SRT3000RMXLI onboard LAN & serial not working

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SRT3000RMXLI onboard LAN & serial not working
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:53 AM . Last Modified: ‎2024-03-18 03:03 AM

0 Likes
2
4208
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:53 AM . Last Modified: ‎2024-03-18 03:03 AM

SRT3000RMXLI onboard LAN & serial not working

Hi

I bought a SRT3000RMXLI unit. There seems to be an onboard NIC included (not the optional extra NMC)

When i connect the RJ45 outlet to a (100MBit) switch nothing happens: no link, no light

I then assumed that the onboard NIC is deactivated for whatever reason and hooked up a serial cable to the serial RJ outlet with the included APC cable. Can't get it to work at all. Windows Desktop with native serial port via putty 9600 / 8 / 1stop / 0flow: nothing happens - blank screen after several [return]. Connecting to a firewall via the same port and putty worked (different cable and settings though).

When I connected the serial cable used for the firewall to the UPS, it immediately turned off (is this supposed to happen?)

Further when the UPS is turned on there is a noticeable buzzing sound, i have 2 other UPS here on site with similar specifications that are quiet (excluding fan, of course)

The printout of the quality assurance test states that MAC Address and Ethernet Connectivity tests have passed. 

Any ideas regarding the onboard NIC, the buzzing sound and the serial connection issues?

The included manual mentions no onboard NIC, just models with included NMS. Inside the manual under rear panel features no model is shown with onboard NIC, but my model has one: right below the RJ Serial Port and above the EPO Terminal

I completely stumped, I have no idea what to do next. There is a NIC with a passed quality assurance test but yet i cannot use it nor do I find proper documentation regarding it. 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • nic
  • onboard
  • serial
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:53 AM . Last Modified: ‎2024-03-18 03:03 AM

0 Likes
0
4207
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:53 AM . Last Modified: ‎2024-03-18 03:03 AM

Hi Liam, 

thank you very much for your great answer. I probably should haveRTFM. After reading your linkedpdf I came to the conclusion that I my nonAPC serial cable must have caused a positive voltage on Pin 9 as it was connected to PC Pin1. (table 4 from manual: Pin 9 "Application of positive voltage for >= 0.25 seconds turns off the UPS immediately.") 

regarding the humming sound: thanks again for your explanation, I'm perfectly fine with that

I was in a hurry when ordering the product and just used a LAN filter on an online price search engine so I wrongfully assumed PowerChute Network functionality was included

https://geizhals.at/?cat=gehups&xf=1494_APC~1508_LAN~3331_2016

You are also right regarding the plastic cap on the ethernet jack

I'll give up with serial communication, as the UPS is already productive and i cannot risk another unplanned downtime and just buy the NMC you mentioned for the required network shutdown

best regards

Paul

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:53 AM . Last Modified: ‎2024-03-18 03:03 AM

0 Likes
0
4207
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:53 AM . Last Modified: ‎2024-03-18 03:03 AM

Hi Paul,

Your unit does not feature an onboard NIC. If you need network management capability the appropriate Network Management Card would be the AP9630. There is an ethernet port on the UPS that is not currently enabled and is included for potential future use. I believe when you received the unit it had a cap over it. There is no way currently to enable that port.

When using the serial port, it is important to use the serial cable (Part #940-0625) included with the UPS. If you connect a standard pass through serial cable, the UPS will turn off as you mentioned. 

It is normal for the units to make some humming sound, although it shouldn't be overly loud. You may find that the load attached to the UPS can affect the volume or tone of the sound the UPS makes. This is due to the way the power supply of the load interacts with the inverter of the UPS. When comparing sound levels to other UPS units, make sure you are comparing to other double conversion units (IE: Smart-UPS SURT or SRT). Smart-UPS products are designed for computer room type use, so they may seem noisy if you are trying to use them in a quiet environment. If the sound seems dramatically louder than other similar units, I would suggest contacting your local tech support team.

If you are looking for more detailed information on communications with Smart-UPS, you might find this App Note helpful:

http://www.apc.com/salestools/MPAO-9E5RB5/MPAO-9E5RB5_R1_EN.pdf

Thanks,

Liam

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:53 AM . Last Modified: ‎2024-03-18 03:03 AM

0 Likes
0
4208
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:53 AM . Last Modified: ‎2024-03-18 03:03 AM

Hi Liam, 

thank you very much for your great answer. I probably should haveRTFM. After reading your linkedpdf I came to the conclusion that I my nonAPC serial cable must have caused a positive voltage on Pin 9 as it was connected to PC Pin1. (table 4 from manual: Pin 9 "Application of positive voltage for >= 0.25 seconds turns off the UPS immediately.") 

regarding the humming sound: thanks again for your explanation, I'm perfectly fine with that

I was in a hurry when ordering the product and just used a LAN filter on an online price search engine so I wrongfully assumed PowerChute Network functionality was included

https://geizhals.at/?cat=gehups&xf=1494_APC~1508_LAN~3331_2016

You are also right regarding the plastic cap on the ethernet jack

I'll give up with serial communication, as the UPS is already productive and i cannot risk another unplanned downtime and just buy the NMC you mentioned for the required network shutdown

best regards

Paul

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore