SRT6KXLT not hardwired?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SRT6KXLT not hardwired?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:36 AM . Last Modified: ‎2024-03-15 04:55 AM

0 Likes
3
936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:36 AM . Last Modified: ‎2024-03-15 04:55 AM

SRT6KXLT not hardwired?

My U.S.-licensed electrician has proposed that he will wire a 50A breaker with 6AWG wire to a 14-50R receptacle where I intend to install an APC SRT6KXLT. He has stated that he will wire a 14-50P plug at the end of 6-foot electrical lead so the UPS can be disconnected and moved without calling him back.

I have read up on the topic and asked around as this model is meant to be hardwired. Specifically, I have read APC support (FAQ FA156549). The UPS model is not specifically mentioned in the FAQ and the unit has more than one output receptacle. This post suggests APC uses a relay to prevent backfeed on the input terminal. Is this relay present on the SRT6KXLT? Is there any other reason why adding an electrical lead to the SRT6KXLT is not advised? Finally, will this sort of installation void the warranty? 

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:36 AM . Last Modified: ‎2024-03-15 04:55 AM

0 Likes
0
935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:36 AM . Last Modified: ‎2024-03-15 04:55 AM

Hello - 

Yes, even though the SRT6KXLT is intended for hardwire input, it does have relays to prevent any backfeeding into the input wiring when on battery. Using the L14-50 as an input is fine as long as a licensed electrician performs the install. 50 amp plugs aren't that common, so all of our Smart-UPS units that require more than 30 amp input connections ship with hardwire terminals rather than a plug. They all meet the same UL standards for backfeed protection regardless of input.

Good question btw! 

Liam

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:36 AM . Last Modified: ‎2024-03-15 04:55 AM

0 Likes
0
935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:36 AM . Last Modified: ‎2024-03-15 04:55 AM

Hi Critical,

I've looked up the SRT6KXLT and it is meant to be hard wired, the product page lists it as having a hard wired input and output. 

Here's the product page:

https://www.apc.com/shop/us/en/products/APC-Smart-UPS-SRT-6000VA-208V/P-SRT6KXLT

Here's the wiring and installation guide:

https://download.schneider-electric.com/files?p_File_Name=SUO%20IM%20990-5090F_EN.pdf&p_Doc_Ref=SPD_...

The SRT6KXLT-IEC is similar in that it has a hard wired input but IEC outputs. If you want any more technical details then I'd advise you to contact your local APC by SE support team, even if you haven't purchased the unit yet they should be able to help.

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:36 AM . Last Modified: ‎2024-03-15 04:55 AM

0 Likes
0
935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:36 AM . Last Modified: ‎2024-03-15 04:55 AM

I appreciate the response but it does not answer my question. My licensed electrician has reviewed all of the wiring and installation guide. He states that it is not a big deal to add a lead but I can contact the local APC support team.

The issue is whether the input side of the UPS remains hot when it goes to "On Battery" mode because it is expecting, for example, a multiple earth neutral (MEN). It appears many APC SRT UPSs at least up until the SRT5KXLT have the relay referenced in the linked thread within my post. I don't see why it would not be present to meet the requirement of safety agencies (UL, VDE, etc.) but I need APC to confirm since they designed it and secured the safety approvals. Can anyone that you have access to respond to the question regarding the referenced relay being present on the SRT6KXLT?

Here is the thread again if you missed it: https://community.se.com/t5/APC-UPS-Data-Center-Enterprise/bd-p/datacenter-forum

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:36 AM . Last Modified: ‎2024-03-15 04:55 AM

0 Likes
0
936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:36 AM . Last Modified: ‎2024-03-15 04:55 AM

Hello - 

Yes, even though the SRT6KXLT is intended for hardwire input, it does have relays to prevent any backfeeding into the input wiring when on battery. Using the L14-50 as an input is fine as long as a licensed electrician performs the install. 50 amp plugs aren't that common, so all of our Smart-UPS units that require more than 30 amp input connections ship with hardwire terminals rather than a plug. They all meet the same UL standards for backfeed protection regardless of input.

Good question btw! 

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of