Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Signal shutdown to multiple devices without the use of an NMC?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Signal shutdown to multiple devices without the use of an NMC?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:23 AM . Last Modified: ‎2024-02-29 10:10 PM

0 Likes
5
2393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:23 AM . Last Modified: ‎2024-02-29 10:10 PM

Signal shutdown to multiple devices without the use of an NMC?

Signal shutdown to multiple devices without the use of an NMC?
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:23 AM . Last Modified: ‎2024-02-29 10:09 PM

0 Likes
0
2393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:23 AM . Last Modified: ‎2024-02-29 10:09 PM

Following on from my first message and problem:

I managed to procure a suitable RJ45->Serial cable for the APC UPS. This is now connected to our Windows Server running PowerChute. The UPS is connected via USB to a QNAP NAS. This in turn acts as a master for a second QNAP NAS, which queries the first for UPS state.

I can happily confirm that we have had no problems with this setup; both the Windows machine and NASs can query the UPS simultaneously. Only the Windows Server ever changes any settings on the UPS, so this has worked perfectly.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-07-08 02:23 AM . Last Modified: ‎2024-02-29 10:10 PM

0 Likes
0
2393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:23 AM . Last Modified: ‎2024-02-29 10:10 PM

I'm unsure of the new generation (SMT/SMX) but certainly the earlier SUA would not do serial & USB together. I'm also not familiar with windows, but I do use APCUPSD to manage several UPS and several servers. This allows full logging, e-mail alerts and pretty much anything else you want to configure it for. I see APCUPSD does support Windows, so that might be an option for you.

Currently I have 3 servers off one UPS. One talks to the UPS over serial, and the other two talk to the first one using the APCUPSD slave network protocol. It all works like it should. I have a fairly non-standard configuration whereby the first server and network gear stay up as long as I can, so when I get a mains failure the secondary servers shut down after 20 minutes. That gives abut 530 minutes for the main server vs 230 minutes with all running. Enough to ride out most outages or give me time to get the generator out.

APCUPSD is pretty flexible when you get into it.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:23 AM . Last Modified: ‎2024-02-29 10:10 PM

0 Likes
0
2393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:23 AM . Last Modified: ‎2024-02-29 10:10 PM

If APCUPSD provides as much functionality as PowerChute, I'm happy to consider switching!

Annoyingly QNAP servers don't let you change their username or password for network connectivity but I believe that they're compatible with APCUPSD.

The config you described is what I've been hoping to achieve. Keeping the 'master' server on and powering the QNAP servers down to extend runtime would be ideal and I think the NASs support WoL so can be woken back up by the master.

Thanks for the advice!

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-07-08 02:23 AM . Last Modified: ‎2024-02-29 10:10 PM

0 Likes
0
2393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:23 AM . Last Modified: ‎2024-02-29 10:10 PM

Please let us know how you get on. I honestly don't know much about the interaction with APCUPSD and Windows, and feedback is always good.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:23 AM . Last Modified: ‎2024-02-29 10:10 PM

0 Likes
0
2393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:23 AM . Last Modified: ‎2024-02-29 10:10 PM

Will do, just need to find a suitable period of time for me to take the servers offline whilst I tinker with them!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:23 AM . Last Modified: ‎2024-02-29 10:09 PM

0 Likes
0
2394
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:23 AM . Last Modified: ‎2024-02-29 10:09 PM

Following on from my first message and problem:

I managed to procure a suitable RJ45->Serial cable for the APC UPS. This is now connected to our Windows Server running PowerChute. The UPS is connected via USB to a QNAP NAS. This in turn acts as a master for a second QNAP NAS, which queries the first for UPS state.

I can happily confirm that we have had no problems with this setup; both the Windows machine and NASs can query the UPS simultaneously. Only the Windows Server ever changes any settings on the UPS, so this has worked perfectly.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of