Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

SRTL3000RM4UXLI-NC battery pack disconnected

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SRTL3000RM4UXLI-NC battery pack disconnected
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
5059
voidstar_apc
voidstar_apc
196
Teken
Teken
164
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
TillH
TillH
Explorer

Posted: ‎2025-04-24 02:03 AM . Last Modified: ‎2025-04-24 02:08 AM

0 Likes
12
2770
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-24 02:03 AM . Last Modified: ‎2025-04-24 02:08 AM

SRTL3000RM4UXLI-NC battery pack disconnected

Dear all,

we happen to have two brand new SRTL3000RM4UXLI-NC UPSs which both are not working properly.

We already have been in contact with APC support, but ended up "returning" these, get a credit note and order traditional lead-acid UPSs instead. APC however seems to have given up on these Li-Ion UPSs and don't want them back. As I hate to just throw brand new stuff away, I'd like to somehow get these working.

 

as far as I can tell from datasheets + the product pictures, we've received the correct components per kit SRTL3000RM4UXLI-NC:

1x SRT3000UXI-NCLI

1x XBP48RM2U-LI

 

Issue is: the battery pack is detected when we connect it, but a few seconds later connection seems to be lost.

We've tried with multiple combinations of battery packs and communication cables - none worked.

 

what happens in detail:

- connect AC input + power on UPS

- connect battery 48V + comm. cable + ground cable

- battery status LED is green

- UPS detects a new battery pack (strange: always as battery pack 2, not 1. there has never been a battery pack 1)

- on UPS front panel, I confirm a new (or existing, doesn't matter) battery pack has been connected

- 1-2 seconds later, battery pack status LED is flashing green and then goes off, red LED flashes once

- + the UPS states: battery pack disconnected

- UPS detects a "new" battery pack

- ....and so on....

 

We've already updated UPS firmware (UPS 16.6 (ID1046)).

Battery firmware is SMBc02.2, didn't touch this.

 

does anyone have an idea how to fix this?

Thanks a lot in advance!

greetings

Till

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 12
TillH
TillH
Explorer

Posted: ‎2025-04-24 07:43 AM

0 Likes
1
2676
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-24 07:43 AM

interesting: according to release notes for firmware 16.6, the UPS's ID changes from 1024 to 1046 when updating it to firmware 16.x

we've received the UPSs with firmware 16.5 installed, so most likely it was already on ID1046
However: I can't seem to find ANY firmware for ID 1046 anymore. all I find is v15.6 for ID1024

TillH_0-1745505743570.png

so I tend to think it might have sth to do with a buggy firmware.. not sure, though.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2025-04-24 09:00 AM

0 Likes
0
2749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-24 09:00 AM

Please show me the About Tab for both the UPS / NMC.

 

Complete the action items on page 10 and follow up with the outcome:

 

https://download.schneider-electric.com/files?p_Doc_Ref=SPD_SUO-IM-990-91565_EN&p_enDocType=User+gui...

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

TillH
TillH
Explorer

Posted: ‎2025-04-24 11:16 PM

0 Likes
0
2668
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-24 11:16 PM

Hi Teken,
thanks for picking this up!
I'll do that on Monday as I'm currently not in the office

BR

Till

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2025-04-25 05:21 AM

In response to TillH
0 Likes
0
2652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-25 05:21 AM

That was the first thing I checked and came to the same conclusion about the UPS ID being changed.

 

Along with a 16.X firmware that I’ve never seen published! 🤦‍♂️

 

Lastly, you mentioned the extended battery pack firmware was not updated. I would suggest you update the UPS with v16.6 firmware you noted as having.

 

Insure all extended battery packs are connected so the system will update the firmware on those units.

 

I saw similar problems on the standard SRT models prior to doing the upgrade. It also changed the UPS ID from 1019 -> 1025 on my units! 🤦‍♂️

Reply

Link copied. Please paste this link to share this article on your social media post.

TillH
TillH
Explorer

Posted: ‎2025-04-28 07:14 AM

0 Likes
0
2557
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-28 07:14 AM

Hi Teken,

about UPS:

TillH_0-1745827753598.png

NMC:

TillH_1-1745827803808.png

and battery info:

TillH_3-1745828061632.png

 

TillH_2-1745828047147.png

it's empty because I tried what happens if I keep input power disconnected + put some load on the UPS output.
result: same behavior as described above

battery firmware: what i meant was we didn't touch the firmware - not sure whether or not it was updated by the UPS itself

 

wrt the manual page 10:
went through the steps but no matter what I try: result is the same.
I however can't do a self-test. display states: refused; SoC not acceptable.
and of course I have to be quick while walking through the menu, as the battery pack disconnects every few seconds

Reply

Link copied. Please paste this link to share this article on your social media post.

TillH
TillH
Explorer

Posted: ‎2025-04-28 11:09 PM

0 Likes
1
2543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-28 11:09 PM

also strange: the UPS about section of the NMC lists XBP48RM1U2-LI as battery SKU, which is  the smaller 600Wh battery pack. + the 2400Wh battery pack (XBP48RM2U-LI) is detected as "Battery pack 2", there is no Battery Pack 1, no matter what I try.
however, the 600Wh battery pack is neither shown on the pictures of SRTL3000RM4UXLI-NC,
nor listed as child SKU. Got the following info from our supplier:

 

TillH_1-1745906745396.png

 

that could also speak for a buggy / wrong firmware..

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2025-04-29 05:12 AM

In response to TillH
0 Likes
0
2517
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-29 05:12 AM

Can you please upload a photo of all the units currently on hand. Provide a front & back photo of all the units.

 

My first suggestion is disconnect everything and only have the main system running.

 

Default the main UPS system and NMC to a factory state.

 

Follow up with removing the main battery cartridge from the system while off. Turn the system on and report back if the unit declares a battery fault.

 

If so, wait another ten seconds than connect the battery cartridge. The system should prompt you to confirm this is a new battery pack so enter the month & year and hit save.

 

If the system indicates the battery pack is low in SOC. Allow it to fully charge back up to 100% SOC.

 

Manually initiate a self test and report back the results. If it passes allow the system to recover back to 100% SOC.

 

Once the system is fully charged remove AC Mains from the wall outlet. The system should indicate a loss of AC power.

 

Leave the system running like this for five minutes and than reconnect the AC Main to the wall.

 

Report back the results and outcome.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

TillH
TillH
Explorer

Posted: ‎2025-04-29 11:30 PM

0 Likes
0
2471
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-29 11:30 PM

Hey Teken,

UPS was powered off, as I disconnected everything yesterday afternoon. battery pack was fully charged when I did that (charging took ~24h)

this morning:

- plugged in power input, reset NMC and UPS to defaults

- UPS display red + alarm: no battery pack available (as expected, of course)

- removed power input, pressed power button for 30sec

- connected power input to UPS -> again see the alarm that no battery pack is available, as expected

- reset UPS to defaults again + finished initial config wizard on the UPS panel

- connected battery ground, power and communication cable 30sec later
- battery status LED lights green, then flashes again

- battery detected, configured as new (it doesn't ask for month/year)

- battery pack detected as disconnected a few seconds later. didn't manage to get to the self-test before

long story short: same issue as before 😕

 

when I disconnect the battery power cable, the loop continues.
When I also disconnect the communication cable, UPS display turns red again + alarm: no battery detected (as expected)

I'll upload pictures later, first need to tidy up (several cables, switches + computers used as test load for the UPS)

 

PS: I've contacted Schneider support in parallel and asked for a newer/stable firmware - unfortunately there is no newer one and downgrade to 15.x is not possible

Reply

Link copied. Please paste this link to share this article on your social media post.

TillH
TillH
Explorer

Posted: ‎2025-04-30 01:10 AM

0 Likes
3
2467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-30 01:10 AM

Hi Teken,

 

looks like we can stop trying to get this stuff alive.

APC support just stated there is a known issue with these battery packs. even the ones they still have on stock  are affected by this serial fault.

That wasn't known when we have been in contact with APC a few months back.

 

anyway,
thanks a lot for your efforts and advices!

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2025-04-30 05:12 AM

In response to TillH
0 Likes
0
2460
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-30 05:12 AM

Appreciate you going through all the effort and also engaging APC Technical Support.

 

Along with receiving a formal reply as to root cause and final outcome. Sadly your personal experience mirrors ours and many other Enterprise clients who Alpha / Beta tested the APC line of lithium based UPS systems. ☹️

 

When everything was taken into account there was absolutely no savings in investing into their so called new technology! 🤦‍♂️

 

The obvious problems and issues for us were huge upfront costs. No readily available battery replacement never mind third party.

 

Along with insane replacement cost for the battery cartridge itself. This was compounded by products arbitrarily being end of life with no notice and bad firmware!

 

This can be easily seen by all the first and second generation lithium based systems displayed as discontinued / end of life on the product page. 🤢

Reply

Link copied. Please paste this link to share this article on your social media post.

upsss_apc
upsss_apc
Explorer

Posted: ‎2026-08-29 04:35 AM

In response to TillH
0 Likes
1
122
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-29 04:35 AM

I have this same issue, 5 months out of a 5 year warranty, APC refuse to repair / refund or offer any support. Is there a link to the official support statement that there is a known issue with these devices / batteries?

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2026-08-31 04:48 AM

In response to upsss_apc
0 Likes
0
117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-31 04:48 AM

There are no official APC / SE public facing documents that state this.


If you have a MSP reach out to them to see if they can help and facilitate this matter to a positive outcome.

 

As noted above we abandoned and stopped all purchases of any lithium based systems from APC. Because history proved out they would not stand behind the product to identify root cause and fix it!

 

Replacing the UPS with a brand new unit with a known defect is not a solution and costs each side time, finances, and resources.

 

All of the first and second generation of lithium based systems have and were quickly EOL! 

This clearly tells you SE / APC Management had no clue or could buy a clue as to fixing the issue. Besides churn out another half baked unit with a new SKU and face plate! 🤦‍♂️👎

 

As an aside if there was ever a time to have an extended warranty in place this is it. Fortune favours the bold & brave and that saved us hundreds of thousands of dollars from this disaster. 🤢

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore