APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-06-25 11:08 PM . Last Modified: 2024-03-19 03:20 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 11:08 PM . Last Modified: 2024-03-19 03:20 AM
Dear Team,
I have installed SRT2200XLI and i am trying to configure SNMP Card AP9631 but i am unable to configure IP on SNMP because i didn't found SNMP option on UPS LCD screen only MODBUS option is on the screen while SNMP Card in inserted into the UPS and card is also active.
Please guide me how can i configure this on my network.
Picture is also attached for reference.
Thanks
MS
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 11:08 PM . Last Modified: 2024-03-19 03:20 AM
Hi,
Would you please provide a screenshot of the NMC interface when connected to using telnet.
Example
In the capture above I used Putty and to connect using Telnet to SMX Smart-UPS.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 11:08 PM . Last Modified: 2024-03-19 03:20 AM
Hi Muhammad,
I recommend first making sure that the NMC is running the latest firmware revision - here are the applicable firmware upgrade file and guide. If this still doesn't enable the SmartSlot option on the UPS LCD display, there are alternative methods to configuring a network management card, please see this FAQ.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 11:08 PM . Last Modified: 2024-03-19 03:20 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 11:08 PM . Last Modified: 2024-03-19 03:20 AM
Hi Sbazi,
I was trying to contact by HyperTerminal by using this procedure (https://www.apc.com/us/en/faqs/FA156064/) but there is no response from UPS side then i configured the NMC by using another UPS and and then inserted in this UPS and issue was still exist and i didnot found SNMP option.
I try to monitor via IP by Web browser it its login was normal but UPS measurement and data or logs was not found and its shows that UPS not found.
Please look into this issue.
Regards
MS
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 11:08 PM . Last Modified: 2024-03-19 03:20 AM
Hi,
Would you please provide a screenshot of the NMC interface when connected to using telnet.
Example
In the capture above I used Putty and to connect using Telnet to SMX Smart-UPS.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.