SU700NET - Dead or ??

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase โ†’ Use quotes " " (e.g., "error 404")
  • Wildcard โ†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR โ†’ Combine keywords (e.g., login AND error, login OR signโ€‘in)
  • Keep it short โ†’ Use 2โ€“3 relevant words , not full sentences
  • Filters โ†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SU700NET - Dead or ??
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 06:22 AM . Last Modified: โ€Ž2024-03-08 12:14 AM

0 Likes
12
1441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 06:22 AM . Last Modified: โ€Ž2024-03-08 12:14 AM

SU700NET - Dead or ??

Good Day! New to the forums here, with a few questions. I have 5 SmartUPS and BackUPS running here at the house flawlessly, but recently one of my 700NET's took a nose dive. Since documentation is scarce at best, I hope ya'll can help me....

I have a new battery pack in the SU700NET, during plugged in operation i have the "on-line" LED lit and 100% battery LED's. Problem is when I pull the plug from the wall (to simulate power outage), or hit the TEST button, the unit powers off and I get no battery backup.

This condition happens weather I test it on a computer / monitor (75% load), or just plug in a household lamp (0% load lights). I can not get this thing to power on battery back up.

Additionally, sometimes on re plugging in the unit, the "on-line" LED and the "on-battery" LED will flash rapidly together, and I will hear the internal relay trying to switch over.

I posted a video of the unit not switching to battery power:

http://www.youtube.com/watch?v=4-iPlTAop2U

Any help would be great....

Z

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: โ€Ž2021-06-30 06:22 AM . Last Modified: โ€Ž2024-03-08 12:14 AM

0 Likes
0
1441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 06:22 AM . Last Modified: โ€Ž2024-03-08 12:14 AM

Hello,

You can contact APC's only authorized UPS repair service, Coastal Business Machines, at 1-888-234-9877. They will be able to fix the parts and basically do a factory restore for you, and also give you a two year warranty with them, for a fraction of the price of the Trade-UPS. If you're looking to hold onto that workhorse, you may want to go that route.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 06:22 AM . Last Modified: โ€Ž2024-03-08 12:14 AM

0 Likes
0
1441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 06:22 AM . Last Modified: โ€Ž2024-03-08 12:14 AM

Hey Notorious.....

Thanks so much. With that information, I would have to go along with that. I did not realize the possiblity existed for such a relay to go bad (...or I didn't want to believe it could).

Looks like I'll head on over to trade up, unless someone suggests parts, etc.... before Monday... ๐Ÿ™‚ (I guess I'm cheap, LoL)

Thanks for posting, I appreciated it very much.

Z

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: โ€Ž2021-06-30 06:22 AM . Last Modified: โ€Ž2024-03-08 12:14 AM

0 Likes
0
1442
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 06:22 AM . Last Modified: โ€Ž2024-03-08 12:14 AM

Hello,

You can contact APC's only authorized UPS repair service, Coastal Business Machines, at 1-888-234-9877. They will be able to fix the parts and basically do a factory restore for you, and also give you a two year warranty with them, for a fraction of the price of the Trade-UPS. If you're looking to hold onto that workhorse, you may want to go that route.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 06:22 AM . Last Modified: โ€Ž2024-03-08 12:14 AM

0 Likes
0
1441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 06:22 AM . Last Modified: โ€Ž2024-03-08 12:14 AM

UserZ wrote:
I contacted them for an exchange for mine on a refurb unit. Great way to lower consumer elect waste!

Thanks, I believe this to be the best way to renew / recycle an end of life unit!!!

Z
SU700NET is no longer made, so I'm guessing it wasn't a warranty. Do you mind if I ask how much this end up costing you?

I wish I was able to get to this thread sooner. The symptoms you're describing is exactly what you'd get from a very worn out battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: โ€Ž2021-06-30 06:22 AM . Last Modified: โ€Ž2024-03-08 12:14 AM

0 Likes
0
1441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 06:22 AM . Last Modified: โ€Ž2024-03-08 12:14 AM

This was not done as an APC repair, it was done through coastal business machines. However, the symptoms originally described were a load drop without any transfer to battery. Even customers who have batteries that are 8-10 years old will be able to transfer to battery for approximately 5 seconds. This instance however, was an instantaneous drop upon loss of utility power, indicative that it was not the battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 06:22 AM . Last Modified: โ€Ž2024-03-08 12:14 AM

0 Likes
0
1441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 06:22 AM . Last Modified: โ€Ž2024-03-08 12:14 AM

The Notorious K.M.P. wrote:
This was not done as an APC repair, it was done through coastal business machines. However, the symptoms originally described were a load drop without any transfer to battery. Even customers who have batteries that are 8-10 years old will be able to transfer to battery for approximately 5 seconds. This instance however, was an instantaneous drop upon loss of utility power, indicative that it was not the battery.
I disagree. What described happens all the time on units I serviced. It all depends on the history of that UPS's battery. The battery can develop a very high internal resistance from wear/abuse(usually storage w/o semi-annual replenishment).

Smart-UPS monitors voltage at battery terminals and if there is none, it will not allow power-on. If the battery is severely worn down, it's possible for it to have the voltage to turn on, but sharply drop upon under load.

Inverter failure is not common. At this point, the correct diagnostic procedure is to measure the instantaneous floor voltage of the battery pack on bench in refurb/repair operation..

for end users.. take battery pack to dealer. ask for load test.

If it's the inverter, the battery will pass, if it fails the load test, new pack will do 99% of the time.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 06:22 AM . Last Modified: โ€Ž2024-03-08 12:14 AM

0 Likes
0
1441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 06:22 AM . Last Modified: โ€Ž2024-03-08 12:14 AM

Hey Gang!

I'm back.... I emailed Coastal Business Machines. They are very nice, but I did not feel the "deal" was there for me. I have several of these "work horse" units, and love 'em to death.

They told me $99.00 for a refurb unit, and they would pay to have mine shipped back. -or- I could pay about the same, send mine in, they refurb my unit, and send it back. In other words I was getting no credit for mine.

Although this seems like an OK deal, I am pressing on with finding parts to rebuild the two I have broken now. I have the ability and knowledge to get to "componet" electrical level if need be. I was just hoping for a quick solution.

Logic points to the battery (and that was also Coatal's first guess), but when I switch this battery pack to a "known good" 700NET, it switches and they carry the load fine. Thus, I suspect an internal failure of something related to circuit detection or inverter.

So I don't know, maybe we all need to group together and discuss rebuilding out units ourselves.....or with help of those here.



PS: I have another SU700NET, new batt pack that will not even power on. All "standard" problematic issues checked already... CB, etc..... I 'll have to start a thread on that one soon too.

Message was edited by: UserZ

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: โ€Ž2021-06-30 06:22 AM . Last Modified: โ€Ž2024-03-08 12:14 AM

0 Likes
0
1441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 06:22 AM . Last Modified: โ€Ž2024-03-08 12:14 AM

Hello,

Sorry you did not like the deal CBM gave you. Keep in mind that they would refurb it all for less than a hundred dollars, when I believe the price on a new SUA750 is around 350 or so.

Also, if you're going to discuss fixing these yourself, I know KVAR will have some input, and I ask for the purpose of these boards being present, that any information pertaining to you two discussing fixing these, just be done in private messaging. Unfortunately we won't be able to help with part numbers or pricing, as APC will not sell parts alone (and neither will CBM), but I'm sure KVar has a way of obtaining parts and numbers that will be beneficial to you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 06:22 AM . Last Modified: โ€Ž2024-03-08 12:14 AM

0 Likes
0
1441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 06:22 AM . Last Modified: โ€Ž2024-03-08 12:14 AM

Hello again Notorious K,

Thanks so much for the great info and hospitality toward me here.

If I did not have two of these broke units sitting here, I would buy a SU700NET from CBM. $99 is a steal on one of those, and I can vouch the units step up when needed. At home alone, I am running seven (yes 7).

In my business of car parts, I always allow for a return part if it benefits me and the customer. If i can allow them a "trade" or "core" value, refurb it, and sell it as such, his cost goes down and my profit goes up. Win - Win.

I can get a 700NET from CBM for $99 whether I trade my old unit or not. The only benefit to me is they would pay the shipping on the broke unit to "get it off my hands". A free shipping value is not enough to get it since I can fix it for that is my bet..... and with 7 units, I really can't add to the fleet or wifey will kill me.

So sorry for the long explaination. I have NO beef with CBM, in fact I will use them when the time is right for me. Mr Jon over there emailed me back within a few hours, with a complete explaination of his thoughts, ON A SUNDAY!!! WOW. If I had employees that would do that, I'd rule the world. (LoL). Seriously though, very nice touch to customer satisfaction.

I can't allow $700 in my budget over the next year to keep these things running. (since they are starting to give way) This is my main motivation to find parts and "refurb" the units myself and save as much of that as I can.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 06:23 AM . Last Modified: โ€Ž2024-03-08 12:14 AM

0 Likes
0
1441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 06:23 AM . Last Modified: โ€Ž2024-03-08 12:14 AM

If the battery pack is good, pull it and keep for later use. I would imagine the refurb unit comes equipped with new batteries and ready to use and you'll even have current pack as a spare, that will stay good for many years, as long as you top them off every six months or so.

So, for $200 shipped for two SU700NET replacement units, I'd just go ahead and get 'em.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 06:23 AM . Last Modified: โ€Ž2024-03-08 12:14 AM

0 Likes
0
1441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 06:23 AM . Last Modified: โ€Ž2024-03-08 12:14 AM

.
Thanks Kvar..... Would you say I can not do this myself for less than $200 to bring my current units back to life?

:-)

I guess my goal is my least expensive way to keep them in service. Right now I still believe that refurb units, although attractive, are my 2nd choice.

Thanks!

Z

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 06:23 AM . Last Modified: โ€Ž2024-03-08 12:14 AM

0 Likes
0
1441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 06:23 AM . Last Modified: โ€Ž2024-03-08 12:14 AM

I contacted them for an exchange for mine on a refurb unit. Great way to lower consumer elect waste!

Thanks, I believe this to be the best way to renew / recycle an end of life unit!!!

Z

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 06:23 AM . Last Modified: โ€Ž2024-03-08 12:13 AM

0 Likes
0
1441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 06:23 AM . Last Modified: โ€Ž2024-03-08 12:13 AM

Good Day! New to the forums here, with a few questions. I have 5 SmartUPS and BackUPS running here at the house flawlessly, but recently one of my 700NET's took a nose dive. Since documentation is scarce at best, I hope ya'll can help me....

I have a new battery pack in the SU700NET, during plugged in operation i have the "on-line" LED lit and 100% battery LED's. Problem is when I pull the plug from the wall (to simulate power outage), or hit the TEST button, the unit powers off and I get no battery backup.

This condition happens weather I test it on a computer / monitor (75% load), or just plug in a household lamp (0% load lights). I can not get this thing to power on battery back up.

Additionally, sometimes on re plugging in the unit, the "on-line" LED and the "on-battery" LED will flash rapidly together, and I will hear the internal relay trying to switch over.

I posted a video of the unit not switching to battery power:

http://www.youtube.com/watch?v=4-iPlTAop2U

Any help would be great....

Z

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 

Youโ€™ve reached the end of your document

WHATโ€™S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore