever I use something like putty or hyperterminal my only options are com1 and com2.

Message was edited by: sc84

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:21 PM . Last Modified: ‎2024-03-14 04:36 AM

0 Likes
0
2849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:21 PM . Last Modified: ‎2024-03-14 04:36 AM

take a look at [this picture|http://www.apc.com/products/moreimages.cfm?partnum=SUM3000RMXL2U&type=Back]

yours looks different? i see a serial port on the top left hand corner. we cannot use the RJ-45 to USB cable to work on this.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:21 PM . Last Modified: ‎2024-03-14 04:36 AM

0 Likes
0
2849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:21 PM . Last Modified: ‎2024-03-14 04:36 AM

No that is the correct one, sorry I thought you were talking about something else.

I've connected the serial cable but it's still not receiving a response from the unit when I try to console in to it.
How do I reseat the power module? Is this going to require downtime from machines attached to the apc unit?

Edit: Started working, reconnected the serial cable and was able to manually set the IP configuration through the Wizard local connection setting

Thank you.

Message was edited by: sc84

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:21 PM . Last Modified: ‎2024-03-14 04:36 AM

0 Likes
0
2851
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:21 PM . Last Modified: ‎2024-03-14 04:36 AM

no problem!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore