SYMMETRAF Generic fault error message?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SYMMETRAF Generic fault error message?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:41 AM . Last Modified: ‎2024-03-13 03:22 AM

0 Likes
3
761
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:41 AM . Last Modified: ‎2024-03-13 03:22 AM

SYMMETRAF Generic fault error message?

Hello All-

Our SYMMETRAF 16KVa (full frame) UPS seems to have one or more gremlins lurking. The unit powers up ok, with no faults, but as soon as we switch the load on (which is zero at the moment BTW) the unit fails with a generic message- 'Unable due to fault'. There is no fault code or numbers displayed, just that generic message which is less than helpful. We did recently replace the bypass contactor with a new one, so we're pretty sure its not that. It used to fault on that saying that the 'Bypass contactor was stuck in the online position'. So now we are stuck again with a different error message and a non-functional UPS. What tests or checks can we do to help narrow down what's wrong? FYI- All batteries are new, they all charge O.K. and both Main and Backup Intelligence modules show as ok as well. Running out of things to check...

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:41 AM . Last Modified: ‎2024-03-13 03:21 AM

0 Likes
0
760
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:41 AM . Last Modified: ‎2024-03-13 03:21 AM

Clarkson-

You NAILED IT! Nice job. Turns out it was the RIM that was giving the problem, not the Main. I stripped it down to One Power and Battery module like you said and added them all back in one section at a time. As soon as I put the redundant IM back, problem returned. Unit is up & running now without it. Guess we will have to figure out why the diags said both were o.k. when in fact they were not.

Thanks again, you rock!

E.E.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:41 AM . Last Modified: ‎2024-03-13 03:21 AM

0 Likes
0
761
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:41 AM . Last Modified: ‎2024-03-13 03:21 AM

Clarkson-

Thanks for the reply- Here's what we do and what we see:

1. Turn on UPS via switch on back, unit comes to life.
2. PowerView display lights up, says please wait...
3. NO LED's are lit at this time on either the PowerView Display or the MIM or RIM's
4. PowerView display shows Fuel @97%, Load @ 0%, 211 Volts In, 0 Volts out, 60Hz, Runtime 4 Hr, 31 Min (only 3 batteries in system)
5. Via PowerView display, we hit ESC\ Control\ Turn Load On...
6. "UPS has been commandeed to turn load power on"
7. Bypass Contactor down below clicks 3 times
8. Load turns on, but PowerView display also lights fault LED and Bypass LED
9.Message on Powerview display- "UPS in Bypass due to Fault, Press Any Key..."
10. Lights on MIM = Left LED= ORANGE RIgfht LED = GREEN
11. Lights on RIM = BOTH GREEN
12. We can Turn load OFF successfully via the PowerView display.
13. All Power Supplies show O.K.
14. All Batteries show O.K. 137.7 volts + 3 batteries, 0 Bad, Cap = 12 KVa, Fault Tol= n+2, Total Power supplies = 3, Bad = 0, IM= O.K. RM= O.K.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:41 AM . Last Modified: ‎2024-03-13 03:21 AM

0 Likes
0
760
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:41 AM . Last Modified: ‎2024-03-13 03:21 AM

CLarkson-

Are you sure there is only one green LED on the MIM when the display reports that it is in bypass?
Is the orange LED on the IM solid? or is it flashing with a pattern? Typical LED patters are: off, solid, very slow flash, fast flash, combination flash (mix of slow and flash).
-Yes. Upper module is the RIM and it has 2 GREEN LED's lit. Lower module is MIM and left LED is solid Orange with right LED solid Green.


Also, when the bypass contactor was replaced, was it just the bypass contact itself? or the entire tray that housees that assembly as well as many other components? This is known as the AC try (part no. 0M-612).
-We replaced the whole bypass contactor with a Brand new one. This included all of the contacts and even the micro switch. It is certified brand new and operational. The A/C tray was not replaced due to the cost

When the UPS says "in bypass due to fault" is there power being output? This can be checked via the display and verified at the block (or outlets if this model has them) with a multimeter if you have one.
-Yes. Output voltage is there and within spec.

Also, when it is in this state, can you provide the raw status of the MIM?
-Either with load on or off, the status of both the RIM and MIM shows as O.K. according to the status report from the PowerView display

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:41 AM . Last Modified: ‎2024-03-13 03:21 AM

0 Likes
0
761
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:41 AM . Last Modified: ‎2024-03-13 03:21 AM

Clarkson-

You NAILED IT! Nice job. Turns out it was the RIM that was giving the problem, not the Main. I stripped it down to One Power and Battery module like you said and added them all back in one section at a time. As soon as I put the redundant IM back, problem returned. Unit is up & running now without it. Guess we will have to figure out why the diags said both were o.k. when in fact they were not.

Thanks again, you rock!

E.E.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of