Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Silcon 60KVA, Battery voltage

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Silcon 60KVA, Battery voltage
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 04:57 AM . Last Modified: ‎2024-03-19 01:15 AM

0 Likes
9
1458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:57 AM . Last Modified: ‎2024-03-19 01:15 AM

Silcon 60KVA, Battery voltage

Hi guy's
Our client have 3 units of 60KVA Silcon UPS ( SL60KH ), connected in parallel and everything are doing good no alarm/fault.
But my concern is, 1 of the UPS show the battery voltage on the display panel was 423, 424, but when we measure the actual battery voltage the reading was 436.1, 436.7 Vdc. They said that the battery Voltage from Display Panel and the actual battery voltage reading will not be the same at all, is it true??

any advise..thanks

Attachments
Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-26 04:57 AM . Last Modified: ‎2024-03-19 01:14 AM

0 Likes
0
1458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:57 AM . Last Modified: ‎2024-03-19 01:14 AM

Hi guy's
Our client have 3 units of 60KVA Silcon UPS ( SL60KH ), connected in parallel and everything are doing good no alarm/fault.
But my concern is, 1 of the UPS show the battery voltage on the display panel was 423, 424, but when we measure the actual battery voltage the reading was 436.1, 436.7 Vdc. They said that the battery Voltage from Display Panel and the actual battery voltage reading will not be the same at all, is it true??

any advise..thanks

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Anonymous user
Not applicable

Posted: ‎2021-06-26 04:57 AM . Last Modified: ‎2024-03-19 01:14 AM

0 Likes
0
1458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:57 AM . Last Modified: ‎2024-03-19 01:14 AM

Hi

actually i prefer from you guys to answer all my issue or some technical question/explanation, coz you give me good justification.
anyways, for this issue i try to call or email the support of APC here in our country.

thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-26 04:57 AM . Last Modified: ‎2024-03-19 01:14 AM

0 Likes
0
1459
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:57 AM . Last Modified: ‎2024-03-19 01:14 AM

This can be fixed by calibrating the unit. You would need to call into APC to have one of their technicians perform this if you don't know how.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:57 AM . Last Modified: ‎2024-03-19 01:14 AM

0 Likes
0
1459
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:57 AM . Last Modified: ‎2024-03-19 01:14 AM

APC service partner already go down to the site for calibration but still the display is the same.
What should be the truth about the actual reading and display from the panel, by rights it should be the same or not?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:57 AM . Last Modified: ‎2024-03-19 01:14 AM

0 Likes
0
1459
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:57 AM . Last Modified: ‎2024-03-19 01:14 AM

hi

I just want to verify if the display on the panel and the actual reading should be the same or not?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:57 AM . Last Modified: ‎2024-03-19 01:14 AM

0 Likes
0
1459
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:57 AM . Last Modified: ‎2024-03-19 01:14 AM

Hi

thanks, great..., are you able to send me email regarding this issue, just for the record and a black and white statement from APC.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 04:57 AM . Last Modified: ‎2024-03-19 01:14 AM

0 Likes
0
1459
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:57 AM . Last Modified: ‎2024-03-19 01:14 AM

Hi Hanz,

I noticed from your profile that you are from the Philippines, for faster response time you could contact them on you local time.

* Call us at toll free 1800 144 10535
* For Globe Subscribers, please call +6346437 3288
* For Blackberry mobile users enter the numbers directly into your mobile when calling the toll free number.
* E-mail: asetech@apcc.com
* Business Hours: 9:00AM-6:00PM Monday-Friday

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 04:57 AM . Last Modified: ‎2024-03-19 01:14 AM

0 Likes
0
1459
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:57 AM . Last Modified: ‎2024-03-19 01:14 AM

We would try our best to assist/ help you to the best that we can here in the APC Forum. For mission critical cases/ emergency cases the Philippine Team can assist you. Let's see if clarkson can fill in your request for an e-mail.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:57 AM . Last Modified: ‎2024-03-19 01:14 AM

0 Likes
0
1458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:57 AM . Last Modified: ‎2024-03-19 01:14 AM

Hi

Thanks.., hopefully clarkson able to send me a statement..:-)

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:57 AM . Last Modified: ‎2024-03-19 01:14 AM

0 Likes
0
1459
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:57 AM . Last Modified: ‎2024-03-19 01:14 AM

Hi guy's
Our client have 3 units of 60KVA Silcon UPS ( SL60KH ), connected in parallel and everything are doing good no alarm/fault.
But my concern is, 1 of the UPS show the battery voltage on the display panel was 423, 424, but when we measure the actual battery voltage the reading was 436.1, 436.7 Vdc. They said that the battery Voltage from Display Panel and the actual battery voltage reading will not be the same at all, is it true??

any advise..thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore