Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

SNMPWALK issues finding correct data.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SNMPWALK issues finding correct data.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:00 AM . Last Modified: ‎2024-03-18 12:14 AM

0 Likes
5
1155
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:00 AM . Last Modified: ‎2024-03-18 12:14 AM

SNMPWALK issues finding correct data.

When I use snmp walk on our AP8865 it shows the load in Amps for 6 different banks (rPDULoadStatusLoad.1-6) When I look on the actual unit or on the web interface it says there are only 3 banks.  Also each of the 6 entries in snmpwalk after devided by 10 show on average about 8 amps per bank. The web monitor shows no more than 5 for each of the 3 banks. How can I putt the correct data to create a historical graph with it. Thank you.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • ap8865
  • monitoring
  • snmp
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:00 AM . Last Modified: ‎2024-03-18 12:14 AM

0 Likes
0
1155
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:00 AM . Last Modified: ‎2024-03-18 12:14 AM

Hello,

To begin, for AP8XXX series Rack PDUs, you should ideally be using the .iso.org.dod.internet.private.enterprises.apc.products.hardware.rPDU2 subtree. The rPDU subtree is used for older AP7XXX series Rack PDUs. You may find some supported values but they are only there as to not break customer's polling completely.

Anyway, I set up an AP8865 simulator. I see what you're talking about when I use rPDULoadStatusLoad. What it is providing to you is the phase load - for the 3 phases since it is a 3 phase PDU, and then it is providing you the bank load in amps for each of the three banks (I put some test values in so I could associate to them what I see on the web). I think this relates back to how I said the rPDU subtree is not perfect for AP8XXX PDUs and is showing you "load" for AP8XXX which is both phase and bank load for this model. Older AP7XXX PDUs could only show bank load I think.

You'll find in the rPDU2 subtree, we have separate OIDs now for phase, device, and/or bank loads which should only return three values each so I'd refer to those which should work better.

Let me know if you have any questions. The one quirky thing I did find is for rPDU2BankStatusCurrent, I got 5 responses. They appear to be bank 1, bank 2, and bank 3 readings. The last two appear to be the readings from L-N for the (2) 120V outlets this model has - I confirmed this by polling rPDU2BankPropertiesPhaseLayout.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:00 AM . Last Modified: ‎2024-03-18 12:14 AM

0 Likes
0
1156
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:00 AM . Last Modified: ‎2024-03-18 12:14 AM

Hello,

To begin, for AP8XXX series Rack PDUs, you should ideally be using the .iso.org.dod.internet.private.enterprises.apc.products.hardware.rPDU2 subtree. The rPDU subtree is used for older AP7XXX series Rack PDUs. You may find some supported values but they are only there as to not break customer's polling completely.

Anyway, I set up an AP8865 simulator. I see what you're talking about when I use rPDULoadStatusLoad. What it is providing to you is the phase load - for the 3 phases since it is a 3 phase PDU, and then it is providing you the bank load in amps for each of the three banks (I put some test values in so I could associate to them what I see on the web). I think this relates back to how I said the rPDU subtree is not perfect for AP8XXX PDUs and is showing you "load" for AP8XXX which is both phase and bank load for this model. Older AP7XXX PDUs could only show bank load I think.

You'll find in the rPDU2 subtree, we have separate OIDs now for phase, device, and/or bank loads which should only return three values each so I'd refer to those which should work better.

Let me know if you have any questions. The one quirky thing I did find is for rPDU2BankStatusCurrent, I got 5 responses. They appear to be bank 1, bank 2, and bank 3 readings. The last two appear to be the readings from L-N for the (2) 120V outlets this model has - I confirmed this by polling rPDU2BankPropertiesPhaseLayout.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:00 AM . Last Modified: ‎2024-03-18 12:14 AM

0 Likes
0
1154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:00 AM . Last Modified: ‎2024-03-18 12:14 AM

Sorry I know this next question isnt directly related to APC products but how do i do an snmpwalk for that specific subtree? I usually type in "snmpwalk -v2c -c public myserver.mydomain.com enterprises". What do I specify in order to get to the other part of the tree? Thank you for your quick repsonse!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:00 AM . Last Modified: ‎2024-03-18 12:14 AM

0 Likes
0
1155
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:00 AM . Last Modified: ‎2024-03-18 12:14 AM

Nevermind it as easy to figure out what to change in the command. Thanks again.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:00 AM . Last Modified: ‎2024-03-18 12:14 AM

0 Likes
0
1154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:00 AM . Last Modified: ‎2024-03-18 12:14 AM

Did you delete one of your messages about the phase thresholds? Haha - I tried to reply and it said the message was not found. If you still have questions on phase balancing/bank balancing, let me know.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:00 AM . Last Modified: ‎2024-03-18 12:14 AM

0 Likes
0
1155
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:00 AM . Last Modified: ‎2024-03-18 12:14 AM

OH - I see, you decided to make a new thread. I'll post my response there smile

Pertientne to this thread though, I just realized I made a mistake. I have two Rack PDUs connected in a Network Port Sharing group. Responses 4 and 5 (from rPDU2BankStatusCurrent) for me on were actually from my Rack PDU 1 where as Rack PDU was AP8865. So, disregard what I said and you should just get the three responses.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now