Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Serial Port Config on SUA2200RM2U?
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3012:34 AM. Last Modified: 2024-03-1104:02 AM
Serial Port Config on SUA2200RM2U?
What are the port settings (baud rate, ect) to talk to the serial port on the SUA2200RM2U? I'm not finding that in the User Manual (990-1352A 11/2003).
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3012:34 AM. Last Modified: 2024-03-1104:02 AM
Hi,
If you connect to the UPS serial port directly with your PC and a terminal program, it requires 2400 baud, 8 data bits, parity none, 1 stop bits, flow control none.
This can change when you have an accessory installed or connected to the UPS or you're using PowerChute software. If this applies, let us know what is installed or configured for any other possibilities.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3012:34 AM. Last Modified: 2024-03-1104:02 AM
Hi,
If you connect to the UPS serial port directly with your PC and a terminal program, it requires 2400 baud, 8 data bits, parity none, 1 stop bits, flow control none.
This can change when you have an accessory installed or connected to the UPS or you're using PowerChute software. If this applies, let us know what is installed or configured for any other possibilities.
This is a heading
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.