Matrix 5000 Smartcell XR "No Battery Communications"

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Matrix 5000 Smartcell XR "No Battery Communications"
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
138
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:42 AM . Last Modified: ‎2024-03-18 04:11 AM

0 Likes
4
1197
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:42 AM . Last Modified: ‎2024-03-18 04:11 AM

Matrix 5000 Smartcell XR "No Battery Communications"

Hi All

We inherited a Matrix 5000 with 4 Smartcell XR battery packs.
The only thing missing were the battery communication cables.
From information I found in the forums, I decided to try connecting
everything using phone handset cables.

The only problem now, is the Matrix still displays ‘No battery
Communications’. I’ve connected each of the 4 Smartcell battery
packs with the same results.

The phone cables work on phones, but I’m not sure how to test
them while connected to the Matrix/Smartcell.

I doubt the all 4 Smartcell battery communication cards are bad.
Is there a way to check the Battery Comm card in the Electronics Unit?
Is that card replaceable?


Thanks for any help.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:42 AM . Last Modified: ‎2024-03-18 04:11 AM

0 Likes
0
1196
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:42 AM . Last Modified: ‎2024-03-18 04:11 AM

Thanks for the reply Erasmus

The main cable from the Matrix to the first Smartcell goes through a small hole
in a concrete wall. I just made a new cable for that. I tried straight through, and
flipped 180. Neither worked.

I double checked the proper connection from the Battery Pack Output, to the
Batt Comm Input on the Matrix. I connected the cable to each of the 4 battery
packs, to test for a bad Battery Assy comm module. Could all 4 be bad?

Can I remove the Matrix comm card while the Matrix is hot?
Can I purchase a replacement, if it is bad?
Do you think I'll be able to find a part number for it, somewhere at APC.com?

Thanks for your help.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:42 AM . Last Modified: ‎2024-03-18 04:11 AM

0 Likes
0
1196
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:42 AM . Last Modified: ‎2024-03-18 04:11 AM

Hello JimFitze,

I´m having the same problem. I was wondering if you could fix the problem.

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 04:42 AM . Last Modified: ‎2024-03-18 04:11 AM

0 Likes
0
1196
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:42 AM . Last Modified: ‎2024-03-18 04:11 AM

Sorry for the delayed response.

None of the parts needed for a Matrix are still in stock from APC. You will need to go to a reseller or distributor to find them.

The Matrix comm card itself is is very difficult to work with. We typicaly do not have customers play with it at all. The Smartcell-XR comm card can be removed hot, however. I would recommend calling in to tech. support for assistance with this procedure.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 04:42 AM . Last Modified: ‎2024-03-18 04:11 AM

0 Likes
0
1196
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:42 AM . Last Modified: ‎2024-03-18 04:11 AM

The Symmetra systems use a straight through, 4 wire 2 line cable, which differs from the Matrix systems, which use a twisted pair RJ9, basically the handset cable you have been using. The cable part you would need from APC is a 0W0271-A or -B, in case you feel like ruling out bad cables.. Are you sure you are connecting the cable from the Batt Comm Input port on the Matrix unit to the Output of the 1st battery pack? This pattern must be followed for the remaining connections. Have you tried connecting one SmartCell-XR at a time as the first pack in the series to rule out one causing a chain of failures? There is no supported "method" of checking the Matrix comm card but it is removable...physical damage would be a dead give-away for replacement.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:42 AM . Last Modified: ‎2024-03-18 04:11 AM

0 Likes
0
1197
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:42 AM . Last Modified: ‎2024-03-18 04:11 AM

Thanks for the reply Erasmus

The main cable from the Matrix to the first Smartcell goes through a small hole
in a concrete wall. I just made a new cable for that. I tried straight through, and
flipped 180. Neither worked.

I double checked the proper connection from the Battery Pack Output, to the
Batt Comm Input on the Matrix. I connected the cable to each of the 4 battery
packs, to test for a bad Battery Assy comm module. Could all 4 be bad?

Can I remove the Matrix comm card while the Matrix is hot?
Can I purchase a replacement, if it is bad?
Do you think I'll be able to find a part number for it, somewhere at APC.com?

Thanks for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore