Shutdown computer not APC at so many minutes battery left

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Shutdown computer not APC at so many minutes battery left
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:48 AM . Last Modified: ‎2024-03-13 01:23 AM

0 Likes
3
1278
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:48 AM . Last Modified: ‎2024-03-13 01:23 AM

Shutdown computer not APC at so many minutes battery left

I have a Smart-UPS RT 3000 XL and a network management card installed.  I just installed the PowerChute Network Shutdown tool on one of the computers (ver 4.1) and scratching my head on how to configure it so the computer shuts down if/when there is 5 minutes of battery life left.

On the APC itself, under shutdown there is a low battery duration and a shutdown delay.  Plus an end of shutdown option.  Not sure what that does physically.  Then on the Powerchute software not sure what I'm looking at or have to do.  From some readings the only setting under configure events is the Shutdown option which usually just has a checkbox that seems to be about the APC itself and not the computer but not sure.

Guess in a nutshell, running Windows 2012 R2, how do I go about shutting down the computer thru the network shutdown tool 5 minutes before the APC dies?

Thanks.

JR

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • apc
  • PowerChute
  • shutdown
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:48 AM . Last Modified: ‎2024-03-13 01:22 AM

0 Likes
0
1279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:48 AM . Last Modified: ‎2024-03-13 01:22 AM

John,

All of the settings are described in the NMC help file. Open the web interface to the NMC and go to Configuration the select Shutdown. In the upper right hand corner click on help and all of the setting for that page will be discussed. 

On 8/3/2016 12:55 PM, John said:

What does the shutdown delay in seconds do to that number anything?

It does not affect the low battery setting.
Shutdown Delay
Defines how long the UPS waits before it shuts down in response to a sync control turn-off command.
On 8/3/2016 12:55 PM, John said:

Also with the "End of Shutdown" what does that do?  Turn on something? 

End of Shutdown
Return Runtime Duration
The amount of time that the UPS must be able to support the load by battery power in order for the UPS to end its sleep time (or turn back on when rebooted) and resume providing output power.
Return Delay
Defines how long the UPS waits before it turns on after a shutdown that was caused by a power failure, after a scheduled shutdown, or after a shutdown initiated by a Control command. If the battery is depleted below the percentage configured as "Minimum Battery Capacity", the UPS first waits until the battery is recharged to that minimum capacity. If the battery is depleted below the capacity to provide the runtime configured as "Return Runtime Duration", the UPS first waits until the battery is recharged to the capacity that is able to provide that runtime.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:48 AM . Last Modified: ‎2024-03-13 01:23 AM

0 Likes
0
1279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:48 AM . Last Modified: ‎2024-03-13 01:23 AM

Hi,

There are 2 option

1 - Set low battery threshold on the NMC to 5 minutes. Then when the battery falls below 5 minutes of runtime all configured PCNS clients will be told to power down.

2 - In PCNS under Events there is an event Runtime remaining below threshold. When the UPS in running on battery power and the runtime remaining on the UPS drops below the threshold, PowerChute will trigger a shutdown sequence. Set that for 300 seconds and when the battery drops below 5 minutes a shutdown will happen. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:48 AM . Last Modified: ‎2024-03-13 01:23 AM

0 Likes
0
1279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:48 AM . Last Modified: ‎2024-03-13 01:23 AM

Thanks for the reply Bill.  So I set the Low Battery Duration in NMS to 5 minutes.  Assume that's the option you were referring to under "shutdown"?  What does the shutdown delay in seconds do to that number anything?

Also with the "End of Shutdown" what does that do?  Turn on something? 

Thanks.

JR

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:48 AM . Last Modified: ‎2024-03-13 01:22 AM

0 Likes
0
1280
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:48 AM . Last Modified: ‎2024-03-13 01:22 AM

John,

All of the settings are described in the NMC help file. Open the web interface to the NMC and go to Configuration the select Shutdown. In the upper right hand corner click on help and all of the setting for that page will be discussed. 

On 8/3/2016 12:55 PM, John said:

What does the shutdown delay in seconds do to that number anything?

It does not affect the low battery setting.
Shutdown Delay
Defines how long the UPS waits before it shuts down in response to a sync control turn-off command.
On 8/3/2016 12:55 PM, John said:

Also with the "End of Shutdown" what does that do?  Turn on something? 

End of Shutdown
Return Runtime Duration
The amount of time that the UPS must be able to support the load by battery power in order for the UPS to end its sleep time (or turn back on when rebooted) and resume providing output power.
Return Delay
Defines how long the UPS waits before it turns on after a shutdown that was caused by a power failure, after a scheduled shutdown, or after a shutdown initiated by a Control command. If the battery is depleted below the percentage configured as "Minimum Battery Capacity", the UPS first waits until the battery is recharged to that minimum capacity. If the battery is depleted below the capacity to provide the runtime configured as "Return Runtime Duration", the UPS first waits until the battery is recharged to the capacity that is able to provide that runtime.
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore