Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
SX boltdown without feet/casters
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2804:42 AM. Last Modified: 2024-03-1804:11 AM
SX boltdown without feet/casters
Looking to buy sum SX (AR3100) racks. The manual states "Warning: The enclosure cannot be stabilized using the bolt-down bracket or stabilization plate if the casters or leveling feet are removed". I just want to take off the caster and leveling feet and bolt it directly to the floor. Is this possible?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2804:42 AM. Last Modified: 2024-03-1804:11 AM
APC does not support the loss of stabilization created by removing the casters & leveling feet, but it is technically feasible to remove them and bolt the rack to the floor directly using your own kit, or preferably, the APC stabilization kits listed in the manual. If the rack suffers damage or there is a load stability issue suffered due to removing the leveling feet or casters, then APC reserves the right not to honor claims or complaints based on this fact.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2804:42 AM. Last Modified: 2024-03-1804:11 AM
APC does not support the loss of stabilization created by removing the casters & leveling feet, but it is technically feasible to remove them and bolt the rack to the floor directly using your own kit, or preferably, the APC stabilization kits listed in the manual. If the rack suffers damage or there is a load stability issue suffered due to removing the leveling feet or casters, then APC reserves the right not to honor claims or complaints based on this fact.