SUART8000XLT not charging batteries

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUART8000XLT not charging batteries
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
119
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 02:15 AM . Last Modified: ‎2024-03-10 11:54 PM

0 Likes
4
785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:15 AM . Last Modified: ‎2024-03-10 11:54 PM

SUART8000XLT not charging batteries

I have four SUART8000XLT systems, each with the big external step-down transformer and one external battery pack each installed into my server room. Over the holiday weekend, the building's circuit breaker for one of the 4 systems failed, losing only one of the two legs of the 208v AC circuit feeding the one UPS. The batteries ran down all the way down and it of course shut off. We've had the circuit breaker repaired, and the UPS powered back up, but only the bottom most battery LED lit up and it was blinking. I swapped out all the batteries with a second SUART8000XLT system, and it charged them all back up to 100% just fine, but the fully charged batteries from the 2nd system that were placed into the first system slowly discharged and they're not getting charged back up at all. I tried a manual "recalibration" routine I found instructions for a different model, but it did no good. The system in question passes its self-test and reports no problems.

Is it possible that the charging circuit in this UPS is just simply failed even though the self-test says nothing wrong?

I've got about 4 months of standard warranty left, and so will call APC tomorrow to see what they say.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:15 AM . Last Modified: ‎2024-03-10 11:54 PM

0 Likes
0
785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:15 AM . Last Modified: ‎2024-03-10 11:54 PM

do you have a voltmeter to check the voltage on them and let us know what they read for DC voltage? that'd be the first thing I ask and the first thing i assume tech support would ask. if you install them back in the UPS, it should also read the voltage for you too i think.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-30 02:15 AM . Last Modified: ‎2024-03-10 11:54 PM

0 Likes
0
785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:15 AM . Last Modified: ‎2024-03-10 11:54 PM

I just tried another "manual recalibration" procedure to see if that would help, but it did not.

Right now with the batteries in a mostly discharged state (after the latest manual recalibration "rundown"), and the unit freshly plugged back in and started up, the voltage is showing 197.6VDC which is giving a 22% level. Sometimes when I power the unit up, one or two battery LEDs on the bottom will light up blinking, but sometimes they come on solid.

When I put freshly charged, known-good batteries in it, power it up and login to the web GUI, the voltage is briefly 216.0VDC and 99% at first for just a very short while then both the voltage and percentages start dropping downward and never return.

This same set of batteries stays at 216-217VDC and 100% when I place them into any of my other three properly functioning UPS systems. I've now swapped batteries three times amongst the systems and this demonstrates that the batteries themselves are all still good.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:15 AM . Last Modified: ‎2024-03-10 11:54 PM

0 Likes
0
785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:15 AM . Last Modified: ‎2024-03-10 11:54 PM

Hi,

Your battery have some block failure inside battery module. The UPS detect enough VDC for whole battery module not each block. It's will say ok if this VDC reached the setpoint.

1. When your single block failure, it's can asbord charged current.

Example you have 2 block 12V 6 cell VRLA in serial connection. Typical you need good voltage is 2*13.75 = 27.5V (or let say 28V)
When discharged on 1.7Vpc, lowest voltage is 2*6*1.7= 20.4V.

==> If it's failure 1 block : when recharged one block can give up to 18VDC, and the other may be only 10VDC (Still weak). But whole module is 28VDC, and UPS still say it's ok.
When apply the load, the run time will drop very fast since this module is not full charged yet.

In long time, your good battery become overcharged and damage also.

2. Solve :

Some tactics: you need measure Voltagge in block to detect weak battery block. Take out these weak blook and charged in separate charger. In serial connect charged it's wont help.

Tried to discharged it 1 - 2 time and charged again

Put all the block in to the battery module and discharged 1 time. Recharged again as final.

Message was edited by: trinhkhai79

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 02:15 AM . Last Modified: ‎2024-03-10 11:54 PM

0 Likes
0
785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:15 AM . Last Modified: ‎2024-03-10 11:54 PM

APC tech support says an internal failure.

Surprisingly enough, they say the self-test does not test the charging circuit in this system.

Looks like I'm going to have to process a warranty replacement for this unit.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:15 AM . Last Modified: ‎2024-03-10 11:54 PM

0 Likes
0
786
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:15 AM . Last Modified: ‎2024-03-10 11:54 PM

do you have a voltmeter to check the voltage on them and let us know what they read for DC voltage? that'd be the first thing I ask and the first thing i assume tech support would ask. if you install them back in the UPS, it should also read the voltage for you too i think.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of