SU3000 - Master Reset?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SU3000 - Master Reset?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 03:25 AM . Last Modified: β€Ž2024-03-13 02:53 AM

0 Likes
9
1134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 03:25 AM . Last Modified: β€Ž2024-03-13 02:53 AM

SU3000 - Master Reset?

Hi Folks;

Is there any way to do a master reset on a smart ups?

I have a SU3000 that I'd like to reset right back to the factory settings and I don't know how to do that.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 03:26 AM . Last Modified: β€Ž2024-03-13 02:02 AM

0 Likes
0
1134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 03:26 AM . Last Modified: β€Ž2024-03-13 02:02 AM

Hahaha - same old same old. The only reason I asked was because I changed the float voltage in the firmware but have yet to see those changes reflected at the batteries themselves. This is why I was thinking that perhaps it's nothing more then a 'decorative' setting.

At any rate, thanks for taking the time (and effort) to look into it for me even if it didn't end up in a conclusive answer πŸ™‚

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 03:25 AM . Last Modified: β€Ž2024-03-13 02:02 AM

0 Likes
0
1134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 03:25 AM . Last Modified: β€Ž2024-03-13 02:02 AM

do you have a network management card anywhere? it will allow you to issue the reset to defaults command to the UPS. powerchute business edition software doesnt seem to let you do that. the only other way would be to issue a command directly to the UPS via a serial cable (940-0024 or 940-1524 specifically). if this is not done correctly, you can cause permanent damage to your UPS though.

so, do you have any of these cables or accessories?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 03:25 AM . Last Modified: β€Ž2024-03-13 02:02 AM

0 Likes
0
1134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 03:25 AM . Last Modified: β€Ž2024-03-13 02:02 AM

Hello - earth to winna - come in winna.....

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 03:25 AM . Last Modified: β€Ž2024-03-13 02:02 AM

0 Likes
0
1134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 03:25 AM . Last Modified: β€Ž2024-03-13 02:02 AM

Hi Winna πŸ™‚

No, to the network management card 😞
Yes! to the 940-0024C cable πŸ™‚

Were you thinking of issuing a 'z' over the serial cable? If so, I tried that but it did not seem to set the float voltage back to it's original value (I forgot what it was).

Most importantly however, can you confirm for me that adjusting the float voltage through the serial cable on this unit actually does change it and not just the displayed voltage?

Specifically the unit is a SU3000NET (90.14.d & 10/14/05 & XS0609000169)

Thanks very much!

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 03:25 AM . Last Modified: β€Ž2024-03-13 02:02 AM

0 Likes
0
1134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 03:25 AM . Last Modified: β€Ž2024-03-13 02:02 AM

lol, i am trying to follow up for you. Smart UPS is not my expertise like network management cards so I am not sure how to answer your question. yes, i was thinking of the Z command as you already tried.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 03:25 AM . Last Modified: β€Ž2024-03-13 02:02 AM

0 Likes
0
1134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 03:25 AM . Last Modified: β€Ž2024-03-13 02:02 AM

OK, and thank you!

It would be nice to be able to confirm whether the float voltage on that unit is adjustable via hyperterminal though so maybe you can keep your ears open or ask someone in the know?

Either way, I appreciate your help πŸ™‚

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 03:25 AM . Last Modified: β€Ž2024-03-13 02:02 AM

0 Likes
0
1134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 03:25 AM . Last Modified: β€Ž2024-03-13 02:02 AM

i checked - unfortunately you cannot change the float voltage on any Smart UPS.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 03:25 AM . Last Modified: β€Ž2024-03-13 02:02 AM

0 Likes
0
1134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 03:25 AM . Last Modified: β€Ž2024-03-13 02:02 AM

What does this do then?

Connect your serial (APC) cable to the UPS and your computer
Make sure the APC monitor service if installed is stopped otherwise the serial port will be in use.
Open hyperterminal (On Windows start->run hypertrm)
Create a new connection on the proper com port and use 2400 baud, 8-N-1 Xon/Xoff)
Press Shift+Y you will get SM
press 1 - wait a second - press 1 again
you should see PROG
type B
A value of 27.XX should be read back. On older Smart UPS systems with the mentioned bug you will see 27.60, 27.67 or in some cases even higher. Newer revisions use 27.30, but even that is not our perfect setting and can cause issues. We're going to reprogram the system's EEPROM all together for the perfect setting.
Press the - key (minus) then press B
Repeat this step above until you see 27.20 (If you're on a 48VDC unit select 54.24)
Confirm the setting of 27.20 by pressing B again
Press Shift+R to exit
Close hyperterminal
Reset your unit (Disconnect battery and AC)

Does it just change the displayed voltage or does it actually change the float voltage?
It uses the same process as doing the rest you mentioned above just in a different section.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 03:25 AM . Last Modified: β€Ž2024-03-13 02:02 AM

0 Likes
0
1134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 03:25 AM . Last Modified: β€Ž2024-03-13 02:02 AM

i checked back and was told that it was for factory use only (which I unofficially assume is for adjusting the actual float voltage) and we can't provide any additional information since it is not supposed to be touched or used by the end user. thus i don't have any more information on it and nobody will give it to me. :S

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 03:26 AM . Last Modified: β€Ž2024-03-13 02:02 AM

0 Likes
0
1135
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 03:26 AM . Last Modified: β€Ž2024-03-13 02:02 AM

Hahaha - same old same old. The only reason I asked was because I changed the float voltage in the firmware but have yet to see those changes reflected at the batteries themselves. This is why I was thinking that perhaps it's nothing more then a 'decorative' setting.

At any rate, thanks for taking the time (and effort) to look into it for me even if it didn't end up in a conclusive answer πŸ™‚

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of