SRT10KRMXLI Max power draw per outlet group

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SRT10KRMXLI Max power draw per outlet group
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
The6thDay
The6thDay
Cadet

Posted: ‎2025-02-09 12:38 PM . Last Modified: ‎2025-02-09 12:42 PM

0 Likes
1
254
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-09 12:38 PM . Last Modified: ‎2025-02-09 12:42 PM

SRT10KRMXLI Max power draw per outlet group

Hello everyone,

 

we have multiple SRT10KRMXLI, these units have multiple outlet groups including two groups with two c19 receptacles each.

 

These groups are labeled as „group1 16 amps max“ and „group2 16 amps max“.

 

Unfortunately it is entirely unclear and documented nowhere in any manual I could find, if that is 16 amps max for the whole group or 16 amps max per c19 receptacle(allowing for 32A power draw from a single group). 


The latter would be perfectly reasonable because c19 receptacles are rated for 16A 230V and the former could become quite problematic because it would require carefully balancing the powerdraw for each outlet group and this should be clearly documented.

 

(please do not respond with assumptions, this needs a clear statement from apc, since it could lead to major issues if an outlet group were to unexpectedly shut down because of an overload)

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-02-10 01:58 AM

1 Like
0
217
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-10 01:58 AM

Hello,

 

The Nominal full current to the load is 47 A for this UPS. the output receptacles is split into switched outlet groups (SOG).two SOG 16 A and one SOG 10 A, this SOG ampere represents the maximum  current at which this SOG provide ,it is not representing the ampere for each power outlet in  the group 

 

so to summarize the total ampere that is provided by three SOGs is 42 A ,they are split as 2 SOG 16 A and one SOG 10 A for entire SOG and not each of the power  outlet C19 or C13 within the SOG, it is recommended to split the loads between the three SOGs to avoid  specific SOG breaker trip due to overload  

 

It is illustrated in attachment that ampere related to the entire  SOG and each of SOG is protected by circuit breaker rating that represent the maximum ampere value for each group 

 

Regards,

 

Karim

See Answer In Context

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Reply 1
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-02-10 01:58 AM

1 Like
0
218
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-10 01:58 AM

Hello,

 

The Nominal full current to the load is 47 A for this UPS. the output receptacles is split into switched outlet groups (SOG).two SOG 16 A and one SOG 10 A, this SOG ampere represents the maximum  current at which this SOG provide ,it is not representing the ampere for each power outlet in  the group 

 

so to summarize the total ampere that is provided by three SOGs is 42 A ,they are split as 2 SOG 16 A and one SOG 10 A for entire SOG and not each of the power  outlet C19 or C13 within the SOG, it is recommended to split the loads between the three SOGs to avoid  specific SOG breaker trip due to overload  

 

It is illustrated in attachment that ampere related to the entire  SOG and each of SOG is protected by circuit breaker rating that represent the maximum ampere value for each group 

 

Regards,

 

Karim

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of