SUA1500I : Changed battery, but runtime hasn't improved

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA1500I : Changed battery, but runtime hasn't improved
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:57 AM . Last Modified: ‎2024-03-18 03:55 AM

0 Likes
3
647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:57 AM . Last Modified: ‎2024-03-18 03:55 AM

SUA1500I : Changed battery, but runtime hasn't improved

Changed battery yesterday and let it charge overnight. Ran a calibration afterwards, but the runtime is still 7 mins with 7% load (should be around 2hrs i think).

Also my log looks like this now:

09-10-23 15:04:45 Sufficient Runtime Available
09-10-23 15:04:42 Insufficient Runtime Available
09-10-23 15:04:39 Sufficient Runtime Available
09-10-23 15:03:48 Insufficient Runtime Available
09-10-23 15:03:33 Sufficient Runtime Available
09-10-23 15:03:18 Insufficient Runtime Available
09-10-23 15:03:15 Sufficient Runtime Available
09-10-23 15:03:03 Insufficient Runtime Available
09-10-23 15:03:00 Sufficient Runtime Available
09-10-23 15:02:54 Insufficient Runtime Available
09-10-23 15:02:51 Sufficient Runtime Available
09-10-23 15:02:48 Insufficient Runtime Available
09-10-23 15:02:42 Sufficient Runtime Available
09-10-23 15:02:39 Insufficient Runtime Available
09-10-23 15:02:30 Sufficient Runtime Available
09-10-23 15:02:24 Insufficient Runtime Available
09-10-23 15:02:09 Sufficient Runtime Available
09-10-23 15:02:06 Insufficient Runtime Available
09-10-23 15:02:00 Sufficient Runtime Available
09-10-23 15:01:22 Insufficient Runtime Available
09-10-23 15:01:18 Sufficient Runtime Available
09-10-23 15:01:15 Insufficient Runtime Available
09-10-23 15:01:09 Sufficient Runtime Available

Is the UPS broke?

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:58 AM . Last Modified: ‎2024-03-18 03:55 AM

0 Likes
0
647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:58 AM . Last Modified: ‎2024-03-18 03:55 AM

Actually, when running a calibration, you need at least a 30% load (fluctuating no more than +/- 5%) for an accurate result. Anything less than that and the UPS can't properly determine it's actual available runtime. Since you have 7% load on one unit and 25% load on the other, that's likely part of the issue. Try connecting some more equipment and run another calibration.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:58 AM . Last Modified: ‎2024-03-18 03:55 AM

0 Likes
0
647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:58 AM . Last Modified: ‎2024-03-18 03:55 AM

And now I've found out, I have the same problem with my SU3000 RMINET. Load is 25 %, so according to specifications, the runtime should be ~1 hr. PowerChute reports 24 mins after a calibration. The same as it was before i changed the batteries.

Would it be wise to initiate a new calibration?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:58 AM . Last Modified: ‎2024-03-18 03:55 AM

0 Likes
0
647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:58 AM . Last Modified: ‎2024-03-18 03:55 AM

Hi,

From my past experience the UPS's own internal calibration went nuts due to prolonged bad batteries. Upon replacing your batteries, disconnect any load on the UPS and do a full calibration again, it will take very very long normally to do so and thereafter it will correct the bad calibration data! Hope it helps! 🙂

Cheers,
Pavit

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:58 AM . Last Modified: ‎2024-03-18 03:55 AM

0 Likes
0
648
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:58 AM . Last Modified: ‎2024-03-18 03:55 AM

Actually, when running a calibration, you need at least a 30% load (fluctuating no more than +/- 5%) for an accurate result. Anything less than that and the UPS can't properly determine it's actual available runtime. Since you have 7% load on one unit and 25% load on the other, that's likely part of the issue. Try connecting some more equipment and run another calibration.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of