Posted: 2021-06-30 07:01 AM . Last Modified: 2024-03-07 11:37 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:01 AM . Last Modified: 2024-03-07 11:37 PM
The SUA2200 and its RM equivalent is rated at 2200VA only if you change the original plug L5-20P 125V 20A or hardwire it into the panel per UL 1778.
Out of the box with the pre-installed plugs, it is limited to 1920VA and this is explained in answer ID 184.
Installation doesn't warn about this.
http://www.apcmedia.com/salestools/ASTE-6YWRZE_R0_EN.pdf
Product description page says nothing of it.
http://www.apcc.com/resource/include/techspec_index.cfm?base_sku=SUA2200RM2U
I think this is something that should be made clear up front in spec page and manual. Why isn't it?
By the way, Answer 184 links to ID 942 but the photos on answer ID 942,does not load.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:02 AM . Last Modified: 2024-03-07 11:36 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:02 AM . Last Modified: 2024-03-07 11:36 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:01 AM . Last Modified: 2024-03-07 11:37 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:01 AM . Last Modified: 2024-03-07 11:37 PM
Hello,
Not exactly sure what you're getting at here. The SUA2200 and SUA2200RM2U both come standard with a NEMA 5-20P as the units' standard input plug. The 20amp plug plus the 120V supply, will give you 2200VA capacity out of the box. VA is a simple equation of Volts x's Amps.
If I am missing something please let me know.
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:01 AM . Last Modified: 2024-03-07 11:36 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:01 AM . Last Modified: 2024-03-07 11:36 PM
Did you read the answer ID I mentioned?
http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=184
It says that UL limits the current to 80% of the circuit's maximum capacity, so it wouldn't be orthodox to draw more than 16A through 5-20P.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:01 AM . Last Modified: 2024-03-07 11:36 PM
KVAr is right. It seems most other APC UPS models respect the 80% circuit capacity rule, but perhaps the APC marketing people forgot about it with the 2200 models.
APC would be selling SmartUPS 1800s with 5-15 plugs if they were allowed to use the entire 15 Amp circuit, no?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:02 AM . Last Modified: 2024-03-07 11:36 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:02 AM . Last Modified: 2024-03-07 11:36 PM
Link copied. Please paste this link to share this article on your social media post.